10/03/2014 7:02 AM

3DB panel.3elcb.onetime1elcbtripped.few times another one.phase3

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Elcb tripping

10/03/2014 7:21 AM

Then you have a fault. You need to have an electrician investigate and remove the fault so that the things don't trip.

__________________
Good moaning!
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Elcb Tripping

10/03/2014 11:30 AM

Anothermember.ofthetextinggeneration.who.cannotadequately.4m.sentences.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: Elcb Tripping

10/03/2014 5:38 PM

They shouldn't be allowed to breed.

__________________
Good moaning!
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #2

Re: Elcb Tripping

10/03/2014 7:07 PM

im nt d o1 dat h8s smsthn

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: Elcb Tripping

10/03/2014 10:35 PM

ELCB tripped ? Well that is what it is for anyway isn't it ? raison d'etre

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Active Contributor

Join Date: Jun 2014
Posts: 19
Good Answers: 1
#6

Re: Elcb Tripping

10/04/2014 12:04 PM

Hi,

Nowadays ELCB/RCCB trippings are not necessarily caused by faults. Switched-mode-power-supplies (SMPS) commonly found in electronic equipment, for example, computers and the like, are inherently "leaky". They cause standing earth leakage currents even though such equipments may be perfectly healthy. Single phase ELCBs are "sensitized" by standing currents which reduce their threshold tripping current. On the other hand, 3-phase ELCB are desensitized by such standing earth leakage currents. Therefore, check that you do not have too many computers or other SMPS equipment connected to the single phase ELCB. As a matter of good practice, where possible, avoid using three phase DB & ELCB to supply single phase loads.

Regards.

Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#7
In reply to #6

Re: Elcb Tripping

10/04/2014 12:30 PM

Speculation. The original poster didn't say that.

__________________
Good moaning!
Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#8

Re: Elcb Tripping

10/05/2014 7:49 AM

Call an electrician or leave from the location.

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ade_jkrs (1); Alanvaderi (1); Crabtree (3); JRaef (1); kvsridhar (1); TonyS (1)

Previous in Forum: Voltage Regulators   Next in Forum: HV Motor

Advertisement