Transformer Explodes!

10/07/2014 12:52 AM

this happened years ago and im justing repeating what i was told by eyewitnesses.

a 415v/ step-up to 11kv 50 hz transformer rated about 750 KVA was hooked up to

a backup generator.

the generator was in use before and so was the transformer.

the transformer was shut off to check its tap setting, but no changes were made in that tap setting or anything else. transformer was approx. 40 years old.

the generator got up to speed, an then its breaker was flipped on.

the transformer made a loud sound, "like it was being wound up."

then it visibly bulged and exploded.

most of our transformers are air and oil cooled, im gonna assume this one had no burkholz relay.

because of its making that loud noise, and because this happened at startup, im assuming this was out of control harmonic ringing. or insulation failure.

no, i wasnt there, im hearing this story from eyewitnesses years later.

please comment on the possible causes and what should have been done differently.

I would recommend:

1. bring the loads up more gradually, branch circuit by branch circuit.

2. always use a Burkholz relay

3. do insulation resistance test on transformers every ___ years after they are older than ten years.

4. am I missing something?

__________________
BSEE but always learning
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#1

Re: Transformer Explodes!

10/07/2014 8:00 AM

Wild guess:

Open circuit voltage from generator possibly quite a bit higher than loaded voltage making an arc across an insulation failure more likely. Once you draw the arc then you are at risk of molten metal dripping/flowing. At that point it's all over except for the fireworks.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Transformer Explodes!

10/07/2014 9:07 AM

Sounds more like the generator was out of syc with the 11KV line.

A Buchholtz unit may have minimised the effect but the damage had been done to the transformer by the time it operates. This also proves the value of pressure relief devices.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
3
Participant

Join Date: Oct 2014
Posts: 3
Good Answers: 1
#3

Re: Transformer Explodes!

10/07/2014 12:00 PM

Without more information on the whole arrangement and a post-mortem revision it is very difficult to diagnose this failure.

First, I'd like to think that the starting procedure was performed many times before, to rule-out wrong procedures.

BruceFlorida's response may be right, but we need to know what kind of generator was used; the off/on load voltaje difference may not be as high to create arching.

The out of sync suggestion by TonyS seems very probable, but the type (and condition) of transfer switch must be known.

One thing is true, the transformer was doomed the instant it was energized; the buchholz relay is usually used in oil cooled transformes to detect and release of pressure from internal gases formed by micro-arching and ionization on the oil, so if there was no relay, there's a high posibility that the transformar was of the dry type. Sometimes totally enclosed transformes are equipped with pressure relief devices to direct the explosion blast upward.

I'd suggest that since this was an old transformer, 40 yrs old, insulation may have degraded and this time it was stressed beyond capacity abd couldn't prevent a short on the coils.

About prevention:

1. If the transformer failed because of degraded insulation, it was just a matter of time for it to fail; inrush current is taken into account when designing the transformer and shouldn't be a problem.

2. There' not a need for a Buchholz relay if it is a dry tranformer.

3. Insulation tests must be performed regularly, the schedule must be commented with the transfromer designer. If you don't have technical information available, depending on the type of transformer and insulation used the frecuency and type of tests vary a lot.

if its paper/plastic based I'd suggest to test insulation at least every two years, comparing it with previous readings; degradation is very gradual but accelerates near its end of life; epoxy embedded transformers require longer periods for testing.

Oil based transformers require to check for insulation and oil condition. A sample of the oil is taken and sent to a laboratory to check for gasses and degradation.

Register to Reply Good Answer (Score 3)
Participant

Join Date: Oct 2014
Location: Venezuela
Posts: 2
#4

Re: Transformer Explodes!

10/07/2014 10:49 PM

I agree with dzenizo, as we don't have enough information to accurately explain why the transformer exploded under those specific conditions.

Yet, I wouldn't conclude that the equipment was indeed a dry-type transformer, only on the assumption that there was no Buchholz relay. I personally believe that the equipment could have been an oil cooled transformer, and it could have exploded even if it had a Buchholz relay installed. We have to remember that pressure gradients developed during low impedance faults are too fast for mechanical devices, therefore the importance of Pressure Relief Valves.

There was probably an arc across the coils, originated by the high transient current associated to the load connection to the generator. As BruceFlorida stated, perhaps the generator was out of sync (in terms of frequency and/or voltage magnitude). Evidently, the stress associated to the transient current combined with an insulation degradation due to the extended transformer lifetime, was a key condition for the arc to appear, and ultimately leading to a non prevention of a short circuit between the coils. Under these conditions, what I explained above could be a valid trigger for the explosion to happen.

Of course, we also have to consider the following question: Why didn't the main circuit breaker trip during the event? Two conditions may be considered: 1) The MCB was oversized for the short-circuit current of the transformer. 2) Event happened too quickly for the MCB to react. It has been proven that the best breaker technology trips in 50 ms, way too late to prevent an explosion. TP tests have also demonstrated that the first MJ in a low impedance failure produces 80ft3 of gas during the 1st ms.

Recommendations:

- Always use a coordination of protections using a Buchholz Relay and Pressure Relief Valves.

- Perform short-circuit studies and correctly calculate and coordinate all the protections associated to the system.

- Constantly check the transformer's insulation levels. The best recommendation for oil cooled transformers, is to extract oil samples and have them tested. This should be done at least once a year.

Best regards to you all.

Register to Reply Off Topic (Score 4)
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#5

Re: Transformer Explodes!

10/08/2014 3:20 AM

Nobody has yet mentioned water absorbtion by the oil. At that age it was probably a PCB oil. It is somewhat hygroscopic but I don't know just how much. The water could have boiled and made a lot of noise doing so. The resultant steam pressure would do the rest. Constant use may have prevented this.

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Participant

Join Date: Oct 2014
Posts: 3
Good Answers: 1
#6
In reply to #5

Re: Transformer Explodes!

10/08/2014 12:33 PM

Good point, buy as stated above:

"...the generator was in use before and so was the transformer..."

So it may be safe to assume the transformer wasn't turned off for a long time and was still warm.

The oppening of the service cover to check taps doesn't take too much time. Here I'm curious about why you have to check taps in the first time if everything was OK? And then they left taps untouched and closed the cover...

Another possibility may be sabotage...

Register to Reply
Anonymous Poster #1
#7

Re: Transformer Explodes!

10/15/2014 2:12 AM

I think that there could be an inrush current appearing in this situation, and because it's value was too high to cause the transformer damage. Furthermore, the protective devices could not tripped correctly, and the insulation of the transformer was aged since it has run for so many years.

Register to Reply
Register to Reply 7 comments