Vacuum Pressure Transmitter

07/03/2007 4:32 AM

Can we install the differential pressure transmitter for vacuum measurement.

Also VFD is for variable frequency drive and what will be for VVFD.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: VACUME PRESSURE TRANSMITTER

07/03/2007 8:49 AM

VVFD is an undefined acronym.

Reply
Commentator

Join Date: Jun 2007
Location: Colorado, USA
Posts: 91
Good Answers: 1
#2

Re: Vacuum Pressure Transmitter

07/03/2007 10:59 PM

How about video/voice/fax/data

for the first, I don't see why not. You just have to find the proper equipment for the application. So long as there is a difference in pressure and vacuum is an absence of pressure,, you can use a differential pressure transmitter. or am I way off base here?

__________________
Home is where the heart is!
Reply
Power-User

Join Date: Jan 2007
Location: Berlin (Germany)
Posts: 332
Good Answers: 1
#3
In reply to #2

Re: Vacuum Pressure Transmitter

07/04/2007 5:23 AM

1. If you put one of the difference inputs on vacuum and seal it, you get a direct vacuum transducer.

2. If you leave it open (=ambient pressure) you have to measure the ambient pressure, too, to get an idea of the vaccuum (indirect transducer).
Uwe

__________________
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Reply
Anonymous Poster
#4

Re: Vacuum Pressure Transmitter

07/04/2007 7:37 AM

VVFD is veriable voltagae veriable frequency drive.

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5
In reply to #4

Re: Vacuum Pressure Transmitter

07/04/2007 9:53 PM

I believe that all models of AC variable frequency drives being marketed at this time include variable voltage, because motor design requires that the voltage and frequency remain in a (nearly) fixed ratio. Thus, a motor with a name plate rating of 480V at 60Hz can be safely operated at 400V and 50Hz, with derating only for horsepower output because of the slower speed. The algorithms which are used to form the drive output choose spacings between the pulses as well as pulse widths to increase or decrease the voltage as the frequency increases or decreases, in addition to changing the voltage continuously to create the sinusoidal waveform.

If you are speaking of a change in drive input voltage, this is much more of a problem, because their setup parameters usually require the internal DC voltage bus to remain between a high and low limit or else the drive will fault out. With some brands of drives and with factory assistance, one may be able to change internal parameters to reduce these settings (to correspond to a reduced input voltage for the same piece of equipment), but you generally cannot increase them because the electronic components would have dielectric failure.

-JMM

Reply
Anonymous Poster
#6

Re: Vacuum Pressure Transmitter

07/05/2007 1:36 PM

Guest,

Sure! We utilize a differential pressure transmitter to determine our vacuum pressure in a vacuum furnace application. Check out the following link. This is what we use to read from ATM to full vacuum. Very reliable.

http://www.omega.com/pptst/Px305.html

Hope this helps.