Inrush Restraint in Differential Protection

09/12/2014 3:04 AM

In our plant 5MVA and above rated Transformers are having Low impedance Differential protection (Schneider P632 relay) with 2nd harmonic restraint during TRF energization (setting:>20%) feature. It has been observed that during a TRF energization under stable power system condition the TRF charging current is more than 2 times of TRF FLC and 2nd harmonic component is also significant (much higher than 20% of fundamental) and transformer is successfully charged.

But after a grid failure condition, when power resumes from grid (the 11KV distribution system with a wide cable network and approximately 300 nos of TRFs are energized simoultaneously) the TRF charging current is very low 0.1 to 0.2 times of TRF FLC and 2nd harmonic component varies between 5% to 40% of of fundamental and the TRFs are tripping on differential protection.

What could be the cause of such behaviour & how to overcome the situation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: Inrush Restraint in Differential Protection

09/12/2014 3:48 PM

What is the voltage level during these conditions?

More than likely the electrical system is suffering a severe voltage drop due to being overloaded by the equipment inrush current.

1. I suggest that you look closely at harmonic filter configuration, inductors, capacitors, and whatever other power factor correction devices present in your system.

2. I suggest that you install low-voltage tripping protection on all equipment & transformers so that all of the equipment/transformers trip off line from the grid when a failure occurs.

3. I also suggest you selectively energize your plant equipment in an orderly sequence so that all of the transformers are not being energized at the same time. This can be accomplished manually by adopting a switching program or by installing a PLC or DCS system with proper programming that prioritizes equipment start sequence position and timing.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#2

Re: Inrush Restraint in Differential Protection

09/13/2014 12:17 AM

Did it energize on Load or without Load?

Register to Reply
Participant

Join Date: Sep 2014
Posts: 4
#5
In reply to #2

Re: Inrush Restraint in Differential Protection

09/13/2014 5:49 AM

All the 300 odd TRFs are always energized without load only.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Inrush Restraint in Differential Protection

09/13/2014 3:35 AM

More clarity is required.

Which transformer trips? 5MVA or 300 transformers. The inrush current will be 8 to 10 times full load current. How many differential relays are there and how many tripping ?Are these tripping due to differential relay operation or for some other fault.

Please clarify so that appropriate solution can be suggested.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Participant

Join Date: Sep 2014
Posts: 4
#4
In reply to #3

Re: Inrush Restraint in Differential Protection

09/13/2014 5:47 AM

During mass energization of all the 300 odd TRFs, some or all (14nos) the transformers with differential protection trip on differential protection only. It has been observed (from relay disturbance recordings) that on these instances (mass energization) TRF energization current is not exceeding 0.2 to 0.3 FLC with very low 2nd harmonic component whereas in normal energization TRF energization current is >2X FLC and the 2nd harmonic component is also much higher than 20% of fundamental.

All the 300 odd TRFs are always energized in OFF LOADed condition.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6
In reply to #4

Re: Inrush Restraint in Differential Protection

09/13/2014 6:32 AM

some link is missing.

What will be rating of each of the transformer.

How is that on 5 MVA system you have connected 300 and Odd Transformers. Even if you take 14 transformers (as given by you) into consideration of 1 MVA rating , the total capacity will be 14 MVA.Generally Differential relays are provided for rating 2.5 MVA and above.

Another point is for any transformer the inrush current will not be less than 100%.

I have a feeling most of the information furnished by you are not in order, some where some important information is missing. This is my opinion

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: Inrush Restraint in Differential Protection

09/13/2014 6:36 AM

Sorry I misunderstood as 5 MVA total plant Capacity. My apologies to you.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #7

Re: Inrush Restraint in Differential Protection

09/13/2014 6:41 AM

Please check the voltage monitoring of these relays. Can you please share the SLDand relay setting details.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Participant

Join Date: Sep 2014
Posts: 4
#9
In reply to #6

Re: Inrush Restraint in Differential Protection

09/13/2014 7:08 AM

1)We have a 132KV GRID incomer connected to 132 KV bus to which 4nos (2X26.5MVA, 2X37.5MVA, 132/11KV) power TRFs connected. To the 11KV system along with these power TRFs 4 nos of TGs (18.5MW each) are also connected.

2) The total plant load is 80MW out of which 45-50 MW is provided by the TGs and the rest by GRID.

3) The total plant load is catered by 300 odd distribution TRFs of various ratings (12.5MVA/5MVA/3.15MVA/2MVA/1.6MVA/1.25MVA etc). The TRF of more than 5MVA capacity (14 nos out of 300 odd) are equipped with DIFF protection.

4) In case of Grid failure the TGs also collapse in some cases before Islanding & load shedding takes place. In such cases the 11KV CBs of distribution TRFs remains ON & on resumption of GRID supply all the TRFs are charged simoultaneously. In such cases we are facing the typical problem.

5) In case the Islanding & load shedding is successful the 11KV CBs of the TRFs (with DIFF protection) trip and on power resumption they are closed one by one. In such cases the TRFs close successfully.

5) I am also aware that TRF magnetizing current can't be below 100% of FLC. The same also occurs in case of charging of individual TRFs ( observed from relay disturbance recordings) . But in case of DIFF tripping (in 14 nos of TRFs) during GRID resumption the relay disturbance records show magetizing current less than FLC and very low 2nd harmonic magnitude due to which harmonic restraint of DIFF protection fails to act.

6) The relays have been tested to be working perfectly ok with OMICRON relay test kit CMC356.

7) Although the DIFF relays installed (P632) are having 2 Phase voltage input (used for overfluxing protection & for voltage display purpose) the is no provision of any voltage based protection in them.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#10
In reply to #9

Re: Inrush Restraint in Differential Protection

09/13/2014 9:31 AM

Differential current setting of 20% seems to be slightly less. You can try to set it at 30-35% and try .Similarly slightly increase the setting of trip time. Different manufacturer of relays recommend different settings,ABB recommends min settings of 35%

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanvaderi (1); rahul_123 (3); ramvinod (5); SHOCKHISCAN (1)

Previous in Forum: Ascertain the Continuity of Earth Grid and Lightning Grid   Next in Forum: Electrical Questions

Advertisement