High Voltage Cable Fault Location Finding

10/21/2014 4:37 PM

Hi all,

During testing of 11kV trefoil formation cables at our site, one of the cable failed the High Voltage test. High Voltage Test was carried out using VLF (Very Low Frequency) method - 21kV AC, 0.1Hz for 30 min. HV VLF Test was tripped at 7kV AC. Device used was HVA30.

Also, note that insulation resistance for faulted cable after HV Test was found to be about 450 MOhm.

Hence, to identify, we used Time domain reflectometry (TDR) meter, but could not locate any fault on the cable, as TDR meter gave perfectly OK reflection at other end. (attenuated pulse)

Now, as per vendor's recommendation, there is no other way than to apply thumping surge generator which can burn the fault by making IR value equal to zero.

However, I understand that during thumping of cable, it will get damaged.

Is there any other way to locate the fault on HV cable without damaging the cable?

As per vendor's reply, cable will not get damage during thumping.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: High Voltage Cable Fault Location Finding

10/21/2014 8:00 PM
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: High Voltage Cable Fault Location Finding

10/22/2014 1:17 AM

"As per vendor's reply, cable will not get damage during thumping."

If the cable manufacturer is happy with you using a thumper what's stopping you?
Any damage will occur at the point of the fault which I believe is what you're looking for.
Once located it is normal practice to remove several metres and insert two joints removeing the fault.

What I do find strange is a newly installed cable failing. The cable manufacturer would normally attend a fault like this as their reputation is on the line. Are you afraid they will find poor installation methods has caused the damage?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Oct 2014
Posts: 5
#3
In reply to #2

Re: High Voltage Cable Fault Location Finding

10/22/2014 3:12 AM

Yes, we are trying to locate the damage using thumper. But in process, we don't want to damage other cables, as 1 core cables are installed in trefoil formation.

These cables were already tested for Hipot during Factory and passed the tests. Hence from, vendor's point of view, it is either transportation or installation problem.

Register to Reply
Power-User

Join Date: Jun 2007
Location: Derbyshire UK
Posts: 362
Good Answers: 6
#5
In reply to #3

Re: High Voltage Cable Fault Location Finding

10/22/2014 5:43 AM

There may be a way, I do not know.

One approach would be to say 'Testing by Thumping may damage the other two cables', locate the fault, and go in prepared to repair three. (I am assuming the damage will occur at the same site.) That way if the other cables are damaged, at least you predicted it, and were prepared, and the finger points more at transportation than installation.

I'm sorry it's not a solution.

cnc

Register to Reply
2
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#4

Re: High Voltage Cable Fault Location Finding

10/22/2014 5:38 AM

1. Go straight to the termination and check the stress cone and earthing and if the insulation from the lug is clean between the lug barrel and the top of the stress cone.

2. If you have a joint in the run, check jointing of that phase.

3. If you use a thumper it will cause damage to the phase and you have no choice but to cut out cable and install 2 joints and a section of cable as carbonising will occur on the semi con.

Register to Reply Good Answer (Score 2)
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#6

Re: High Voltage Cable Fault Location Finding

10/22/2014 4:46 PM

Waty back when I did industrial experience in a coal mine there was a method used to detect insulation faults and broken conductor strands in trailing cables (1100V and 6600V).

They applied a DC Voltage to the cable and capacitor coupled one end to an amplifier with a headphone speaker set. When the cable was disturbed at the fault location, the movement created a noise on the DC voltage that was very detectable in the headphones.

The cables were also draped through a grounded trough of water. Any failures in insulation typically showed as a trail of bubbles as the cable moved through the water.

Probably not possible to test this way if already installed.

Suggest if the termination and jointing reviews are not conclusive, then the once off cost to remove and inspect the cable is worth the effort compared to future costs if the cable fails and causes serious outcomes.

__________________
Just an Engineer from the land down under.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#7

Re: High Voltage Cable Fault Location Finding

10/24/2014 7:18 AM

SSKale, can u pls post a followup showing the result of the thumper test?

The IR test value was 450 Mohm, which is very excellent. Hence my interest in seeing the result of your thumper test.

One question: was that IR test at 11 KV?

__________________
BSEE but always learning
Register to Reply
Member

Join Date: Oct 2014
Posts: 5
#8
In reply to #7

Re: High Voltage Cable Fault Location Finding

10/25/2014 3:47 PM

Thank you for support everybody.

Today, we have tested 11kV cable by thumper. While thumping, at 9kV DC, fault happened again. Then, we walked along the cable route with audio detection device and finally we found the location of fault.

As seen in photo, cable is burned during thumping. But, we were fortunate that other cables were not harmed during thumping as cables in trefoil were not isolated.

This fault has happened in another plant substation, where contractor has dug the cables while doing some other civil work. Also, proper installation methods were not followed while soil backfiling. There was no gap between protection tile and cable.

Anyway, now we will install cable jointing kit at above location.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#9
In reply to #8

Re: High Voltage Cable Fault Location Finding

10/25/2014 8:33 PM

Thanks for the feedback. I appreciate that. Glad you found the fault.

Register to Reply
Register to Reply 9 comments