Earthing In Motor Terminal & Body

09/03/2014 7:21 AM

We have earthed the terminal box of the motor with the cable from the respective feeder of the MCC room.. again I was asked to do earthing on both sides of the motor body.. my question is since we earthed motor terminal box already, why motor body earthing required..? Since motor terminal box and motor body are mechanically connected.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Earthing In Motor Terminal & Body

09/03/2014 8:01 AM

It is conceivable that the terminal box might work loose from vibration. But then, either earthing connection could also work loose. Maybe there should be 6 earthing connections, in case 5 of them work loose. Isn't contingency analysis fun?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Earthing In Motor Terminal & Body

09/03/2014 8:19 AM

redundancy just might save your life

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: Earthing In Motor Terminal & Body

09/03/2014 8:58 AM

Go back to the person who asked you, and ask "why?".

__________________
Good moaning!
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4
In reply to #3

Re: Earthing In Motor Terminal & Body

09/03/2014 9:09 AM

Or just do it and move on to something more productive.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5
In reply to #4

Re: Earthing In Motor Terminal & Body

09/03/2014 9:43 AM

Good point.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#6

Re: Earthing In Motor Terminal & Body

09/03/2014 9:44 AM

The feeder cable ground is there to protect equipment & personnel from exposure to an electrical ground fault in the cable between the switchgear and motor and also to provide an alternate path for the equipment ground.

The equipment ground (motor body) is there to protect equipment & personnel from exposure to an electrical fault in/at the motor and/or the equipment the motor is attached to.

If the cable ground is damaged or severed, and the equipment ground is intact and functional, the motor as well as whatever it is attached to will still have ground fault protection and personnel will also be protected.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Earthing In Motor Terminal & Body

09/03/2014 9:44 AM

Since you don't know why, how can you speculate about why not.

Just do it!

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#8

Re: Earthing In Motor Terminal & Body

09/03/2014 11:16 AM

The answer was in your question. The motor terminal box and motor body are mechanically connected.

The bonding is the electrical connection.

__________________
common knowledge...less common than common sense
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#9

Re: Earthing In Motor Terminal & Body

09/03/2014 11:35 PM

Is the terminal box insulated with a rubber gasket? Best to have as many earthings as you can to keep everyone safe.

__________________
"Real Bass Players" do not use picks
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#10

Re: Earthing In Motor Terminal & Body

09/04/2014 1:38 AM

Dear Mohsin,

Your question is relevant. The terminal box you earthed is fixed to body through bolts and has a gasket in between. The gasket is basically provided to make it environmentally protective and proper packing ... but this is electrical insulator. As far as bolts are concerned they may be 4-6 in number but are made of high resistance material normally. Therefore the earthing is demanded on motor body. I don't understand requirement of earthing on both sides of the body... One side .. I can understand. If there are items connected with screws and bolts on either side don't earth them, earth main motor body at the provision made and you may provide a copper strip/wire jumper to bolted parts. This meets Indian standard. You may check for standards if you are elsewhere. I am sure you will certainly agree that a human life saved is much -more costly and valuable than a motor and its earthings.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#11

Re: Earthing In Motor Terminal & Body

09/04/2014 3:39 AM

Blimey, could have done it by now.
Already this morning, I've mended the downstairs cistern... (leaking flap valve... it's my age)

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (2); Fredski (1); Jimh77 (1); lyn (1); M.R.Iyengar (1); SHOCKHISCAN (1); The.Tinkerer (1); Tornado (1); user-deleted-1105 (2)

Previous in Forum: Neutral Shifting   Next in Forum: 05 Vibe Base Motor Mounts?

Advertisement