Previous in Forum: Motor Circuit Breaker Rating   Next in Forum: Inrush Restraint in Differential Protection
Ascertain the Continuity of Earth Grid and Lightning Grid
09/11/2014 11:56 PM
dear all
we have a cable riser from earth grid and another cable riser from dedicated earth rod FOR LIGHTNING PIT both are burried underground when we check the continuity with multimeter we found it to be continious but when we change the lead of meter we find resistance value
on checking the same with meggar we find it to be dead short continious
pls explain this phenomenon as we doubt that both grids HAS BEEN conECTED
is there any other method to ascertain whether both the grids are connected or discontinious underground
regards
Good Answers: 445
Re: ascertain the continuity of earth grid and lightning grid
09/12/2014 12:25 AM
A dead short reading from the Megger is to be expected, after all it is used to check insulation integrity not continuity. More than likely you're using a digital multimeter, they're notoriously bad when there's any chance that some form of stray current/voltage is in/on the circuit your testing.
Either get a low ohm continuity tester or an old analog meter for your test kit.
Re: Ascertain the Continuity of Earth Grid and Lightning Grid
09/12/2014 2:18 PM
Use of Meggar to measure continuity or resistance is a wrong application of right device. The word "meggar" has become common place and even non-electrical engineers use it very frequently. A meggar can measure only insulation resistance (healthiness of insulation). It has nothing to do with grid resistance. Use 3 electrode method or 4 electrode method. Refer IS-3043
Good Answers: 122
09/12/2014 3:59 PM
You really should consider purchasing a ground grid test system that is capable of utilizing a time domain controller to identify grid conductor length, continuity, and condition.
There are several available and an internet search on ground grid testingwill yield a wealth of information.
09/13/2014 4:48 AM
Modern digital meters are designed to have a very high input impedance,and a very
low sensing voltage when measuring resistance.
The high input impedance also makes them susceptible to very minute voltages interfering with an ohm reading.
What do you mean "change the lead on the meter?"
Are you changing the range of the reading?
What value resistance are you reading on the meter?
Some meters can read a very low resistance,so check the range setting on the meter.