Hello,
I am working on a project to install VFDs on freezer evaporator units and have run into a situation where i have a calculated motor load factor over 300%! I am wondering if anyone might give me some ideas on how this is (or isnt) possible.
Some background info on the application:
The evaporator unit consists of a bank of 4 fans all on the same circuit. Each fan has a 0.5 HP motor. We are looking to install (1) VFD to control all (4) motors simultaneously. The temperature of the freezer space (where the fan motors are located) is about -5 degrees Fahrenheit (-20 Celsius).
My calculation process is summarized below:
I logged the amperage draw for two weeks at a sample rate of once every five minutes. I then calculated average amperage draw (obviously excluding any times the amperage draw was zero).
I then performed the load factor calculations as follows:
- Voltage = 480 V
- Assumed Power Factor = 0.9
- Average Amps when on (A) = 9.37
- Average Load (kW)= (Average Amps)*(RMS Voltage)*(Power Factor)*(3^0.5)/1000 = 6.99
- Theoretical load - 6 motors @ 0.5 HP (kW) = 6*0.5*0.746 = 2.238
- Load Factor = Average Load / Theoretical Load = 6.99/2.238 = 312%
Discussion:I spoke with the OEM and they confirmed the HP of the motors is indeed 0.5. I was informed that the fan motors will draw more amperage the colder they are. My question is whether or not it is possible for these motors to be drawing this much more amperage. If not, any ideas on what is going on here? Any help would be greatly appreciated.
Thanks for reading!
Good Answers: