Upstream And Downstream Short Circuit Current

07/28/2014 5:33 AM

Dear Sirs,

I have just got a doubt and seeking your valuable advices. I have a 11kV ring in 3 substations.In two substations the short circuit rating is 25kA for 3 sec and the other substation is 25kA for 1 sec. Is this a correct methodology. Substations are 1-2 kilo meters apart. Connecting with 2 runs of 1Cx500sq.mm Cu/XLPE/AWA/PVC per phase.

One substayion is not yet constructed and Switchgear fabrication is ongoing.

Please advice.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Mar 2014
Posts: 75
#1

Re: Upstream And Downstream Short Circuit Current

07/28/2014 7:33 AM

Who designed this?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Upstream And Downstream Short Circuit Current

07/28/2014 9:40 AM

Do you mean you have 3 Ring [Main Units] of 11[12] kV 25 kA/1-3 sec.? Usually the rated breaker current could be 630 A [See Schneider Electric Medium Voltage Distribution Catalogue RMU 24 kV].

If the 3 RMU are connected in series and the ends are connected to the same source, then the maximum load current would be 630 A.

According to Nexans Cables Catalogue [for BS 6622 6.35/11 kV cable Cu/XLPE/AWA/PVC], maximum current for single-way duct [underground] could be 570 A.

[120 RHO, 15oC Earth temperature, 0.8 m depth].

See: Nexans 6-36kV Medium Voltage Underground Power Cables XLPE insulated cables.

The short-circuit current [one cable per phase] may withstand is 40 kA/3 sec. [from rated 85 oC up to 250 oC]

__________________
Julius
Register to Reply
Participant

Join Date: Jul 2014
Posts: 3
#4
In reply to #2

Re: Upstream And Downstream Short Circuit Current

07/28/2014 12:15 PM

Thanks for your responce.

What i mean is i have three switchgears.One will be considered as upstream substations having two feeders going to two downstream substations. Then this two downstream substations are connected together.This will be a ring circuit. However downstream interconnection will be open in both places and will be keeping as a redundancy source.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Upstream And Downstream Short Circuit Current

07/28/2014 10:06 AM

Is this run as a ring with one point of supply or an open ring with two points of supply?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Jul 2014
Posts: 3
#5
In reply to #3

Re: Upstream And Downstream Short Circuit Current

07/28/2014 12:18 PM

Open ring with two points of supply.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6
In reply to #5

Re: Upstream And Downstream Short Circuit Current

07/28/2014 2:12 PM

In Electrical Engineering power distribution it is always better to draw sketch when you request for any clarification, so that we can understand better to guide you better.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#7

Re: Upstream And Downstream Short Circuit Current

08/12/2014 11:37 AM

There is mistake in your question. Short circuit rating is same for 3 substation but the withstanding time is different. Nobody design time based protection nowadays. It shall be energy based protection . Calculate the fault level for 3 substations and the Equipment/switchgear manufacturer to confirm the withstand time. There is nothing wrong to consider 3 seconds. But it will increase the cost of switchgear.Normally, short circuits shall be protected within milli seconds. No need to withstand for 3 seconds.
Better to re-check and discuss it with consultant engineer for your project.

Register to Reply