In our plant 5MVA and above rated Transformers are having Low impedance Differential protection (Schneider P632 relay) with 2nd harmonic restraint during TRF energization (setting:>20%) feature. It has been observed that during a TRF energization under stable power system condition the TRF charging current is more than 2 times of TRF FLC and 2nd harmonic component is also significant (much higher than 20% of fundamental) and transformer is successfully charged.
But after a grid failure condition, when power resumes from grid (the 11KV distribution system with a wide cable network and approximately 300 nos of TRFs are energized simoultaneously) the TRF charging current is very low 0.1 to 0.2 times of TRF FLC and 2nd harmonic component varies between 5% to 40% of of fundamental and the TRFs are tripping on differential protection.
What could be the cause of such behaviour & how to overcome the situation?