Onan Generator

10/08/2014 2:41 PM

I have an older Onan 30 kw generator. Pic of model and tag info attached. It is used to provide 480 volts to crushers and conveyors. We had a situation where one of the conveyor belts got stuck. Everything else that was running was shut down. Just as I got there I noticed smoke coming from the motor, they had not turn that motor off. Probably because the conveyor belt was not moving.

Though it was then turned off the damage was done. The motor was replaced but there was then no power to the circuit. The breaker in the generator had tripped. There was 480 at the switch, however when even the smallest load was applied the 480 disappeared. A sound like when something new is turned on would momentarily come from the generator and then no more power at the breaker.

Thinking it must be the breaker it was replaced. However, the same thing, any load and the 480 disappeared even at the breaker. My question is what could cause this and where would I look?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Onan generator

10/08/2014 2:53 PM

You have likely damaged a winding inside of the alternator, the electrical part of your generator. The other two work, and induce a voltage on the third that you can read on your meter, but as soon as there is a load, it cannot support it.

Time to call the Onan service tech.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2

Re: Onan generator

10/08/2014 2:53 PM

Does your generator have a regulator board?

It sounds like that could possibly be your problem.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#3

Re: Onan generator

10/08/2014 3:51 PM

Is this load shedding across all three phases? What are you reading phase to neutral for all phases?

__________________
CRTL-Z
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Onan generator

10/08/2014 3:57 PM

Time to do a little troubleshooting....

http://www.cumminsonan.com/www/pdf/manuals/943-0020.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#5
In reply to #4

Re: Onan generator

10/08/2014 4:13 PM

An example of a quality product. The YD's were among the best.

__________________
CRTL-Z
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Onan Generator

10/08/2014 9:04 PM

From your OP you say this is supplying crushers and conveyors. 30KVA seems very low for a duty that by its very nature is liable to overload.

To be honest, I think this last plant blockage has been the straw that broke the camels back.

RIP Onan generator.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#7

Re: Onan Generator

10/09/2014 4:43 AM

Once you've replaced the generator it seems you need to review and make immediate improvements to the way that overload and short circuit protective devices are coordinated across the facility, Mildred. If smoke has come out of a motor then something is seriously wrong that will, if unattended, make your fire insurance company very angry with you!

__________________
Good moaning!
Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#8

Re: Onan Generator

10/09/2014 6:42 AM

Looks like the overload at the conveyors wasn't seen and tripped early enough. Best to set overloads a s low as possible, just on the full load current of the motor so no chance of smoking. There are devices to detect over temperature which can be retrofitted and trip the starter before any fire.

The Onan Genset. There's coil on the rotor part which has brushes, this can be checked for continuity and insulation. Then the generator coils around the stator part, these may be starred at an inaccessible point or you may be able to separate the three windings and check each one. This will show if any windings have burned up, then you have to decide. Personally I'd go for a bigger set and scrap the old one so you have ample capacity in any future heavy loading which you do get in quarrying as stones get jammed. Depends what a shutdown is costing you.

Register to Reply
Guru

Join Date: Nov 2012
Posts: 633
Good Answers: 13
#9

Re: Onan Generator

10/09/2014 7:16 AM

"A sound like when something new is turned on would momentarily come from the generator and then no more power at the breaker." ????

Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#10
In reply to #9

Re: Onan Generator

10/09/2014 3:50 PM

I think he means the humming noise from a power source when you attach a heavy load; which in this case is not sustained due to generator failure ( likely burnt/loose connections or bad winding ).

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#11

Re: Onan Generator

10/09/2014 3:58 PM

Any odours from the generator winding ?, use a megger to check insulation and an ohmmeter to check winding resistance; look for charred wires and overheated signs at every connection terminal from the alternator, all the way to the loads.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Associate

Join Date: Jan 2009
Posts: 43
#12

Re: Onan Generator

10/09/2014 11:36 PM

Thanks everyone, I am heading to the mine early tomorrow and will check it out as best I can. Thanks SolarEagle for the manual it will certainly help.

Register to Reply
Associate

Join Date: Jan 2009
Posts: 43
#13
In reply to #12

Re: Onan Generator - now Kohler

10/11/2014 1:10 AM

I could not find anything that was obviously wrong with the Onan. For now I will set it aside and comeback to it when there is more time to troubleshot.

I also have a diesel 60 to 70 kw Kohler. However I'm having trouble starting it and then to provide the 480 v we need.

It has set for a while, more then a year without running. I am told that the magnetic field relating to the exciter may be dead or needs a 12 volt boost of some kind to get it going. I am totally out of my element here.

What I do know is there is a toggle prime switch that was momentarily held down and then you would push the starter switch until it started. You would need to push and hold it in for 30 to 60 seconds or more and then it would start and run. Until then no sound (except the operator complaining about holding in the switch).

Now there is no starting at all regardless of how many times and for how long the switch is held. I was able to start it by jumping the small solenoid in the control panel. Just a touch and it immediately roared into action. However, no 480 v produced. Across any two leads it showed only 12 volts and after 5 minutes it shut itself down.

There were 3 small fuses just inside the front of the generator cage but they read good. Should someone be able to provide some insight it would be greatly appreciated. Thanks again

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

AZ Miner (2); Crabtree (1); engineertony (1); geraldpaxton (1); JRaef (1); SolarEagle (1); TonyS (1); Unredundant (2); WJMFIRE (1); Yahlasit (2)

Previous in Forum: Wiring Diagram   Next in Forum: Corona Loss

Advertisement