dear all what is the concerns about connection of IEC motors and disconnect switches to NEMA MCC, in fact i need your help to configure best practice to connect Equipment's from different standard?
You provide no useful information, and yet want the forum to provide you with a guide for, "best practice to connect Equipment's from different standard?"
Actually, a competent electrician could tell you most of what you want to know if you bought him a few beers at a local bar. There's not really many surprises if you know what you're doing.
I repeat what Lyn said, noting that it can be done.We work with several European design firms here and frequently get panels designed under the IEC. Usually a few mods are required, but not too much.
I will add that areas of difference that cause concern are, noting that some of them probably wont apply to your case:
1. Exposed equipment with an IP rating won't pass where a NEMA rating is required.
2. For fault calculations, look closely at SCCR ratings with IEC equipment, particularly with MPCB's. My experience with European equipment is that is less of an issue over there. It is quite common to get packaged equipment designed under IEC that only has a 3KA overall rating. (we change breakers or add fuses in European built panels to get a good rating quite often)
3. From what I can find, only NEMA rated breakers will be allowed for branch circuit protection, because all IEC rated breakers I've found are only rated UL 1077, not UL 489 so cannot be used as branch protection. (maybe some IEC breakers exist that are UL 489 - I just can't get them from the manufacturers I normally use)
4. Occasionally you get terminals on the IEC stuff that won't hold the required size wire in a system inspected under NEC. (IEC allows wire smaller than AWG 14 for low amperage AC equipment, so when space is a concern the terminals are reduced to hold what is required under IEC)
5. If doing a UL inspection, the IEC stuff has to also have a UL approval to be used. If not, you get into a complicated isolation transformer arrangement.
6. Some single phase IEC breakers will have a switched neutral. Allowed but not generally desired in a system under the NEC.
__________________
Remember when reading my post: (-1)^½ m (2)^½
Ok, this is good points to consider and actually close to what i'm asking about but still some points needed such like.
1-different voltage and frequency effect
2-tripping curves, protection schemes and short circuit level
· NEMA relay have a wider range: Safe trip is between 100 and 125%, while IEC relays trip between 105 and 120%. There is a risk of tripping too early or too late, which would be negative on the motor lifetime.
· NEMA does not recognize Ex-e protection. This means that
we cannot use Ex-e motors in the ATEX zones.
· For the protection of the IEC disconnect switch how to make sure that Nema C.B will provide the protection
3-MDP panel before MCC is needed or not which will add cost
4-Nema MCC Bus bars rating (Icw/time and ipeak - this needs to match a 2000kVA 6% transofmer,
5-is there any limitation with motor starts / starting[