Generator Voltage

08/19/2014 3:14 AM

We have existing generator, distribution system, load at 380V. Then we have to replace with new generator 400V. Is it better to use 380V or 400V?

Can generator voltage to be changed to 380V?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Generator Voltage

08/19/2014 4:29 AM

As you claim that you have to replace at 400V, the question of which is better does not arise, Mildred.

__________________
Good moaning!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Generator Voltage

08/19/2014 4:42 AM

See that little knob over there? Turn it a smidge to the left.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Generator Voltage

08/19/2014 7:32 AM

Maybe. It depends on a lot of things you seem to not know or at least will not freely tell us. A 5% difference in voltage might be on the tolerance edge for some loads so any momentary over-voltage spike might now be too much. An autotransformer with multiple taps could be used to step this down a little bit but depending on your actual unknown equipment this can easily not be needed.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Generator Voltage

08/19/2014 7:59 AM

This may come as a silly question, why not buy the correct generator? If you have equipment failures any warranty you have may become null and void.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Jun 2014
Posts: 6
#9
In reply to #4

Re: Generator Voltage

08/20/2014 3:15 PM

Actually, this is not a "new" buy, but it was from other site.

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#5

Re: Generator Voltage

08/20/2014 12:12 AM

Look at the nameplates on the loaded equipment. Are they actually 380 volts? If so the 400 will be within the tolerance for electrical equipment, and the actual voltage by the time you get from the generator to the actual equipment under load will have some voltage drop anyway. I don't see a problem. I assume the generator is an extremely small one, or else it would have an adjustment for voltage output level of about + or - 10%.

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#6

Re: Generator Voltage

08/20/2014 1:09 AM

Give complete details of the generator. Like power,(KVA), speed, exciter reserve available etc. Generating lower voltage at rated speed may saturate magnetic circuit, for the same load, load current would be higher. If you reduce the speed for lower voltage to maintain the saturation, generator cooling may get affected.So unless completed details are given, no guidance can be provided. Best is ask generator manufacturer

Register to Reply
Participant

Join Date: Oct 2013
Posts: 3
#7

Re: Generator Voltage

08/20/2014 5:17 AM

Electrical appliances have a range of voltages they work with, if you were using 380V, the source can range from 380 to 415V your new generator is good enough provided the KVA rating is the same as the old one, if the the new one has less KVA, it could be overloaded

Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#8

Re: Generator Voltage

08/20/2014 8:27 AM

Any voltage can be specified for any system, but most use the voltages that are readily available from an outside source.

As for adjusting the voltage, if you have selected a replacement unit, contact the manufacturer or refer to the manual that should accompany the replacement, it may have the info you need, and if not, the manufacturer certainly should have the info.

__________________
Never stop learning
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10

Re: Generator Voltage

08/20/2014 6:56 PM

"Existing generator" is a very vague term.

As such,expect very vague answers.

To give a better answer,provide better information, such as KVA of the generator,frequency of the output,etc.

A copy of the data plate would be helpful.

Also a description of the loads applied would be beneficial,whether inductive(motors) resistive(heaters),Switch mode power supplies,(UPS,computers,etc.)

We are all willing to help, but shooting in the dark is not likely to hit the bulls eye.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

4wsilver (1); Crabtree (1); HiTekRedNek (1); Kevin LaPaire (1); pcchatur (1); redfred (1); satriatengger (1); TonyS (1); Tornado (1); Xtreme (1)

Previous in Forum: Alternator Unable To Supply Power To Welding Machine   Next in Forum: ETAP Training on Skype

Advertisement