Bundling Control Cables Together

08/11/2014 5:40 PM

What are your preferred methods for tieing control cables together so that they can be easily routed through cable trays.

I have a large number of cable bundles to build up. Each bundle averages 350 ft in length and consists of three cables (two are ~3/8-inch and one is ~1/4-inch).

The bundles will be rolled up after securing them together for storage, prior to installation. The bundles originate from a common location, but are routed to a large number (>150) of separate locations through cable trays and short runs through the air.

We have typically tied the three control cables together with waxed line every ten feet and breakage in use is rare, however it is labor intensive to install. Cable ties are an alternative, but the resultant size and sharp edges make them a little difficult and risky to handle.

What are the alternatives that you've used? I would appreciate your responses.

Thanks.

Register to Reply
Pathfinder Tags: bundle cable-tie
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Bundling Control Cables Together

08/11/2014 6:13 PM

Never did this myself, but.........................it's cheap and quick and permanent.

If you can get over the name: hog rings.

Just a thought, outside the tray.

Register to Reply
Power-User
Engineering Fields - Control Engineering - Newby Member Long Time User Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jun 2006
Posts: 224
Good Answers: 9
#2
In reply to #1

Re: Bundling Control Cables Together

08/11/2014 6:23 PM

That's a thought (the name doesn't bother me). I'll keep looking through the images on google. Haven't seen any yet that involve cables.

The images do show some applications with elastic cord and it appears to rely on pinching for that use.

If that holds true, it wouldn't work for control cable that can't have the jackets pinched, although larger rings might just work. I'll keep looking.

Does anyone have experience using hog rings with control cables?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Bundling Control Cables Together

08/11/2014 6:28 PM

Hey, don't blame me if people laugh at you.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Bundling Control Cables Together

08/11/2014 6:41 PM

BD, Your observation is correct, metal hog rings won't flex enough to prevent cable damage as your roll and unroll your cable sets, especially if you pull them instead of laying them in the trays. Properly sized and tightened tie-wraps should work fine unless you're dragging the entire length through multiple twists and turns of the tray.

You might want to consult with a few manufacturers to select the best material/size for your requirements.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Bundling Control Cables Together

08/11/2014 7:39 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Control Engineering - Newby Member Long Time User Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jun 2006
Posts: 224
Good Answers: 9
#9
In reply to #5

Re: Bundling Control Cables Together

08/12/2014 9:47 AM

Awesome suggestion.

I'm going to hunt these down and get some samples.

Thanks much.

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#12
In reply to #9

Re: Bundling Control Cables Together

08/13/2014 6:32 AM

These cable clamps are very popular and reliable. Cost wise also quite cheap. They are available everywhere, if you have any problem then they can be supplied from India. You need not hunt for them.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Power-User

Join Date: Jul 2014
Location: Savannah, GA. The post office decided to change my address again.
Posts: 253
Good Answers: 19
#6

Re: Bundling Control Cables Together

08/11/2014 7:42 PM

Might I suggest short pieces of spiral wrap wire loom? comes in multiple sizes, cut to 3 or 4 inch lengths, does not crimp and it pulls easily if it wraps tight enough to hold the cables.

__________________
Never seem more learned than the people you are with. Wear your learning like a pocket watch and keep it hidden. Do not pull it out to count the hours, but give the time when you are asked.(Lord Chesterfield)
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Bundling Control Cables Together

08/12/2014 4:02 AM

How much time does it take to uncoil the three cores, bind, recoil and finally uncoil them again for installation compared to installing the three cores straight off the drum?

There must be a reason for what you are doing.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
3
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#8

Re: Bundling Control Cables Together

08/12/2014 8:49 AM

Try good old black insulating tape, it is labor intensive but will stay there for at least a couple decades.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#14
In reply to #8

Re: Bundling Control Cables Together

08/13/2014 8:15 AM

Yeah, but...if you have a light colored cable, say yellow PVC, which is a common color and insulation for signal cables, after the black tape is on a while, if you ever have to remove it, you are left with a black goo on the cable that is very difficult to remove. Maybe that doesn't apply here or is of no concern, but I know in the world of sanitary installations, it is not allowed. Just a warning in case.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#10

Re: Bundling Control Cables Together

08/13/2014 2:15 AM

Shrinkable tubings are a good choice for your application. They come in different colors and sizes. Colors that are normally used for marking or color coding the bundled cables. Made of Teflon tubings that can be cut to the desired length. Control cables are pre-inserted through the tubings, then heated using heat gun to shrink to the desired size of the bundled cables.

__________________
vsar
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#11

Re: Bundling Control Cables Together

08/13/2014 4:39 AM

I have used a plastic bag sealer for this type of application (Up to 700x 4x 4mm diameter cable bundles from 30m to 200m long for strain gauge sensor wiring used in on-board ship loading systems). The model we used was a Tachit™ E-9 but there are plenty of other manufacturers on the market. As well as wrapping the cables it produces a ½" soft tag that accepts marker pen so you can write routing information at the ends and at junction points along the route. Because it is a sticky tape you can line up the cables like a ribbon cable making them neat and easy to lay on the tray. The wraps are not a long term solution (max 1-2 months) but this should not be a problem if you are fixing to the cable trays. Each wrap takes about 1 second to apply so we wrapped every 1.5m (one arm span of the operator). We also used a cable length meter so that we knew where to cut and where to mark the tags at tray junctions. Checking back on old records, we allocated 5 minutes for a 50m bundle, wrapped, marked, with number ferrules to each end of each cable and one end fitted with crimped terminals (24 cores total using a powered semi-automatic strip/crimp tool), and the operators made bonus.

Tachit also sell a "defined cut to length tape dispenser that would work with standard electrical tape. Quicker than cutting tape with a kraft knife but you still need to hand wrap.

Register to Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#13

Re: Bundling Control Cables Together

08/13/2014 7:10 AM

I haven't tried them, but Igus has little plastic chain looking things "energy chain" that is supposed to hold cables and be able to move as well.

I had a sample piece of one. Looked pretty good.

http://www.igus.com/energychains

http://www.igus.com/wpck/4843/about_energy_chain_cable_carriers

What I have used a lot of is: band wraps, braided harness, or split tube / split loom. All of those work well enough for the applications I work on, and they are fairly low cost.

Register to Reply
Participant

Join Date: Apr 2014
Posts: 3
Good Answers: 1
#15

Re: Bundling Control Cables Together

08/13/2014 4:01 PM

Take the wires you have and stretch them out straight. Have a friend hold one end and put the other end in a electric drill. Twist them together with the drill.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Oct 2010
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Posts: 159
Good Answers: 4
#16

Re: Bundling Control Cables Together

08/13/2014 5:42 PM

Have you looked at cable lacing, this is old school but effective method before zip ties. http://en.wikipedia.org/wiki/Cable_lacing Google cable lacing for more info.

Register to Reply Score 1 for Good Answer
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!