4 Core Cable

09/27/2014 12:00 AM

Why using 4 core lt cable in 3 phase 3 wire system?We all know there is no neutral in 3 phase 3 wire system than what is the role of 4 core cable?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#1

Re: 4 core cable

09/27/2014 12:25 AM

What?

Register to Reply
Associate

Join Date: Aug 2014
Posts: 35
#4
In reply to #1

Re: 4 core cable

09/27/2014 12:49 AM

In a cable sizeing table there is used 4 core pvc cable for a 30kw ,415v, 62 A ,3 phase 3 wire connected motor feeder.Hence I got confused why using 4 core because systen having no neutral connection.Do u have a answere

Register to Reply
6
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: 4 core cable

09/27/2014 12:34 AM

Depending on if the cable is armoured or not the forth core can form the earth conductor (CPC). Some armours are of insufficient CSA to form an effective CPC therefore the forth core is used.
In the UK we have tables based on the circuit protection disconnection time and the adiabatic equation for such eventualities (they aren't to be found in BS7671 (before PWS mentions them)).

The above is based on you using a system that is referenced to earth.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 6)
Guru

Join Date: Feb 2008
Location: Van Nuys, CA
Posts: 563
Good Answers: 33
#3

Re: 4 core cable

09/27/2014 12:34 AM
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: 4 core cable

09/27/2014 3:04 AM

The 4th wire is to confuse the unknowing.

Register to Reply
4
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#6

Re: 4 core cable

09/27/2014 7:20 AM

It it to provide a medium for conduction for short in the motor. So that when someone touches the motor their body don't. Possibly taking them to their knees, taking their breath away, burning the area of conduction, causing heart failure and death.

In other words it is ground!

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Good Answer (Score 4)
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#7

Re: 4 Core Cable

09/27/2014 10:54 PM

I followed the link to Google and found an answer on the first item that was confusing. It was on a blog/forum and the first reply was that it was an earth, this was rebutted and the poster insisted it was a neutral to give 277v.

I know the fourth conductor as an earth wire ( green and yellow ). If a single phase 240v line is required a fifth conductor is included. We even have 5 pin plugs so that the one machine can have 415v for the motor and 240v for the control, lighting, switching etc. If multiple 240v devices are required then the load is shared between phases so as to not unbalance the 3ph lines. Our plugs and sockets are made so that a 10amp plug will fit into a 10 OR 20amp socket/outlet but not the other way round. Also a 4 pin plug will fit into a 5 pin outlet but not the other way.

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Dec 2009
Location: Karachi, Pakistan
Posts: 22
#8
In reply to #7

Re: 4 Core Cable

09/28/2014 1:19 AM

I agree with JIMRAT clarification.

__________________
Khawaja Raisuddin, Manager Project Technical
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#9

Re: 4 Core Cable

09/28/2014 4:18 AM

3 Phases and a neutral, (earth). Never has been anything else in all these years of dealing with cables for LV systems. MV, HV, EHV can be 3 phase conductors, or one.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10

Re: 4 Core Cable

09/28/2014 8:43 AM

The NEC and the CEC requires a GROUNDING conductor to be carried with all 3 phase circuits.

This is not to be confused with the GROUNDED (neutral) conductor.

If you do not know the difference, don't feel too bad,there are many experienced

electricians that still get the terms confused.

Google the terms for further explanation.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#11

Re: 4 Core Cable

09/28/2014 12:04 PM

Well, if the 3 phase motor is installed on a ship for instance, they can get away with just using a 3 core cable which surprised me, they can use the ship as an earth on AC systems and the same goes for DC systems If the DC system is rectified after passing through an isolating transformer as they are so dam strict on every other part of the electrical wiring on a ship. I only yesterday learned this, as a for the next month I am commissioning plant on a super Yacht (141 Meters) in Abu Dhabi.

So if it is not to be used on a ship, the forth core has to be the earth conductor.

Cheers

Joe

Register to Reply
Active Contributor

Join Date: Feb 2014
Posts: 24
#12

Re: 4 Core Cable

10/02/2014 12:35 AM

In fact U can use it for earthing, but in our case all the factories are rigged in 5 cores. Because many motors although 3 phase have single phase coils in their starters, thereby rq a neutral. And many electronics nowadays in the control panels.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#13

Re: 4 Core Cable

10/02/2014 4:45 AM

Do not confuse Neutral with Ground.

Or vice-versa.

Do not confuse GROUNDING with GROUNDED, or GROUND, as defined by the NEC

Google for the difference.

I cannot begin to tell you all that you need to know, but I can point you in the right

direction:

Dig a little,learn a lot.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Anonymous Poster #1
#14

Re: 4 Core Cable

10/18/2014 2:11 AM

I usually see power cables with 4 cores in LV system.

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: