Overload Class

11/06/2014 4:15 AM

This is for a 3 phase pole changing motor.It has two speeds, each speed is protected by its own overload, both are class 10.It runs for 5 seconds on speed 1 then moves onto speed 2.I don't believe the overload is going to offer much protection on speed 1.Will a class 5 overload be acceptable to use in this case.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: overload class

11/06/2014 4:41 AM

There might be nuisance trips, but otherwise acceptable. If it runs only 5 seconds, it is not clear that an overload is even meaningful at that speed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#2

Re: overload class

11/06/2014 5:09 AM

2 completely independant windings?

What does the rating plate mention for each speed?

I suppose the motor is designed to run at a given power at 100 % ED at speed 1 and another given power at 100 % ED at speed 2.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: overload class

11/06/2014 6:56 AM

The overload class implies the LRA withstand as i understand it. If the motor does not start at all, it should still be able to withstand 7.2x FLA for 10 secs...shouldn't it ? As most motors are designed to withstand DOL starting, this should not be a problem even in your case. i don't think you need a special Class 5 relay. But then, i have no experience with pole-changing motors, so please excuse my ignorance,

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: overload class

11/06/2014 8:43 AM

I'm with Tornado on this. The purpose of an overload relay is to provide protection against a condition that might damage the motor, not to provide tripping at as low a level as possible. So what if your motor never trips with a class 10 overload? Why is that a problem for you? The motor is likely designed for Class 10 protection or better, that's all you need for it, regardless of how long it is used.

Pipe down and be happy!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**