Thermal Protection of Motors?

07/05/2007 7:44 AM

How the thermal protection of motors done ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Thermal Protection of Motors?

07/05/2007 8:38 AM

Some motors have a temperature sensor in their windings, that can be wired through to a control unit in the starter that cuts off power to the starter contactor coil in the event of a predetermined temperature being exceeded.

Other ways of achieving over-temperature protection include setting an over-current trip to do the same thing, though this is less satisfactory as it presumes ambient conditions at the motor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#3
In reply to #1

Re: Thermal Protection of Motors?

07/06/2007 1:20 AM

A bit addition to Mr 'PW.." anwer .

Its the RTD put inside winding to get the correct temperature of motor.

Overload relay(bi-metallic or electromagnetic/microprocessor etc) see the current and estimates the temperature rise from its inbuilt character curve. The trip setting of motor is changeable.

Normally the later one with bi-metallic relay one is followed mostly. But for higher rating motors say 90kW and above or MV motors RTD in winding is used.

BNDas, Kolkata, India

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Thermal Protection of Motors?

07/05/2007 6:42 PM

Any reasonable answer would require you to define what you mean by "motors". 1/10 HP 24VDC motors are protected very differently from 10MW 6.9kV motors. And that is assuming you even mean electric motors! (which I assumed because you posted in an Electrical Engineering forum)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4

Re: Thermal Protection of Motors?

07/06/2007 3:02 AM

A bit addition to Mr 'PW.." answer .

Its the RTD put inside winding to get the correct temperature of motor.

Overload relay(bi-metallic or electromagnetic/microprocessor etc) see the current and estimates the temperature rise from its inbuilt character curve. The trip setting of motor is changeable.

Normally the later one with bi-metallic relay is followed. But for higher rating motors, say 90kW and above or MV motors RTD in winding is used.

BNDas, Kolkata, India

__________________
BNDas
Reply
Power-User

Join Date: Aug 2006
Location: Central Florida in the good old US of A
Posts: 332
Good Answers: 2
#5

Re: Thermal Protection of Motors?

07/06/2007 8:10 AM

If you use a starter (contactor) to run your motor, thermal heater coils are procured based on the full load rating of the motor (approximately 125%). That data is provided on the motor and you use the contactor information to get the correct size heater coils for your starter. Depending on the manufacturer, you will get either one or two for a single phase motor, or two or three for a three-phase motor. Heater coils and contactors are usually not interchangeable between different suppliers.

__________________
Eschew obfuscation.