CTs for REF Protection for Distribution Transformers

10/07/2014 11:08 AM

I have to calculate the Knee point Voltage of the Cts required for a 1000KVA, 11KV/415 Volts transformer having 1600/5A Cts for the restricted earth fault protection using CAG14 relay and for a . If someone has sample calculations for similar ratings, it would be helpful.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#1

Re: CTs for REF protection for distribution transformers

10/07/2014 12:38 PM

Alstom will provide you the CT details. Or the LV switchgear manufacturer too

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: CTs for REF protection for distribution transformers

10/07/2014 12:43 PM

You did read page 10 of the Technical Manual didn't you?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Oct 2014
Location: Venezuela
Posts: 2
#3

Re: CTs for REF protection for distribution transformers

10/07/2014 1:10 PM

Good morning,

The minimum value of the Knee Point Voltage for a CT (Vk) is usually defined in its nameplate, under the denomination of Special Accuracy Class (Class X). It also imposes a maximum value of Rct (CT secondary winding resistance). Sometimes, it specifies the maximum value of the magnetising current Io at knee point voltage. Remember that the knee point voltage Vk is defined as the point on the CT's magnetising curve from which a 10% increase in voltage causes a 50% increase in the magnetising current Io.

Once you have this information, there are some calculations you can perform (according to your relay's technical specs), for you to verify that the Knee Point Voltage is not exceeded under load, short circuit and impulse conditions. I did some similar calculations for a Schneider Electric's overcurrent relay (SEPAM 100 LD), installed with interposed CTs in a 2 MVA Power Transformer. Let me know if you'd like me to send you these sheets.

Best regards from Venezuela.

Register to Reply
Member

Join Date: Oct 2014
Posts: 5
#4
In reply to #3

Re: CTs for REF protection for distribution transformers

10/08/2014 1:50 AM

Dear Sir,

Thanks for your message. I would welcome any calculations you might have done for the ref protection. Emailed Removed CR4 Admin

Regards,

S.K.Lamba