Difference Between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 11:17 AM

What is the difference between a 3P+N (Tri-Poles + Neutral) and 4P (Tetra Poles) Circuit Breaker of 40A 400V (Curve D) in a three phase 4 wires connection type? What is the maximum current (Imax) per phase [Iph1, Iph2, Iph3 and I(Neutral)] in the 3P+N type and the [Iph1, Iph2, Iph3 and I(Neutral)] in the 4P type of the same rating as above? Where each type of the circuit breaker is recommended to use?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 11:45 AM

we dont do others homework here

Register to Reply
Associate

Join Date: May 2008
Location: Mauritius
Posts: 32
#2
In reply to #1

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 12:22 PM

It is surely not a homework question for your information.

May be for certain electricians it will be served as a revision or recapitulation lesson.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #2

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 4:33 PM

"It is surely not a homework question"

For some reason I don't bieve you.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7
In reply to #6

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 4:57 PM

nope

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15608
Good Answers: 983
#3

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 1:15 PM

Did you compare the datasheets from the manufacturers? I'm certain that they will be happy to explain what the difference (if any) is between these products. Once you locate these datasheets, if you need help in understanding a nuance difference then come back to us for an explanation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: May 2008
Location: Mauritius
Posts: 32
#4
In reply to #3

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 1:28 PM

The 3-Pole + N type has three similar CB of 40A plus one Isolator Switch as the 4th pole.

Whereas the 4-Pole type has four similar CB of 40A.

Make: MERLIN GERIN

CODE NO 21420: 3-POLE + N

CODE NO. 24621: 4-POLE

Register to Reply
2
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5

Re: Difference between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 1:36 PM

A1) The neutral current does not/does trip the device, respectively. How one gets more than 40A in the neutral is the question you didn't ask.

A2) 40A in both cases.

A3) Where it says so on the wiring diagram for the equipment you're considering putting each of them in, Boss.

__________________
Good moaning!
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Difference Between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/30/2014 10:14 PM

One thing that hasn't been mentioned.

4P break simultaneously where as TP+N the neutral is early make, late break.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #8

Re: Difference Between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/31/2014 12:04 AM

4P CB is generally used in incomer or changeover system.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #9

Re: Difference Between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

08/31/2014 2:19 PM

And ? ? ? ?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#11

Re: Difference Between a 3-POLES+N and 4POLES (CB 40A 400V) (Curve D) in 3PH+N Inst

09/02/2014 10:48 PM

The answer can be found in one of my previous comment here.

For convenient it is pasted again:

Type of breakers based on number of pole:

Based on the number of poles, the breakers are classified as

SP - Single Pole

SPN - Single Pole and Neutral

DP - Double pole

TP - Triple Pole

TPN - Triple Pole and Neutral

4P - Four Pole

The difference between TPN and 4P (or SPN and DP):

For TPN, protection applies to the current flow through only 3 poles; there is no protection for the current flow through the neutral pole. For the 4 pole breakers, protection applies to current flow through all poles. However when breaker trips or manually opened, all poles are disconnected.

Same type of difference also applies for SPN and DP.

Usage of TP, TPN and 4P in distribution panel:

For any distribution board, the protection system (either fuse and switch or breaker) must be used in the incomer. For a three phase distribution panel, either TP or TPN or 4P can be used as the incoming protection.

TP: It is most commonly used type in all ordinary cases.

TPN: It is generally used where there are dual sources of incomer to the panel (utility source and emergency generator source).

4P: It is used where is the possibility of high neutral current (due to unbalance loads and /or 3rd and multiple of 3rd harmonics current etc).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Crabtree (1); Fredski (2); joomunm (2); msamad (1); pnaban (1); redfred (1); TonyS (3)