Level switch testing

07/05/2007 9:36 AM

Has anyone come up with a design or method for testing level switches that are mounted in the wall of the vessel without removing them from the vessel or tank? We have tuning fork, capacitance and gap switches and many are in applications that are not conducive to opening the system. If the switch is removed, checked and reinserted the probability is good but not certain that it is working. We can run the level up in some instances to positively verify the switch but in most cases this is not possible. I have ideas but I thought someone may have already invented this wheel.

__________________
Support your local Shriners, they have provided FREE medical assistance for over 800,000 kids so far.
Register to Reply
Pathfinder Tags: level switch
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Level switch testing

07/05/2007 10:21 AM

Tuning fork: any solid object in contact with its waggly bits, like a broom handle passed through a suitable flange on the vessel, perhaps?

Capacitance switches: nasty things, usually selected when nothing else will do. No simple solution here. Fill the vessel up with someting innocuous is about as good as it gets.

Gap switches: optical? Put something solid and opaque in the gap, stuck on the end of that broom handle, perhaps!

Seriously, consider that the vessel will, on unlikely occasions, overfill. Consider carefully what happens to the liquid that spills over, its capture, retention and proper disposal. Well-designed tank installations will have a bund, probably sized to accomodate 105-110% of the vessel's contents in the event of a mechanical failure near the bottom of the tank.

There is no short-cut to anywhere worth going and a formal Hazop is highly recommended.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#2
In reply to #1

Re: Level switch testing

07/06/2007 7:56 AM

On the end of the "broom handle", fit a cup, larger than the switch, and with a sealing edge. Also a pipe to fill it with the same liquid used in the tank.

Put in place, fill up, and check output. When done, remove and let the cupfull of liquid add to the current contents of the tank.

__________________
Madness is all in the mind
Register to Reply
Power-User

Join Date: Jun 2007
Location: Port Neches, Texas -- Bond Point
Posts: 117
Good Answers: 3
#3
In reply to #2

Re: Level switch testing

07/06/2007 9:47 AM

Broom handle is good, cost effective, BUT say we don't want to or cain't open the tank to insert said broom stick?

So Maybe---

The tuning fork switch in some of our applications are in powder applications. I am thinking of installing a small air or N2 supply tube that would blow a jet of air or N2 on to one of the forks. I am hoping that this would disrupt the vibration enough to set the switch. I have asked for a setup to test this. One problem is (there is always at least one recognizable and several not so obvious) that the supply into the vessel will be at a pressure greater than the tank is rated for, so failsafe guards will have to put in place to prevent the inadvertant opening of the unregulated supply.

A simular setup for the gap switches( ultrasonic as made by KayRay/Sensall owned by Thermo somebody and run by somebody else, I can't keep track). I plan to try to run a line from the recirculating pump that will flood the gap in the switch with what ever the content of the tank is. This would be controled by a simple ball valve from a convienent location.

In both of the previous apps the switch and pipe nozzle mounting would have to be in a flange with piping and target aligned prior to installation in the tank.

I am still thinking on the capacitance probe (Rosemount, Foxboro, Endress-Hauser, et.al.) installed in a vertical position in the top of the tank, hangs down about 6 feet and reads level by reading the chance in capacitance as the liquid assends the probe.

Whaddua think? Will it work? Any thoughts on the latter?

__________________
Support your local Shriners, they have provided FREE medical assistance for over 800,000 kids so far.
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#4
In reply to #3

Re: Level switch testing

07/06/2007 11:12 AM

As you are measuring liquid, try a tube around the probe which is normally open at both ends. Fit a valve/cover at the bottom, so it can be closed for testing. Then fill the tube (known dimensions/volume) for testing/calibration. Must be default open, or the level will only be sensed once it has raised beyond the top of the tube.

Much easier to design the testing in, rather than add later - but not impossible if the tube can be within the dimensions of the sensor mounting.

__________________
Madness is all in the mind
Register to Reply
Power-User

Join Date: Jun 2007
Location: Port Neches, Texas -- Bond Point
Posts: 117
Good Answers: 3
#5
In reply to #4

Re: Level switch testing

07/06/2007 9:09 PM

I am thinking along these same line however the valve or removable cover inside a tank of 98% caustic will be difficult to operate. perhaps the tube may be enclosed on the bottom with only a few small holes that could flow the level liquid in for measuring. During testing the chamber could be flooded with enough circulated caustic so as to overcome the drain ability of the chamber, thereby rasing the level to trip point. Now for the difficulty--- caustic in solution has a tendancy to coat and solidify in a sort of soap like gel. This may plug the holes, not allow any tank product to enter the chamber, bad level reading result. D a r n.

__________________
Support your local Shriners, they have provided FREE medical assistance for over 800,000 kids so far.
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#6
In reply to #5

Re: Level switch testing

07/07/2007 3:09 AM

Also, with small holes, there would be a delay in the reading, as the chamber would fill slower than the tank.

How quickly does the sensor get coated, thickly enough to stop working? - Can you use this build-up to determine the safe number of cycles before cleaning?

__________________
Madness is all in the mind
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #3

Re: Level switch testing

07/09/2007 11:58 AM

I am thinking of installing a small air or N2 supply tube that would blow a jet of air or N2 on to one of the forks.

Not likely to work unless the N2 were at least supersonic: these things work by detecting a change in natural frequency of vibration as a result of the density between the waggly bits changing.

capacitance

Here's a story for the learning of.

Many years ago an analog capacitance level measuring instrument was installed in a glassed vessel full of nasties. It calibrated fine at initial set-up. After about 18 months someone overfilled the vessel with the capacitance gauge only showing part-full at the moment of the event. The reason? Something other than the liquid with which it had been calibrated had been intoduced to the vessel without going round the HazOp analysis loop in the presence of a controls engineer to consider "something other than". Horrible things. Be afraid. Be very afraid....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #2

Re: Level switch testing

07/09/2007 11:49 AM

Yes. That would do it too.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 441
Good Answers: 20
#9

Re: Level switch testing

07/11/2007 2:33 PM

If I understand you post correctly you need an auxillary system to verify operation of your tank level sensors. Google "Freescale Semiconductor" and look at their AN1516 liquid level control. This is an updated version of the "tube, open to the bottom of the tank. Pressurize with an inert gas and read the (pressure converted to the appropiate schedule) required to vent a bubble".

This system, using the older but sensitive Wallace & Tiernan or Heise analog gauges, is still in use in many fuel farms and volatile fluids storage facilities. Usually the inert gas is Nitrogen and is precisely regulated to allow pressures in at the bottom of the sensing tube or pipe to not be greater than that which will cause a bubble of gas to eacape. This precise pressure is then calibrated in the appropiate schedule (feet, inches, meters, gallons, liters, etc). This system can possibly be made portable for use such as you need for determining the accuracy or operation of your in tank level sensors if the tanks are not pressurized.

__________________
intellectuals solve problems, geniuses prevent them ~ Einstein