Leakage Current

07/18/2014 10:00 AM

Hi All,

We are facing a strange problem where in even though we are not using any electricity, the meter shows units consumption. To isolate the problem, we switched off all the MCB's and found that no units is consumed. But when we switch on all the MCB and still dont use any electricity, still the meter shows the consumption units with MCB's on. ( ex: in 30 mins showing 2 units consumption even though no load, but MCB's ON). can anyone guide us how to isolate this leakage current.

best regards,

venkata

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#1

Re: Leakage current

07/18/2014 10:17 AM

What are the loads being powered? Are there any EMI filters wired into these that are active when the CBs are closed?

If you have EMI filters, it's possible a capacitor is leaking, and drawing more then the reactive power it normally would.

__________________
ignator -
Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Leakage current

07/18/2014 10:18 AM

Follow me here, this is very complex. Turn the MCBs on one at a time, observing the current. When you find one in which current flows, start tracing the wire that is connected to the load side of it. Whenever that wire connects to a device, lift that wire off of the terminal and see if the current flow ceases. If it does, look at the device itself as a consumer, or if it is only a switch, repeat the process starting from the other side of that switch, following every wire in that circuit until you find it. It's there.

Here is what you will likely find by the way. It will be a transformer, a power supply (which will have a transformer inside), an resistor of some sort, an RC snubber (which has a resistor inside), a pilot light (another resistor) or possibly a high resistance ground fault or short circuit.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#4
In reply to #2

Re: Leakage current

07/18/2014 10:47 AM

GA. Even the GFI contain monitoring electronics that consume tiny amounts. For OP to have measurable results, most likely it's a transformer, as you say. There are many " vampire " circuits these days, the only way to track them down is load shedding. Any equipment " off " but on standby could have tiny drains. GA.

__________________
Smart as a post and twice as fast.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#7
In reply to #2

Re: Leakage current

07/18/2014 5:33 PM

Good answer, and a classroom classic as well, a bump on the head followed by an enlightening lesson.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Leakage current

07/18/2014 10:38 AM

Is there no one on your staff who has even a rudimentary understanding of electricity?

Just asking.

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#6
In reply to #3

Re: Leakage current

07/18/2014 5:26 PM

They surely have, but they all are too dazed by the miriads of new devices which turn a light ON, to indicate that the device is OFF.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5

Re: Leakage Current

07/18/2014 3:51 PM

Open the breaker box, get a clamp on ammeter, and check the current for each breaker.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#8

Re: Leakage Current

07/19/2014 10:06 AM

If you have any buried (underground) wiring, it is possible there is a cut in the insulation.The cut does not have to be very large,just a minor nick will do it.The surrounding ground will absorb the heat.This frequently occurs when wires are not buried deep enough,or if there is very rough back fill over the wire,such as crushed brick,etc.

Isolate the circuit as previously described to determine the particular one of interest.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#9

Re: Leakage Current

07/19/2014 10:22 AM

You have electric clocks, door bell, clock radio, cable box, and other electronic appliances like TV, cellphone chargers, etc. that have built-in timers that are always ON and consuming power even if their power switches are on OFF positon!

__________________
vsar
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: Leakage Current

07/19/2014 11:00 AM

Even supplying power on long cables, uses a small amount of power, even though nothing is switched on at the end of them.

The longer the cables, the greater the effects....

Its best to activate circuits with long cables only when actually needed....but also remember, the effects are "cumulative" and a dozen short cable runs will add up to the same power loss as a longer single cable run.....roughly speaking.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11
In reply to #10

Re: Leakage Current

07/19/2014 1:58 PM

How so?Please explain,aside from capacitive charging,which is very negligible,and not a constant drain.I have seen capacitive effects on long communication lines, but never on normal neighborhood occupancy power.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #11

Re: Leakage Current

07/19/2014 3:01 PM

Has the OP stated ".....normal neighborhood occupancy power."

I never saw it. Please be so kind as to mention which post that was?

My impression was that it was industrial, not domestic....

The losses from power station lines can be 5-6%......the national average is in that range, partly resistive of course.....remember. the lower the voltage, the higher the losses....

We are working here with incomplete infos.....remember G.I.G.O?

Now are you surprised? I won't be, either way.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#13
In reply to #12

Re: Leakage Current

07/19/2014 3:41 PM

Where did he mention "power stations" or long distance power transmission,or a national or regional problem?

He mentioned MCB's which are normally indicative of low voltage conditions and a meter,not meters,(Which would consist of 3 meters in industrial applications:

1ea KVa meter, 1ea Kvar meter, And 1ea Demand meter.)

Would the OP please clarify which type system he is referring too, to avoid ambiguity in answers?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #13

Re: Leakage Current

07/20/2014 10:38 AM

I note he says "we" and not "I", which makes me think of a firm rather than a family.....not that its truly indicative either way.....just a thought!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#15
In reply to #14

Re: Leakage Current

07/20/2014 4:07 PM

I am not going to play this game of semantics with you.I will wait for the OP to clarify his question.....or not.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #15

Re: Leakage Current

07/20/2014 5:43 PM

Why not? Its the only best game in Town!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Jul 2014
Location: I live in USA, Colorado in the houses of 7 Summits
Posts: 28
#17

Re: Leakage Current

07/26/2014 3:48 AM

Leakage current is the current that flows through out the protective ground conductor through ground. There are types of leakage current, these are AC leakage, DC leakage etc. To isolate the leakage current, the measurement of leakage current is one of the most important tests in electrical current, to isolate the leakage current by supplying voltage current normally, apply the DUT power source to isolate the leakage current.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); HiTekRedNek (4); ignator (1); JRaef (1); LongintheTooth (1); lyn (1); Rixter (1); ShawnHoppe (1); vsar (1); Yahlasit (2)

Previous in Forum: Stabilizer for Air Conditioners   Next in Forum: M/G Set vs Rotary Converter

Advertisement