Multiple Cables Per Phase

07/17/2014 5:29 AM

I know this may sound like an exam question, but it's from a real life test result.

Scenario:

Single ACB in an enclosure acting as a main intake switch from a generator, each phase fed with 8x240mm2 cables, both in and out. Cables all the same length

Results:

During a temperature rise test, which was carried out at a very low voltage ~15v, there was a huge imbalance between the currents in each cable, in some cases up to double the adjacent cable on the same phase. (The sum of the cable currents is correct)

Question:

Is this an effect of the very low voltage and it's ratio to the cable volts drop, or would this imbalance also be seen at normal mains voltage 400v?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Multiple cables per phase

07/17/2014 6:11 AM

How are the cables run and terminated? If run in groups of all the same phase you will get problems.

One of the best ways is to put one of each phase in trefoil formation, each trefoil group spaced apart.

Something else to consider is magnetic repulsion during a fault. A guy in the UK was killed when the unsecured cores suddenly flew apart causing a trench cover plate to fly in to the air. I used aluminium trefoil cleats.

__________________
The reports of my death are greatly exaggerated.
Reply Score 1 for Good Answer
Anonymous Poster #1
#2
In reply to #1

Re: Multiple cables per phase

07/17/2014 8:27 AM

This was a test scenario, but they were generally lying on the floor, not clipped in . Each phase would be grouped to allow current monitoring and connection to the star point

I understand the issues during short circuit, but for now I'm more interested to understand if the issues seen were due to the low voltage of the test.

Thanks

Reply
3
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Multiple Cables Per Phase

07/17/2014 9:15 AM

The applied voltage has nothing to do with this issue at all. The problem is as Tony mentioned, the physical arrangement of the conductors. The problem is caused by the electrical principal known as "inductive reactance".

Read this thread...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Good Answer (Score 3)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#4

Re: Multiple cables per phase

07/17/2014 9:19 AM

Yes, it is due to the extremely low voltage, but maybe it was used to make the test more stringent, and reveal any unbalance of the contacts closure.

The contacts of the ACB are still being that: contacts, subject to oxidation and contamination; You surely have worked on contactors or relays which (closed)contact's resistance range from a couple ohms to several hundreds, but they work perfect in the actual application.

Anyway, you stick to whatever codes apply for testing and/or installing such devices.

Regards

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Multiple Cables Per Phase

07/17/2014 10:34 AM

Sounds like you were running some tests to get data for determining the generator parameters. How did you create your "bolted three phase short circuit"? Short circuit tests require extreme detail regarding how every connection is made up, everything must be as identical as possible. In particular you must use identical hardware (nuts, bolts, Belleville washers, etc.), torque levels, crimping pressures, surface preparation, lead lengths, etc.

Failure to do so will result in a joint that has slightly different resistance than the others, overheating, and unbalanced currents. Check the voltage drop across each connection, they should all match. Get out your IR thermometer and find the hottest connection, fix it, and do it over and over until everything is within a few percentage points. You may also need to check the internal connections as well, check the phase wiring of the lowest current first.

One last thing, make sure your instrumentation is not introducing the error, swap leads and see if the problem follows, then swap CTs, since any imbalance there will be reflected in your test results. Pay close attention to the breaker, contact resistances can vary by milli-Ohms and be inconsistent between operations.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 3)
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#9
In reply to #5

Re: Multiple Cables Per Phase

07/18/2014 1:23 AM

Hi Ramconsult Sounds like a good place to start. Perhaps one may give some thought to the possibilities of eddy currents especially in the cable glands and gland plates in the panel.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Multiple Cables Per Phase

07/17/2014 1:17 PM

IMO the current unbalance could be in both situations : unbalance due to a wrong laying sequence of cables-mainly if the cables of the same phase being grouped together- and could be the low level of voltage [in this case a insensible difference of a few volts could be a big relative voltage unbalance.

According to:

A CABLE CONFIGURATION TECHNIQUE FOR THE BALANCE OF CURRENT DISTRIBUTION IN PARALLEL CABLES by San-Yi Lee [Fig.1] the current unbalance could be up to 1/7.

__________________
Julius
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7

Re: Multiple Cables Per Phase

07/17/2014 4:02 PM

I assume you were pumping fairly hefty levels of current through the cables and breaker, in order for them to get hot.

Since you have that many cables in parallel per phase, differing resistances in each cable will affect how much current each will carry. Before the temp rise test, you need to check each cable end-to-end (including the bolted connections and the terminal lugs) with a low-resistance ohmmeter. Resistance should be in the hundreds of microohms range or less, I would expect.

If not, then there is some element in the cables that is causing higher resistance. It may be the bolted connection. Maybe the terminal of the breaker or the lug on the cable doesn't have a nice, clean, non-oxidized, flat surface. Maybe the lug wasn't crimped or bolted tight onto the cable end. There are many possible contributing factors, but the likely overall cause is higher resistance in some of the cables than others.

These effects will show up no matter what voltage. P = I2R. You will generate watts based on the current and resistance, with higher resistance cables causing more of a voltage drop across them.

__________________
To get the right answers, first you need to ask the right questions.
Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#8

Re: Multiple Cables Per Phase

07/17/2014 5:12 PM

Sounds like the resistance of the connections is much higher than the cables. Make sure the connections are clean and tight.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Multiple Cables Per Phase

07/18/2014 8:56 AM

The mutual induction between parallel conductors may provoke an unbalance between currents flowing through these conductors. If the conductor positions are symmetric-as in an equilateral triangle-then the induced EMF from the other conductors is the same in all conductors and in turn all the currents are the same. If the conductors of the same phase are arranged in straight line-with clearing space or not-the unbalance is elevated-more conductors per phase, more unbalance.

In the above case of 7 cables per phase grouped per phase in a straight line the unbalance is 1/7[80/600 A].

__________________
Julius
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#11

Re: Multiple Cables Per Phase

07/19/2014 8:19 AM

The low voltage is important. It causes the best heating with the same power applied, and fastest results. I only have seen it done from a distance, smarter people on this forum know much more than me about this.

BTW, why not join this forum. It seems like you have something to say, and joining would distinquish you from the hundreds of noobs, and exam boys out there.

__________________
If it was easy anybody could do it.
Reply
Associate

Join Date: Jul 2014
Location: I live in USA, Colorado in the houses of 7 Summits
Posts: 28
#12

Re: Multiple Cables Per Phase

07/26/2014 4:50 AM

One can use conductor material is made by paralleling phase conductors then by using the large conductors for phase, yeah most of these huge imbalance is an effect of the low voltage, multiple cables per phase with proper modeling is good for the circuit.

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#13

Re: Multiple Cables Per Phase

08/07/2014 12:10 PM

Dear Friend,

The problem is in the way the Cable is connected.

You have stated "Single ACB in an enclosure acting as a main intake switch from a generator, each phase fed with 8x240mm2 cables, both in and out. Cables all the same length"

This type of connection gives a message that - though the cables are identical, 8 cables are CONNECED to R Phase, 8 cables are CONNECED to Y Phase, 8 cables are CONNECED to B Phase. If so this is wrong since the capacitive effect is compounding and results in HEATING EFFECT in the cable.

The correct method of connection in the given scenario is

"The RED Core of all the 8 cables to be grouped and connected to R Phase, the YELLOW Core of all the 8 cables to be grouped and connected to Y Phase, the BLUE Core of all the 8 cables to be grouped and connected to B Phase" This will nullify the EXCESS HEATING EFFECT of the Cable due to CUMULATIVE EFFECT of CAPACITANCE is NULLIFIED.

The reason for the unequal current may be due to some loose connection, improper crimping of Lug(s) adding to Resistance and resulting in over heating.

DHAYANANDHAN.S

Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: