Excessive Motor Load Factor In Freezer Space

10/06/2014 12:40 PM

Hello,

I am working on a project to install VFDs on freezer evaporator units and have run into a situation where i have a calculated motor load factor over 300%! I am wondering if anyone might give me some ideas on how this is (or isnt) possible.

Some background info on the application:

The evaporator unit consists of a bank of 4 fans all on the same circuit. Each fan has a 0.5 HP motor. We are looking to install (1) VFD to control all (4) motors simultaneously. The temperature of the freezer space (where the fan motors are located) is about -5 degrees Fahrenheit (-20 Celsius).

My calculation process is summarized below:

I logged the amperage draw for two weeks at a sample rate of once every five minutes. I then calculated average amperage draw (obviously excluding any times the amperage draw was zero).

I then performed the load factor calculations as follows:

  • Voltage = 480 V
  • Assumed Power Factor = 0.9
  • Average Amps when on (A) = 9.37
  • Average Load (kW)= (Average Amps)*(RMS Voltage)*(Power Factor)*(3^0.5)/1000 = 6.99
  • Theoretical load - 6 motors @ 0.5 HP (kW) = 6*0.5*0.746 = 2.238
  • Load Factor = Average Load / Theoretical Load = 6.99/2.238 = 312%

Discussion:I spoke with the OEM and they confirmed the HP of the motors is indeed 0.5. I was informed that the fan motors will draw more amperage the colder they are. My question is whether or not it is possible for these motors to be drawing this much more amperage. If not, any ideas on what is going on here? Any help would be greatly appreciated.
Thanks for reading!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Instrumentation Engineering - New Member Hobbies - Automotive Performance - New Member Technical Fields - Education - New Member Fans of Old Computers - TRS-80 - New Member Hobbies - Musician - New Member

Join Date: Jan 2008
Location: Tucson, AZ
Posts: 1331
Good Answers: 30
#1

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 12:53 PM

Look-up (1) copper-resistance change vs. temperature and (2) motor "cooling' (heat-dissipation) vs. temperature...should account for much of what you're seeing.

__________________
...and the Devil said: "...yes, but it's a DRY heat..!"
Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#5
In reply to #1

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 3:46 PM

Thank you. I will take a look into these issues

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 3:35 PM

a VFD o .5 hp? are you kidding?

Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#4
In reply to #2

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 3:44 PM

I am not kidding (Not a very funny joke had i been either). A single VFD controlling a bank of (4) 0.5 HP motors.

Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#3

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 3:40 PM

I am unsure of how to edit a post so I am just replying to my own post. The calculation should be as follows (i accidentally referenced a separate spreadsheet that was calculating savings for a different evaporator):

  • Voltage = 480 V
  • Assumed Power Factor = 0.9
  • Average Amps when on (A) = 4.76
  • Average Load (kW)= (Average Amps)*(RMS Voltage)*(Power Factor)*(3^0.5)/1000 = 3.55
  • Theoretical load - 4 motors @ 0.5 HP (kW) = 4*0.5*0.746 = 1.492
  • Load Factor = Average Load / Theoretical Load = 3.55/1.492 = 238%
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #3

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 7:54 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 3:55 PM

if speed control is the goal I'd switch to DC motorshttp://www.weg.net/ca/Products-Services/Drives/Payback-VFD-Calculator

Register to Reply
2
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#7

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 4:12 PM

You do have thermal overloads on each of the motors, don't you?

If not, your motors have no protection against overload.

__________________
paulusgnome
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#16
In reply to #7

Re: Excessive Motor Load Factor In Freezer Space

10/08/2014 9:07 AM

I understand the concept of having overload and short circuit protection when controlling multiple motors on a single VFD. Thank you though

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 5:57 PM

I always thought that electrical resistance went down with temperature....anyway starting these motors with a VFD will provide a gradual startup with low amp draw...Your equation seems to be starting all 4 motors on high speed....

http://www.automation.com/library/articles-white-papers/motor-drives-control/vfds-can-control-multiple-motors

http://www.ke2therm.com/files/W-2-1_More_Fans_or_Fewer.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Sep 2014
Posts: 10
#10

Re: Excessive Motor Load Factor In Freezer Space

10/06/2014 11:08 PM

I am not sure but I think the VFD is thinking it is looking at almost a dead short.

The VFD is going to calculate for six motors in parallel not series.

R Total = 1 / 1/R1 + 1/R2....etc.

For fire safety and motor protection you should use 1 VFD per motor. If speed

isn't a factor take a look at a fractional HP soft start such as Saftronics.

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11

Re: Excessive Motor Load Factor In Freezer Space

10/07/2014 12:48 AM

Please verify if the individual motors have thermal overload protection. (Small motors like this often do, but it is not a given.) What is the nameplate FLA on these?

Compared to room temperature air, cold air imposes a greater load on the motors. However, the cold air also cools the motor better than warm air. The second factor often outweighs the first, so that a 0.5hp motor can produce, say, 0.65hp. This may entail larger wiring and overcurrent devices, allow higher overload settings, etc.

Each installation needs specific study, with full information on components and temperatures.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Dec 2012
Location: Chennai, Tamil Nadu, India
Posts: 8
#12

Re: Excessive Motor Load Factor In Freezer Space

10/07/2014 3:32 AM

Where you have checked the current ( at motor terminal or supply end )

Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#15
In reply to #12

Re: Excessive Motor Load Factor In Freezer Space

10/08/2014 8:58 AM

We installed the data logger at the disconnect located at the MCC panel (maybe up to a few hundred feet from the evaporator). I am confident there are no other equipment on this circuit.

Register to Reply
Member

Join Date: Dec 2012
Location: Chennai, Tamil Nadu, India
Posts: 8
#21
In reply to #15

Re: Excessive Motor Load Factor In Freezer Space

10/09/2014 5:44 AM

So the location of current measured is after VFD . Then calculation based on supply voltage may lead to wrong results on the load calculations.You should have taken the voltage prevailed at the location of current measurement for power calculations

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#22
In reply to #21

Re: Excessive Motor Load Factor In Freezer Space

10/09/2014 7:11 AM

No, currently there is no VFD installed - see #19.

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#13

Re: Excessive Motor Load Factor In Freezer Space

10/07/2014 6:25 AM
  • Your electrical input power equals to Pin = U x I x sqrt (3) x Power factor = 480 x 4.76 x 1.73 x 0.9 = 3557 Watt.
  • Your mechanical output power for 4 motors equals to P out = 4 x 0.5 x 746 = 1492 Watt
  • Your efficiency is Pout / Pin = 1492/3557 = 42%

This means

  • a) you have very low efficiency motors
  • b) your motor has a larger mechanical loaded than the presumed 0.5 Hp. This is possible if the wind flow rate is much higher then it should be.
    • Are all the air ducts closed? (no false draught ?)

    • Can the fans work in serie? (the more flow rate, the more energy : P x V = m x R x T)
  • c) your current measurement is not correct. The current that takes a VFD is not a sinus wave, it can only be measured with a True RMS Amp meter
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#14
In reply to #13

Re: Excessive Motor Load Factor In Freezer Space

10/07/2014 6:59 AM

I think you've got it there.

Also 0.9 power factor is high for a 0.5 HP motor, my data says PF 0.7 and efficiency ~ 65%. Using that PF gives calculated efficiency 54%, not that far short of published figure. The difference could be covered by the other points you made.

__________________
Give masochists a fair crack of the whip
Register to Reply
Active Contributor

Join Date: Sep 2014
Posts: 10
#17

Re: Excessive Motor Load Factor In Freezer Space

10/08/2014 1:39 PM

I hope these help. Resistance in parallel loads is critical to a VFD. You will

still have to solve the problem of getting the VFD to function properly.

NEC Multiple Motor Load Calculations

Motor Load Factors

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18

Re: Excessive Motor Load Factor In Freezer Space

10/08/2014 2:14 PM

When measuring the input current to the VFD, which is the only valid external measurement here, you do NOT factor in the motor power factor, because the VFD is correcting it to .95 or better as far as the line source is concerned. This means that the amp draw on the INPUT of the VFD will be INCLUSIVE of the reactive current being used inside of the motors, making it read higher than what you would calculate on the OUTPUT side based on shaft loading. The Full Load Amps of a 460V 1/2HP motor is 1.1A at the most, likely less. If you have 4 motors, each drawing 1.1A, and each running at a .8PF, the input current to the VFD would be higher than 4.97A total; 4.4 / .8 = 5.5A total, meaning your motors are not even fully loaded. So there is that.

Also, if you are using a cheap multimeter to read the input current the accuracy is immediately suspect, because the cheaper the meter, the more it is going to be affected by harmonics, and the VFD creates a significant amount of harmonics. If you were reading the VFD amp output however, that's different.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#19
In reply to #18

Re: Excessive Motor Load Factor In Freezer Space

10/08/2014 2:32 PM

I don't believe i was clear on my description of the problem. There is currently no VFD installed on the fan motors. I am trying to measure baseline operating conditions of the motors so that i may estimate the energy savings once a VFD is installed.

Register to Reply
Active Contributor

Join Date: Sep 2014
Posts: 10
#20
In reply to #19

Re: Excessive Motor Load Factor In Freezer Space

10/08/2014 3:27 PM

Hi Max,

Maybe I can help a little more.

1. Copy all of the 4 or 6 motor name plate information. Each load could be slightly different, but probably not if you are just dealing with a fan motor.

2. Are these single or three phase motors? Are the compressors part of the fan circuit?

3. It is always a good practice to use Full Load Amps off the motor nameplate when calculating loads.

4. I seem to remember we used a recorder over a ten day period to get the best baseline demand readings. This should help smooth out voltage and temperature changes. Fluke makes a perfect high accuracy meter for this purpose.

5. There is several blogs on the Internet where others have used 1 VFD for multi-motor systems. You might invest some time in reading them.

Applying VFD's to Industrial Refrigeration

Hope this helps.

Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#23
In reply to #20

Re: Excessive Motor Load Factor In Freezer Space

10/09/2014 8:28 AM

Hi Keith,

1. I unfortunately do not have nameplate data. I have serial numbers of the equipment, contacted the OEM, and they confirmed the HP of the motors (at 0.5). I am experiencing the same excessive load factor problem on (3) different evaporators all logged independently (and with three different current transformers too!) and all on their own separate circuit.

2. These are three phase motors. The compressor is not part of the circuit.

3. Again, i do not have the name plate data.

4. I logged the motors for (2) full weeks.

5. I am confident that i will be able to control all the motors with (1) VFD. I have already done research into this and talked with a VFD manufacturer (Danfoss).

Thanks!

Register to Reply
Commentator

Join Date: Apr 2012
Posts: 63
Good Answers: 1
#24

Re: Excessive Motor Load Factor In Freezer Space

10/09/2014 10:52 AM

I spoke with another engineer from the OEM and they said that motors will draw significantly higher amperage when in cold temperatures (-10F). The load factors of 180%-250% did not surprise him. He said that we would need to oversize the VFD to account for the higher amperage draw.

Thanks to all who commented!

Register to Reply
Register to Reply 24 comments