Shunt Release Trip Problem

07/23/2014 2:25 PM

HI EVERYBODY,

I have installed L&T DN0-SH Shunt Release in DU100H MCCB with SM500 series monitoring device MG73BH , my problem is whenever electricity goes off every time when electric is back MCCB trips and I cant switch on the MCCB again without disconnecting the shunt release from monitoring device

p.s. MG73BH relay contact points no. 15 & 16 are used for shunt.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: SHUNT RELEASE TRIP PROBLEM

07/23/2014 2:43 PM

Have you talked to the equipment manufacturer yet?

__________________
Good moaning!
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Shunt Release Trip Problem

07/23/2014 10:12 PM

Poor system design, shady components.

You have a phase monitor relay (MG73BH). It has an "adjustable operate time", although for the life of me, I cannot figure out what the freaking manual says about how that adjusts. So it might be adjustable from 0-15 seconds, or it might be fixed at 5 seconds, it's just completely foggy. Very inadequate descriptive information in my opinion.

You have wired up a Shut trip coil on a molded case circuit breaker to a Normally Closed set of contacts on that relay. The "operate delay", whatever it might be, means those contacts will NOT change state until AFTER the operate delay, then change state AGAIN after the "trip delay", whatever that is.

So when you try to close the breaker, those relay contacts are ALREADY in the closed state, immediately energizing the Shunt Coil as soon as the breaker contacts close, which trips the breaker again. Even if the "operate delay" can be adjusted to zero (if that's what they mean), nothing is ever absolutely zero on electronic devices. If it takes just 1/4 second for the phase monitor relay to power up and recognize that the power is good, it is too long, you have ALREADY commanded the breaker to trip again.

Bottom line, you are attempting to do something that you should not try to do with a breaker and a shunt trip. I can't say what it WAS that you were trying to accomplish, but whatever is was it is never going to work like this, because this never works.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Participant

Join Date: Jul 2014
Posts: 3
#3
In reply to #2

Re: Shunt Release Trip Problem

07/24/2014 2:05 AM

Thanks JRaef, I am very much satisfied with your answer,

actly I bought this system to protect my home appliances ( T.V., fridge, inverter etc.) from high voltage damage from 16 kv transformer three phaze 240v connection which is causing damage even if equipment is off.

Is there any other way for high voltage protection.

P.S. I am living in farm house, very far from city, so I have to manage every thing myself.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4
In reply to #3

Re: Shunt Release Trip Problem

07/24/2014 2:51 AM

If I were you, I'd get on to the local utility supplier and get them to sort out all their neutral links so that high voltages don't happen any more, and claim on their indemnity insurance if they still do. It shouldn't be up to the householder to install any more equipment than is in use elsewhere on the network!

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #2

Re: Shunt Release Trip Problem

07/24/2014 11:23 PM

"You have a phase monitor relay (MG73BH). It has an "adjustable operate time", although for the life of me, I cannot figure out what the freaking manual says about how that adjusts. So it might be adjustable from 0-15 seconds, or it might be fixed at 5 seconds, it's just completely foggy. Very inadequate descriptive information in my opinion."

I see what you mean.

There are three relays in the range. The MG73B9 & MG73BH the on delay is adjustable, 0→15m & 0→15s respectively, off delay fixed at 5s. The MG73BF the on delay fixed at 5s, the off delay is adjustable 0→15s.

I'm glad this has cropped up, I was looking to use one. Whichever I chose I would have been snookered one way or the other.

It'll teach me to RTFM first!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Shunt Release Trip Problem

07/24/2014 10:13 AM

So is this damage being caused by sustained high voltage, or high voltage spikes? Have you been able to document it either way? Because the sustained high voltage is, to Crabtree's point, the responsibility of your serving utility so they should find the reason and correct it. Spikes however are something they will, in my experience, vehemently deny, deny, deny, until you hand them documentation showing it, then they end up telling you it can't be helped anyway and you need to deal with it yourself (so don't waste your time).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Shunt Release Trip Problem

07/24/2014 10:46 PM

That sounds like the US utilities are as good as their UK equivalent, the DNO's.

Whatever the problem, it's nothing to do with them. I've caught them out a couple of times but it was hard work.
Last time was voltage fluctuations, they couldn't argue with 28 days of recorded data. They finally admitted they had a problem with a 33/11KV transformer tap changer. I told them that before the argument started.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2009
Posts: 39
Good Answers: 4
#8

Re: Shunt Release Trip Problem

07/25/2014 4:42 AM

add a on delay timer ( preferable delay 1 to 2 sec) between monitoring device and shunt trip coil.

Anand

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jul 2014
Posts: 3
#9
In reply to #8

Re: Shunt Release Trip Problem

07/26/2014 5:51 AM

thanks Anand, I was thinking the same way and I hope it should work, except in one condition when lights go off and comes again with high voltage then no protection for high voltage is available.

Register to Reply
Member

Join Date: Mar 2014
Posts: 5
#10

Re: Shunt Release Trip Problem

07/30/2014 7:31 AM

Use an on-delay timer at the o/p of the SM500...if u can give me an email id ..I shall send u the circuit diagram

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#11

Re: Shunt Release Trip Problem

07/30/2014 9:28 AM

give a thought to using the undervoltage release while designing your system instead of using the shunt release . . . .

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

anand.mandarapu (1); Crabtree (2); JRaef (2); krajat (1); shikul (2); soebfatehi (1); TonyS (2)

Previous in Forum: System Volatege   Next in Forum: Corrosion Pattern on Press-Fit SCR Pole Faces