Why Electric Power Decrease in Thermal Power Plant When Heater Out of Service?

08/22/2014 9:01 AM

my question is that

Many heaters use for improve thermal efficiency in thermal power plant.if any one heater out of service electric power and thermal power should be decrease.please tell me reason why thermal power decrease?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#1

Re: Why Electric Power Decrease in Thermal Power Plant When Heater Out of Service?

08/22/2014 2:18 PM

Please try to use better diction, you will get better answers.

If a closed feedwater heater is removed from service in an operating thermal electric power plant, more steam will be passed through the turbine. This will enable the generation of more power.

However, when the feedwater heater is removed from service, this will cause the plant heat rate to INCREASE, thereby causing the plant owner to pay mote for fuel.

Review the Rankine cycle.

It is all explained here:

http://en.wikipedia.org/wiki/Feedwater_heater.

What exactly do you mean by "thermal power" ?.... do you mean thermal efficiency ?

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Why Electric Power Decrease in Thermal Power Plant When Heater Out of Service?

08/23/2014 4:23 AM

Dear Mr.awaiscnpp

If the Feed Water Heater or De-Aerator, is taken out of service, even though the fuel supply and combustion remain same, the Enthalpy in the Feed Water is reduced while entering the Boiler for transforming to Steam. Hence the Steam Flow to the Turbine is reduced and hence the Electrical Power out put is reduced.

For example, in a 90 Tonne/Hr., 64 Kg/cm^2, 495 Deg.C Boiler, when the Feed Water Temp is reduced, from 120 Deg.C to 98 Deg.C,due to De-Aerator problem and taken out of service, Deg.C., 1 MW Power (Elec.Power Output) is Lost.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#3

Re: Why Electric Power Decrease in Thermal Power Plant When Heater Out of Service?

10/10/2014 5:47 PM

If you have been advised to reduce load by the manufacturer when taking a heater out of service it is in the interest of reducing bucket/blade loading because more steam can be forced through the turbine than it was originally designed to pass, thus higher load capability that may affect thrust, buckets and generator windings etc.

__________________
If you fail to follow through, you will fail.
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); MJCronin (1); otha (1)

Previous in Forum: Opening in Skirts of Pressure Vessel   Next in Forum: Why Nuclear Power Increase, When Cooling Water Temperature Increase?

Advertisement