AC Generator

10/19/2014 10:46 AM

An AC generator (174 kva) running separately drops it terminal voltage as we increase the load i.e from 450 volts to 435 volts at 100 kw load.Its AVR is functioning properly and speed control is also in good working condition. Should its AVR maintain the terminal voltage (450 volts) at all load conditions?

Whereas the same type of an other generator is maintaining its terminal voltage at all load conditions.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#1

Re: AC GENERATOR

10/19/2014 11:08 AM

You said the AVR is working properly. How did you come to that conclusion? I see an apparent contradiction in your statements. Therefore either I misunderstand you or you misunderstand what is actually happening.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2008
Posts: 13
#2
In reply to #1

Re: AC GENERATOR

10/19/2014 11:19 AM

Thanks for sharing

I switched the AVR to the other generator as I mentioned there its behaviour is as good as the other. it is maintaining 450 volts in all load conditions. then I swithed the other generators AVR to this one but result was the same i.e voltage drops to 435 volts at 100 kw load

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#5
In reply to #2

Re: AC GENERATOR

10/19/2014 11:54 AM

Just trading working circuit boards does not mean the AVR system of a generator is working properly. It only indicates that the problem is probably not the AVR circuit board. Higher rotor winding resistance due to a loose connection, or failing brushes can reduce the maximum exciter current. A break in an isolating bearing can cause a parasitic load on the generator. The load may simply be too heavy for one or all phases causing the magnetic cores to saturate. You could even find that the voltage at the AVR sense point claims that the voltage is fine due to a different wiring path magnetic coupling or just failing output wiring.

You must do some more methodical troubleshooting than just board swapping.

Good Luck

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 13
#7
In reply to #5

Re: AC GENERATOR

10/19/2014 12:12 PM

thanks REDFRED

some more intresting facts are here. I started with the checking of exciting circuit componants one by one, then diode assembly then I swaped AVR but it did not work. Then We were having one brand new generator of the same kind. My boss advised to replace that. I replaced brand new generator and was happy that it will work but unfortunately when we run that the same problem was there. Then we decided to check the switchboard instruments and its Breaker. all those are working perfectly. we run two generators in parallel most of the time but with this defect we are unable to do that cause having load sharing problems. So after putting my all efforts I decided to get advice from this forum. Again thanks for understanding such defect.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#14
In reply to #7

Re: AC GENERATOR

10/20/2014 12:06 AM

This makes even less sense to me now. If having one generator ON produces the expected voltage at load then why add a second generator? What protocols or circuitry keep the two generators operating synchronously? If replacing the whole low voltage generator with a factory new identical model produces the exact same undesired result then I doubt there is anything wrong with the generator. More than likely something is wrong in how you are using the generator.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: AC GENERATOR

10/19/2014 11:39 AM

We have a fundamental problem, as demonstrated by this question from the OP.

"Can I use 230 volt 50 hz electric cooking range on 230 volt 60 hz supply."

Not sure OP is highly qualified for electrical work.

Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 13
#4
In reply to #3

cooking range

10/19/2014 11:52 AM

as cooking range has resistive load so it does not matter if you use 50 or 60 hz supply.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #4

Re: cooking range

10/19/2014 12:05 PM

You obviously had no clue of that when you asked, "Can I use 230 volt 50 hz electric cooking range on 230 volt 60 hz supply. The available ranges in market are mostly 50 hz. I could not find electric cooking range for 60 hz."

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#11
In reply to #3

Re: AC GENERATOR

10/19/2014 2:40 PM

Well, if your directions say cook your roast for 60 minutes, you better set the timer for 72 minutes.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8

Re: AC GENERATOR

10/19/2014 12:29 PM

The load on your generator can also be responsible for what you are seeing. Run the generator connected to a resistive test load bank and see how the voltage drops or not. You may be looking for a trouble in the generator that is not there.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2008
Posts: 13
#9
In reply to #8

Re: AC GENERATOR

10/19/2014 12:47 PM

Thank you for taking intrest in my GEN defect. Once it came to my mind that any load may be cause of this defect but when I run the same load with the other generator that works fine. I mean voltage did not drop and maintain at 450 volts.

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#12
In reply to #9

Re: AC GENERATOR

10/19/2014 4:48 PM

You really need to fine someone knowledgeable in troubleshooting/electricity/power-plants/paralleling/gen-sets.

Anything less, your wasting and money.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Active Contributor

Join Date: Oct 2014
Posts: 14
#15
In reply to #9

Re: AC GENERATOR

10/20/2014 4:02 AM

Are you measuring the terminal voltage by your multimeter, or you are viewing the voltage at the control panel which has some digital meter?

I am wondering maybe if using digital meter at the control panel of the genset has some defect in the voltage sensing circuitary, because you said you have changed the generator and changed the AVR and still having the same problem.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10

Re: AC GENERATOR

10/19/2014 2:11 PM

It sounds like there is a problem with the breaker, have you tested the components with IR heat sensing tool....I would look for elevated temp....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Jan 2014
Posts: 15
#13

Re: AC Generator

10/19/2014 11:44 PM

You did not mentioned that does the voltage drop to 435 and stay there or it goes back to 450volts. I always find question posted on Diesel genset problems that they do not read it up how an genset works(all answer is in the net). Any problems as suggested should always check the health of the alternators by measuring its DC excitation, amps, volts and the running speed, which will tell a story.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#16

Re: AC Generator

10/20/2014 6:24 AM

I think we need a clear defination of the problem.You have stated the generator is running separately and then later it is in parallel.How are u running the set.Secondly 174KVa and then you switch to Kw. 174 KVA is abouy 139 KW.Generator name plate rating is what?Normally ratings go as 125, 160,180 kva and not 174 KVA.Is it the load Kva?What are the connected loads.The load and voltage drop occurs automatically or when something is started.Pl clarify so that the problem can be solved.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#17

Re: AC Generator

10/20/2014 9:59 AM

..........speed control is also in good working condition.

I take it, that by this statement, the gen set is maintaining its correct rpm under all conditions of load and is not dropping at all in speed. Did you check the accuracy of your rev counter. The reason I ask this is there could be a problem with the engine governor.

Also are the Hertz remaining stable or is that inconsistent as well?

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#18

Re: AC Generator

10/20/2014 3:20 PM

Could be the type of load that is causing the trouble!

I know a case where the load that puts a lot harmonics in the system caused this kind of problem. The load was fine on the grid supply but when the load had to be supplied exclusively by the generator the voltage used to dip.

__________________
Raghunath
Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 13
#19
In reply to #18

Re: AC Generator

10/23/2014 2:48 PM

HI, thanks all those shared their experiance and knowlege about AC Generators.today my problem solved. Generator was dropping its terminal voltage from 450 volts to 435 volts at load. Its AVR settings (some pots) was such that it was dropping voltage from noload to ful load by 3.6 percent. when I changed the other generator having same type of AVR that was also dropping the same value of voltage. Then we decided to reset the pots and configured again step by step. we reached the solution.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#21
In reply to #19

Re: AC Generator

10/27/2014 9:01 AM

Pl see one of your replies where you have clearly stated that when u switch the AVR to another Generator it worked well and another AVR swicthed from a diffrernt generator also behaved in the same way ie drop in voltage to435V.If you have adjusted the POT the AVR should have given the same drop when tried on a different generator.Your statements are contradictory.pl clarify.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 13
#22
In reply to #21

Re: AC Generator

10/30/2014 12:27 PM

Both AVRs pots settings were the same. It has S,U,K,T and R47 pots.when I switched the defective generator's avr to the other generator it worked well there. when I put the other generator AVR to this particular generator , It was also droping voltage whereas it was working well on its own gen set.when closely monitored the settings of the pots, that was the same. Then replace the original avr and run the generator first at noload. its noload voltage was 450 volts. then put the 25 percent load and checked the voltage, it droped to 443 volts. I then changed the setting of S pot in lower direction and observed the voltage it changed from 443 to 447 volts and then I changed the setting of U pot a bit and voltage set to 450 volts, then Increased the load to 50, and then 75 percent and observed the terminal voltage which was maintained at 450 volts.After generator was synchronized with other generator and tested the load sharing. Allworked well.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#23
In reply to #22

Re: AC Generator

10/31/2014 6:59 AM

pl c ur reply no7 in reply to5.what u state now and what stated earlier are cintradictory

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Off Topic (Score 5)
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#20

Re: AC Generator

10/27/2014 6:24 AM

Great work done !!!

You must have adjusted DROOP pot on the AVR, this potentiometer is used for kVAR sharing of the Load between the alternators, when the generators are synchronised.

If you want to run the Gensets in SOLO mode, just put a switch which will short circuit the secondary of the QDCT (Quadrature Droop Current Transformer) connected in W phase of the alternator...

Now the voltage will not droop in SOLO mode, in Sync mode put the switch otherway..

Register to Reply
Register to Reply 23 comments

"Almost" Good Answers: