Intensity of the Magnetic Field

07/31/2014 10:40 AM

Dear all

good day

We checked the intensity of the magnetic field in the 400 KV network and found that the field strength of phase R much higher than the other phases and in multiple places in the network, please what is the possible causes

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#1

Re: intensity of the magnetic field

07/31/2014 11:32 AM

It's simple physics. If Hi is higher, then Ii is higher. Your network is probably unbalanced.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: intensity of the magnetic field

07/31/2014 11:43 AM

Current is higher or you're not measuring the field strength at the same distance, R, from the conductor. The H field drops off as 1/R.

Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#5
In reply to #2

Re: intensity of the magnetic field

07/31/2014 7:10 PM

Dear sir

thank you very much for your response

but ,please what mean by (The H field drops off as 1/R.)

thanks

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#8
In reply to #5

Re: intensity of the magnetic field

07/31/2014 8:57 PM

I will try to explain it. A current flowing through a wire creates a magnetic field that circles the wire. We call this field the H field. It is a vector field, meaning that at any point the field has a magnitude and direction.

If you take a circle centered on the wire and you multiply the H field tangent to the circle times the circumference of the circle, it gives you the current flowing through the wire (by Maxwell's laws). The further you are from the wire, the larger the circumference (C=2πR), so the H field will be inversely proportional to R. The circumference times the H field will always give the same answer for the current. (This is called a line integral)

You may be more familiar with the B field. The B field is the H field multiplied by the permeability, μ, (which depends on the material). B=μH.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Intensity of the Magnetic Field

07/31/2014 11:59 AM

And other ferrous metal in the area could affect your readings.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Intensity of the Magnetic Field

07/31/2014 1:39 PM

Is your 400kV network overhead, underground, GIS? What is the configuration of the lines, trefoil, flat, transposed? How did you get close enough to a 400 kV line to measure the field intensity of each phase? Don't forget that a Hall-effect Transducer will show the vector sum of the magnetic field from all sources combined, and distance matters a lot.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#6
In reply to #4

Re: Intensity of the Magnetic Field

07/31/2014 7:47 PM

Dear sir

Thank you for your respone

our 400kV network is overhead line, configuration of the lines is triple wire for

each phase,when i measured the Intensity of the Magnetic Field by 3D

measurement of the magnetic field(Gauss meter) i stood under phase /R

then phase /S then phase /T .In other words,the distance for all measurment was

symetrical

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #6

Re: Intensity of the Magnetic Field

07/31/2014 7:59 PM

Thanks for the feedback! So your OHL is configured flat like this O----O----O and is ordered R-Y-B. Where is the tower in relation to the conductors? What is the distance from the middle phase to ground, and are there any underground conduits/pipelines running parallel with the phases? How long is OHL and are there any transpositions? Did you also record the individual line currents during your tests?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#10
In reply to #6

Re: Intensity of the Magnetic Field

08/01/2014 8:29 AM

If the lines are side by side, then it's not really symmetrical. What are the distances between the wires compared to the height? Any reading directly underneath one line would also see the field from the other lines, depending on the distance of separation, and the center line would have more interference.

I would be suspicious that the electrical field would interfere with the electronics of your current sensor.

Here is a paper on remote sensing of current on lower voltage HV power lines. The sensor must be mounted on the power pole closer to the wires, and the geometry is taken into account in measuring the currents.

http://www.cired.net/publications/cired2001/1_55.pdf

Register to Reply
Commentator

Join Date: Oct 2013
Posts: 72
#11
In reply to #10

Re: Intensity of the Magnetic Field

08/03/2014 6:24 PM

Dear sir

Thank you for your interest

but the problem now, when we need to open the control panel door for 400KV

circuit breaker which that place approximately under the wire for the R/phase

We feel the presence of electricity and we can not touch the door knowing that the

door grounded.

best regards

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #11

Re: Intensity of the Magnetic Field

08/03/2014 7:12 PM

That is a totally different problem, your cabinet is not properly bonded and/or grounded, you are feeling what is known as "touch" or "step" potential.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #4

Re: Intensity of the Magnetic Field

07/31/2014 11:27 PM

Does the measured value of magnetic field include that(how much) of the earth?.

__________________
pnaban
Register to Reply
Register to Reply 12 comments