25 kV Power Cable in Concrete Trench (Grade Raceway)

10/19/2014 11:37 PM

Hi, I have 6(six)- 2 per phase 25 kv 500 mcm XLPE cu power cable which will be routed from 25 kv bus to switchgear building through road crossing heavy duty concrete trench(grade raceway) approximately 55m distance. How I could put my cable? If I put flat formation with 2 layer then what would be the spacing between layers. cable dia 45 mm and what woud be spacing between two cables. Could I put A-B-C from left and on top layer same sequence A-B-C from left. Should I have to calculate any de-rating of ampacity since trench would be be covered.Please advise.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 25 KV Power cable in concrete trench(Grade raceway)

10/19/2014 11:43 PM

Where are you?

Are you aware of local electrical codes, such as NFPA 70?

Maybe you should consider hiring a local electrician?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: 25 KV Power cable in concrete trench(Grade raceway)

10/20/2014 1:22 AM

Usual practice is to put the singles in trefoil formation.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 13
#3
In reply to #2

Re: 25 KV Power cable in concrete trench(Grade raceway)

10/20/2014 1:30 AM

Thanks a lot. Should I have to do any de-rating calculation? Trefoil would be AA-BB and top CC on top per two cables or ABC ABC two trefoil. For first option is there any spacing requirement between A-A

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #3

Re: 25 KV Power cable in concrete trench(Grade raceway)

10/20/2014 7:20 AM

ABC - ABC

There will be a derating factor for which you'll have to refer to your local codes. You don't give the loading so it's hard to say.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#4

Re: 25 KV Power cable in concrete trench(Grade raceway)

10/20/2014 1:40 AM

Lay them in Trefoil formation Each trefoil cable cleats at 1 meter intervals . Ensure at least 350 mm gap between the two Trefoils. See link below for the arrangement. http://www.cablejoints.co.uk/images/gallery/uploads/1380542304_Prysmian%20Dutchclamps%20-%20High%20Voltage%20Trefoil%20Cable%20Cleats.jpg

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Associate

Join Date: Jan 2012
Location: chennai.
Posts: 27
#5

Re: 25 KV Power cable in concrete trench(Grade raceway)

10/20/2014 5:52 AM

Dear Sahababu71,

It will be better to refer the standards like IEC 60364, NFPA 70, BS 7671.

And as per the site condition.

There different type of laying method is there accordingly the de rating factor should be calculated.

thanks

__________________
Prabakar
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: 25 kV Power Cable in Concrete Trench (Grade Raceway)

10/21/2014 4:33 AM

I am sorry, Pracabar.IEC 60364 it is only for low voltage cable standard. Also NEC [NFPA 70]

does not deal with cables in trench- as I know- and BS7671[IEE Wiring Regulation] it is also for low-voltage cables[at a nominal voltage of 230 V a.c. single-phase or 230/400 V a.c. three-phase].

Caterpillar,the way to cleat the single core cables it seems to me correct.Could be the clamps of id-Technik? See:

http://www.id-technik.com/de/start/

__________________
Julius
Register to Reply
Anonymous Poster #1
#8

Re: 25 kV Power Cable in Concrete Trench (Grade Raceway)

10/22/2014 9:49 AM

Useful topic on cable arrangement http://www.psa-outline.com/cable-selection/

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: 25 kV Power Cable in Concrete Trench (Grade Raceway)

10/22/2014 12:23 PM

No standard-as I know-NEC, IEEE, BS [IEE], VDE-which deals with unventilated channels.

This book indicates a way to calculate the air temperature rise in such an unventilated channel:

Power cables and their application by Lothar Heinhold http://books.google.co.il/books?id=u1sjSgAACAAJ&dq=bibliogroup:%22Power+Cables+and+Insulated+Wires%22&hl=iw&sa=X&ei=U85HVIy0Nand7Qax-4GIDQ&ved=0CBwQ6AEwAA

ch.18.5.1

Here attached 4 pages:

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: 25 kV Power Cable in Concrete Trench (Grade Raceway)

10/23/2014 11:17 AM

It is difficult to see the above image.I'll try to expose only one.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: 25 kV Power Cable in Concrete Trench (Grade Raceway)

10/25/2014 4:48 AM

This is the final try:

__________________
Julius