Diff Protection for 33KV/0.415 kv 2 mva Transformer

07/19/2014 2:25 AM

Hello

I have to use 33 KV/.433 KV 2 MVA delta star tranfomer for my plant.

PLs inform do i need to give difff protection for transformer or not required?

If not required then why not required? If we provide it then will it have some stability issues?

One more question is that unbalance load cana lso create some probelm in diff protection? By definition Diff protection will not be affected for the faults out of protection zone or by unbalance loads.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: DIFF PROTECTION FOR 33KV/0.415 kv 2 mva TRANSFORMER

07/19/2014 9:08 AM

I've only come across diff protection on much larger transformers. If the MV/LV protection is set right then there's not much point.

It's your transformer, do you want to spend the money?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: DIFF PROTECTION FOR 33KV/0.415 kv 2 mva TRANSFORMER

07/19/2014 9:32 AM

If the transformer is important to your operations then you protect it with differential and other protective relaying, if it's not you don't. Spurious trips are always a concern, only you can evaluate their impact/cost.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#3

Re: Diff Protection for 33KV/0.415 kv 2 mva Transformer

07/23/2014 6:38 AM

as such Diff prot is not required for smaller transformer but if provided then its added protection.

if stability of diff scheme is ensured then it must not operate for any unbalance in load or out of zone faults.

Register to Reply
Anonymous Poster #1
#4

Re: Diff Protection for 33KV/0.415 kv 2 mva Transformer

08/06/2014 4:34 AM

Hi mate

To protect your Transformer with Differential protection is not a safe guard for your Transformer ......

If your Transformer trips on Diff and the Diff relay settings is worked out correct then their is already a fault inside your Transformer...

For this type Transformer you can protect it with 415volt Overcurrent and Earthfault protection circuit breakers connected to the 415voltage side CT's...

Just put the correct settings on and it will trip when your Transformer gets overloaded.......

Your Differential protection does not help when the transformer gets overloaded

Register to Reply