This is my first post. I am working as electrical design engineer, currently at site and here we have following situation.
Due to some reasons, our owner is not giving power to energize the switchgear, MCCs and has asked us to carry the 4 hours solo run (no load) test of motors powered from DEG. Now, I am calculating DEG size for following priority loads to be tested at no load.
2 Nos. 75kW, 2 Nos. 30kW and 2 Nos. 37kW Motor (all 4 poles)
I understand that Motor No load active power is very less, due to poor no load power factor e.g. PF = 0.2, but reactive power will be high. Also, for 75kW large motor starting, considering 6 times starting current and low starting power factor e.g. 0.2, starting vars will be very high.
As per my calculation, total active power required = 126kW and Reactive Power =617kVAr. Hence, overall load factor to be very low i.e. 0.2 again.
Now, I have question here.
1) Whether to select DEG with 750kVA with 0.8, power factor so that Generator will provide reactive power = 750 X 0.6 = 450kVAr X 1.5 = 675kVAr, considering 150% overload capability for 30sec.
2) Whether DEG with smaller size can be selected considering Generator can provide overload capability higher than 150% for duration less than 30 sec. I understand that motor starting time at no load will be very low i.e. <1 sec for LV Motor.
3) Or whether I have to select DEG which can operate at very low power factor. e.g. 500kVA with power factor 0.5 and whether such Gensets will be available easily for renting.
Appreciate your help to solve the issue.