LV Motor Over Load

09/06/2014 10:25 PM

Sir,

why LV motor got over load if i increase the voltage more than rated voltage

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: LV motor got over load

09/06/2014 11:01 PM

You have not stated what type of load you are driving with the motor, but like any physically realizable device it has limits, and you have exceeded them.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Jun 2012
Posts: 7
#6
In reply to #1

LV motor got over load

09/07/2014 11:02 AM

Rotary feeders, screw conveyors.

I am I having one scraper chain, which so long form load centre, aprox 1km and i getting voltage 400 to 410V, and while starting this chain conveyor it is taking very high load, voltage drop to 300V, to start this chain we have to increase the voltage form 440V.

This increase in voltage, trips the rotary feeders, screw conveyors at load centres MCC

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: LV motor got over load

09/06/2014 11:22 PM

This is nothing more than the electrical equivalent of Fudd's First Law.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#18
In reply to #2

Re: LV motor got over load

09/08/2014 1:26 PM

A web address just for that...now that's a good use of the internet.

__________________
common knowledge...less common than common sense
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: LV motor got over load

09/06/2014 11:36 PM

You overloaded it.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#4

Re: LV motor got over load

09/06/2014 11:36 PM

Dude, that's the design limits.

Wow, you're definitely fired, once your superiors find out what you're doing.

Try, something else.

Well now at least you know. Stay sober alright?

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Member

Join Date: Jun 2012
Posts: 7
#7
In reply to #4

Re: LV motor got over load

09/07/2014 11:05 AM

YES, I KNOW THAT IS DESIGN LIMIT. I AM ASKING WHY IT IS TRIP BY OVER LOAD.

Register to Reply Off Topic (Score 3)
2
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#9
In reply to #7

Re: LV motor got over load

09/07/2014 11:30 AM

Are you mad or what?

Let's go back to this simple Law V=IR (eyes on this)

for a free turning motor with out a load, imagine increasing (V) voltage since R (coil resistance) is fixed, what do you think will happen to (I) current? Since your winding coil is with limited current capacity (size, diameter of wire), it will heat up and compensate to the increase of no. of turns or revolution. Heating and over current in the safety feature of the motor with its limit, that will trip off your motor.

Get it now?

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#13
In reply to #7

Re: LV motor got over load

09/08/2014 6:14 AM

You have the answer...it is trip by overload because that is the design limit!

lim·itˈlimit/nounnoun: limit; plural noun: limits

  1. 1. a point or level beyond which something does not or may not extend or pass."the limits of presidential power"
    • the terminal point or boundary of an area or movement."the city limits"
      synonyms:boundary, border, bound, frontier, edge, demarcation line; Moreperimeter, outside, confine, periphery, margin, rim "the city limits"
    • the furthest extent of one's physical or mental endurance."Mary Ann tried everyone's patience to the limit"
      synonyms:utmost, breaking point, greatest extent More"resources are stretched to the limit"one's/the breaking point, the last straw; informalthe end, it, one's wits' end, one's/the max "I've reached my limit !"
  2. 2. a restriction on the size or amount of something permissible or possible."an age limit"
    synonyms:maximum, ceiling, limitation, upper limit; Morerestriction, check, control, restraint "a limit of 4,500 people"
    • a speed limit."a 30 mph limit"
    • (in card games) an agreed maximum stake or bet.
    • the maximum concentration of alcohol in the blood that the law allows in the driver of a motor vehicle.noun: legal limit; plural noun: legal limits"the risk of drinkers inadvertently going over the limit"
  3. 3. Mathematicsa point or value that a sequence, function, or sum of a series can be made to approach progressively, until it is as close to the point or value as desired.

verbverb: limit; 3rd person present: limits; past tense: limited; past participle: limited; gerund or present participle: limiting1. set or serve as a limit to."try to limit the amount you drink"

synonyms:

restrict, curb, cap, check, hold in check, restrain, put a brake on, freeze, regulate, control, govern, delimit "the pressure to limit costs"

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #4

Re: LV motor got over load

09/07/2014 11:27 AM

What worries me more is that management wants the OP to "fix" this.

"To hell with the equipment protection, get it running."

Unless you're taking enemy fire, run away from any boss that tells you this.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#10
In reply to #8

Re: LV motor got over load

09/07/2014 11:37 AM

I guess, he's running a destructive testing Redfred, must be from R&D department.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: LV motor got over load

09/07/2014 12:05 AM

According to IEC 60076-1 ch.7.3 Voltage and frequency variations during operation Figure 12 - Voltage and frequency limits for motors

if the frequency stays as rated then up to 5% increased voltage will not change the all other rated properties [current, torque, slip].Up 10% overvoltage it will be still permissible. After then the no-load current will rise very much [due magnetic core saturation].Also the winding insulation may be damaged if the overvoltage is very high.

However, you may increase the voltage increasing the frequency in the same time keeping the magnetic flux constant. Of course, the limit it is the insulation permissible voltage.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15
In reply to #5

Re: LV motor got over load

09/08/2014 9:19 AM

Sorry,I meant IEC 60034-1[IEC 60076-1 it is for power transformer standard!]

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: LV Motor Over Load

09/07/2014 11:32 PM

Try VFD

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: LV Motor Over Load

09/08/2014 5:48 AM

Because by doing that there is a risk of turning it from a motor to a convector heater, and it isn't designed to be a convector heater. So the overload device has prevented it from happening by disconnecting the power.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#14

Re: LV Motor Over Load

09/08/2014 6:46 AM

I think it has become a habit to beat around the bush in CR4. Calculate current value for the load ( which could be calculated based on normal voltage and current at that period. Then check the FLA rating of motor and also the setting of Over Load relay. You will come to to know the reason. Mostly at higher voltage current increases as motor parameters are mostly fixed. Set the OL relay to proper level within FLA.Beyond FLA motor windings may get damaged. This phenomenon may be commonly found on systems with substantial initial load.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16
In reply to #14

Re: LV Motor Over Load

09/08/2014 12:03 PM

I think it has become a habit to beat around the bush in CR4.

you noticed!!

Actually is called.. extracting the urine!!

While the whole purpose of the forum is to exchange experience and ideas, help those that are stuck and so on, it becomes open season when a post such as we have receivd from the OP, is either a wind up (can anyone be that stupid really?) or they should NEVER have left their job in McDonalds.

It is quite apparent by some of the questions posed that in many cases the OP knows the square of nothing in the subject matter related to the question, and is looking for someone to do his work and get him out of the merky mire!

Stick around.. it's gets better!! and if you think this is bad... wait until a 1st year electrical student asks us to do his homework...

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#20
In reply to #16

Re: LV Motor Over Load

09/09/2014 1:01 AM

Please look at the bottom line of my postings.

I have once strongly messaged about it.

Why cant we be strict enough - not to respond such queries or respond straight on face to refer text books or net search rather than beating around the bush ... I feeel facing head on shall be a better way.. you all may discuss if need be or let's start.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#17

Re: LV Motor Over Load

09/08/2014 12:57 PM

OK, aside from the regulatory issues and such, the CONCEPT behind it all is this;

An induction motor does the work of providing torque at a given speed, the result is called kW or HP, depending on where you are. In the course of fulfilling that basic function, there are deeper design elements that are involving the magnetics that take place inside of the motor stator and rotor, the stuff that turns the steel and copper into something other than a boat anchor.

In those magnetic details, a PORTION of the current that flows to the stator is creating the magnetic FLUX inside of the motor, the remainder is creating the TORQUE in the motor. The RATING of the motor is the optimum confluence of those issues without creating more heat in the motor than it can handle safely. If you increase the voltage, it begins to increase the FLUX producing current much faster than it increases the torque. So you begin to get less bang for your buck as we say here in the US, meaning less gain in performance than loss of efficiency. That translates to the fact that the added flux producing current is increasing the heat by virtue of more current flowing, but without a corresponding increase in output mechanical power, or at least not at anywhere near the same rate.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#19

Re: LV Motor Over Load

09/08/2014 4:00 PM

The feeder conductors are too small,causing excessive voltage drop at the scraper motor.

Increase the feeder conductor size to solve the problem.

Information needed will be:

FLA of motor,Locked Rotor Amps of Motor,Service Factor of Motor,Power Factor of Motor.

The designed voltage and frequency of the motor,and number of phases.

The available voltages at the Main Control Panel,1 Km away,and the available amps from the Main Control Panel.

The highest ambient temperature that the conductors will encounter,and how the conductors are routed,: Direct Buried underground,underground in conduit,or aerial span.

Provide ALL of this information, and I may be able to help you determine the best remedy.

The problem can not be effectively solved without all of this information.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#21

Re: LV Motor Over Load

09/12/2014 4:49 AM

As I understand, before the voltage was raised to 440 V it was a problem at start. In my opinion

the conveyor was overloaded or even locked and or the motor torque was wick to overcome the load. The starting torque is proportional with square of supplied [at motor terminals] voltage.

It seems to me at 440 V the start [ 325 V at the motor terminals- may be] was successful but after then at steady state the motor was still overloaded-this not due to overvoltage but the conveyor overload. In my opinion if you cannot discharge the conveyor you have to change the motor.

__________________
Julius
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#22

Re: LV Motor Over Load

09/13/2014 12:53 AM

Because, during the high voltage , motor to draw excessive current to magentize the iron beyond the point where magnetizing is practical.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#23

Re: LV Motor Over Load

09/14/2014 12:20 PM

Sorry, 6% overvoltage it is not overvoltage at all. Since it is an induction motor the current will be less 6% at such "overvoltage" [not more 20%- in order to start an overload relay].

__________________
Julius
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: