Can any one help for steps for calculate asymmetrical short circuit calculation for a 3 phase system?
Re: Calculation
08/10/2014 5:52 AM
Yes. Loads of people can.
Good moaning!
Good Answers: 445
Re: Calculation
08/10/2014 11:01 AM
This is a very good first step until you get your EE degree in power engineering.
Re: Calculation
08/10/2014 11:10 PM
i just wanted to calculate asymmetric short circuit inside a panel .If you don't know don't comment again ok.
Reply Off Topic (Score 4)
Good Answers: 445
Re: Calculation
08/11/2014 3:26 PM
0
Good Answers: 445
Re: Calculation
08/11/2014 3:29 PM
Your question indicates that you're the one that doesn't know that it is not formula-based and requires detailed knowledge of the system and its components.
If I told you to take the reciprocal of X"d and add it to the reciprocal of Xs would you know where to get the data and what to do with it? Indicate a scrap of knowledge from the degree that you bought and you might get some help.
Re: Calculation
08/14/2014 8:29 PM
Hire a electrical consultants to do it for you. Your question show that you did even know what is asymmetrical short circuit. There is no information on what you are asking.
Re: Calculation
08/18/2014 2:52 AM
1.Asymmetrical Short Circuit Current
Short circuit current normally takes on an asymmetrical Characteristic during the first few cycles of duration [4]. The asymmetrical short circuit current for the High Voltage (HV) and the Low Voltage (LV) windings are calculated
= .................. (1)
Where,
Iph = Rated Phase Current
R = % Resistance
X =% Reactance
Ez = Per unit impedance
R/X = 0.6/6.222 = 0.0965
For HV Winding =
Isc = 894.2 A
For LV Winding =, where π = 3.141
Isc = 82089.5 A
Good Answers: 170
Re: Calculation
08/24/2014 5:32 AM
Refer IEC 60909
Re: Calculation
10/09/2014 2:12 PM
Hi!
I think that it is quite complicated to show you the details of calculating asymmetrical short circuit currents for a three phase system. However, I can tell you that the calculation is done based on the method of symmetrical components. The fault becomes more complex depending on the scale of the power systems. In the case of a power network containing hundreds of buses, you are even unable to calculate short-circuit by hand. So, you have to use a software to do this. To understand more on short-circuit calculation, you can refer to this link http://www.psa-outline.com/fault-anlysis/
Good luck!