The common discharge line of condensate extraction pumps 3x50%, pump design flow 357m3/hr, pump discharge pressure 27.3 bar a, pipe size DN350 has 3 pressure transmitters in a horizontal line whose tapping has been taken from top of the pipe. Is it correct? As usually it is preferred to take tapping in a condensate line in center or below centerline of the pipe. Some justly it by saying as it is a discharge line the flow is turbulent not laminar and this tapping is justified for measuring pressure.
Re: Pressure taps on pump discharge line on top of pipe
09/21/2014 10:45 AM
What do you say?
Re: Pressure Taps on Pump Discharge Line on Top of Pipe
09/22/2014 5:19 AM
I think the main issue would be to ensure that the line is liquid filled. If it is I do not see why having the pressure tappings on top, side or below would have any significant impact on pressure (the pressure change for height in a 350mm line is insignificant compared to the operating pressure). Provided the line is liquid filled (which it should be on a pump discharge) then you will see the same pressure all the way around the circumference. Instinctively I would expect to see the pressure tappings on top of the line but I cannot justify that comment with any reasoning.
I am not sure that the service has any significant impact but could you clarify the service
e.g. is it condensate from a steam system or hydrocarbon condensate?