Soft Starters for a Textile Dryer

07/05/2007 3:46 AM

We have a relaxed textile dryer with four 40 KW 380-440voltsmotors which drive the belt driven blower. We have our own natural gas based electricity generation the problem is the starting torque the motors are two speed motors. I wanted to install soft-starters to prevent the starting current inrush current as it affects the generator. I have 2 200 ampere and 2 240 ampere soft-starters. Is there an issue if I use these over capacity soft-starters as their capacity is much more that 40KW.

Register to Reply
Pathfinder Tags: soft starter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: soft starter

07/05/2007 4:45 AM

I haven't any experience with excessive oversizing of soft-starters. Best is to get a product engineer help you determine if that's possible. Hopefully the rep would be more concerned with helping you rather than just getting you to buy another unit .

That said, in theory it will function. However, most soft-starters I know have current-limiting limits, meaning, their current-limit settings have a certain range based on their power rating. It's very possible that your existing soft-starter's current-limits are way, way over your 40kW motor's full-load-current (FLA).

Since your aim is to limit the starting current of your motor, your soft-starter will probably not be able to do it since its lowest current-limit setting would be much higher than what you need.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: soft starter

07/05/2007 6:58 PM

He's right. Most soft starters with current limit capability are either fixed (in the case of an older analog starter) or if digital, can only be adjusted down to a certain point, usually no more than 50% of their max. rating. So if you have 200A soft starter it might be able to be adjusted down to 100A, but that is still more than the 75A that a 380V motor would draw. Even so however, if you want to use them anyway because you already own them, you might be able to forgo the current limiting capability and just use them as a voltage ramping device only. That will indirectly limit the current by stretching out the ramp time, but you can run in to a limit on the amount of acceleration time you have on the motor before the overload relay trips. Just be aware though, some soft starters do not do straight voltage ramping.

You will also need to be aware of the overload protection capability of the soft starters, because they too may not turn down low enough to protect your small motors. That will mean external OL relays as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Hobbies - CNC - New Member Hobbies - Musician - New Member

Join Date: Jan 2007
Location: South Africa Johannesburg
Posts: 187
Good Answers: 3
#3

Re: Soft Starters for a Textile Dryer

07/06/2007 3:11 AM

Gas driven internal combustion engines to replace the electric motors might be a solution

__________________
Think and move like an electron