Delta Wye Connection in Transformer

08/29/2014 4:01 PM

What happen in delta wye ungrounded transformer (primary is delta) if any one delta phase is broken. I am interested to know the behaviour of voltage on secondary wye connection.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: Regarding delta wye connection in transformer

08/29/2014 6:02 PM

If one of the delta primary phases (say phase A) is 0 volts, the voltage between the other phases and that dead phase are reduced by a factor 1/sqrt(3). So 2 of the secondary Y phases will have voltage reduced by this factor, and the difference in phase angle will no longer be 120 degrees. In the diagram, black is normal and red is situation with primary delta phase A grounded.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Aug 2014
Posts: 35
#3
In reply to #1

Re: Regarding delta wye connection in transformer

08/31/2014 6:25 AM

Can U please explain me from where u get the factor 1/sqroot3 as a reducing factor.Also I am mot clear if phase A is broken and its voltage become 0 in such case how we get the close delta phasee diagrame.Why not open delta ? Waiting for reply.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4
In reply to #3

Re: Regarding delta wye connection in transformer

08/31/2014 12:35 PM

1/sqrt(3) is the ratio: (red)AC/(black)AC. If you draw a vertical line through Black A, red A, to the base you have two triangles with the same base. The ratios of the hypotenuses is cos(60)/cos(30) = 1/sqrt(3).

If phase A were open there would only be current between B and C, so on the output only one phase would be present, phase BC. Phases AB and CA would be zero.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#6
In reply to #4

Re: Regarding delta wye connection in transformer

08/31/2014 11:29 PM

If phase A were open there would only be current between B and C, so on the output only one phase would be present, phase BC. Phases AB and CA would be zero.
Corrrection: The BC voltage would also go through the CA and AB windings. So the outputs CA and AB would be 1/2 magnitude and opposite in phase with the BC.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5
In reply to #3

Re: Regarding delta wye connection in transformer

08/31/2014 8:47 PM

1/sqrt(3) is the ratio: (red)CA/(black)CA, or (red)AB/(black)AB. If you draw a vertical line (blue) as shown, you have two triangles with the same base with angles at C of 30 and 60 degrees. The ratios of the hypotenuses is cos(60)/cos(30) = 1/sqrt(3). (cosine = adjacent/hypotenuse)

Register to Reply
Associate

Join Date: Aug 2014
Posts: 35
#7
In reply to #5

Re: Regarding delta wye connection in transformer

09/02/2014 3:15 AM

I like yr explaination it will be very helpful to me.

Thanks & Regards

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#2

Re: Regarding delta wye connection in transformer

08/30/2014 9:41 AM

Transformers main functionality is based solely on the winding "Turn Ratio" and "number of electromagnetic flux induced then cut or interrupted by its windings, while its rated capacity will mainly depend on the (AWG) size of magnet wire used and corresponding core size.

Therefore when one of the primary connections is broken, the net effect will be directly and proportionately reflected to the corresponding secondary winding(s).

__________________
vsar
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Delta Wye Connection in Transformer

09/04/2014 2:28 PM

Only 2 secondary phases, a and c, remain. The single-phase apparatus supplied from aN and cN will be supplied as usual. The bN supplied installation will be blackout.

Three-phase motor will not start but if it already started the current in phases a and c will be 73% more and the power produced by motor will be only 70% than when was three phases supplied [due to copper losses].See[also]:

IEEE Std 242-2001 ch. 10.3.3.2 Single phasing.

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Delta Wye Connection in Transformer

11/20/2024 6:55 AM

Is that before or after the appropriate circuit protective device has disconnected it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (1); PWSlack (1); Rixter (4); sensourabh (2); vsar (1)

Previous in Forum: Design of a Control Circuit   Next in Forum: SF6, ACB Working Principles and Comparison Between SF6 and Vacuum Circuit Breaker

Advertisement