Crompton Greaves Induction Motor Data

11/13/2014 11:16 PM

Hi,

We have Crompton Greaves Induction Motor, which is of 7.5 hp, and 415 volts as mentioned in its nameplate. When converted to kW, it is arond 5.595 kW (7.5*0.746), so full load current calculated comes as 9.73 Amps (taking 0.8 pf - as we have used 0.8 pf for the diesel generator rating also). But 11.3 Amps is mentioned on its nameplate. Why? (This is possible if power factor is reduced to 0.6888, but how to justify).

Regs,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Crompton Greaves Induction Motor Data

11/14/2014 12:10 AM

Is the motor efficiency stated on the nameplate? Is the power factor (or cos phi) stated? Most 415 volt systems are in SI countries, so why does the nameplate specify hp?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Crompton Greaves Induction Motor Data

11/14/2014 12:27 AM

The FLA will vary according to rpm, due to efficiency losses....

http://www.roycecross.com.au/documents/manualsPDF/CG%20THREE%20PHASE%20CATALOGUE.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
2
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3

Re: Crompton Greaves Induction Motor Data

11/14/2014 4:25 AM

Because the efficiency is 86% (= 9.73/11.3). Motor rating is the shaft output power, not the electrical input.

__________________
Give masochists a fair crack of the whip
Reply Good Answer (Score 2)
Anonymous Poster #1
#4
In reply to #3

Re: Crompton Greaves Induction Motor Data

11/14/2014 5:26 AM

the efficiency at full load is: 86% and rpm is 950 as mentioned in the nameplate,

Regs,

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Crompton Greaves Induction Motor Data

11/14/2014 5:34 AM

Is there an echo in the room?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#6
In reply to #5

Re: Crompton Greaves Induction Motor Data

11/14/2014 6:19 AM

sorry, 85% full load efficiency, frame 132M, ambient 50 degree centigrade, RPM 950.

Regs,

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #4

Re: Crompton Greaves Induction Motor Data

11/14/2014 8:01 AM

Yes, you should have divided by that as well to get FLC. Rpm does not affect current.

__________________
Give masochists a fair crack of the whip
Reply
Anonymous Poster #1
#8
In reply to #7

Re: Crompton Greaves Induction Motor Data

11/14/2014 10:38 AM

taking the value of efficiency as 0.861048 gives FLC of 11.30 Amp, but with 85% efficiency, we get FLC as 11.447 Amps. Is there adjustment for ambient temperature of 50 degree centigrade?

Regs,

Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#9
In reply to #8

Re: Crompton Greaves Induction Motor Data

11/14/2014 10:46 AM

At this point, I think you are 'splitting hairs'.

Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Crompton Greaves Induction Motor Data

11/14/2014 11:38 AM
  • "...taking the value of efficiency as 0.861048 gives FLC of 11.30 Amp, but with 85% efficiency, we get FLC as 11.447 Amps. Is there adjustment for ambient temperature of 50 degree centigrade?"
  • "At this point, I think you are 'splitting hairs'."

Working so hard to account for 0.147A out of 11.447A is in my opinion more like splitting the split ends of hairs... This should be nominated for being the defining statement in describing "anal retentive" for the year.

That level (1.28417926094173%) of exactitude can be more than accounted for by measurement error.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#11
In reply to #8

Re: Crompton Greaves Induction Motor Data

11/14/2014 11:41 AM

Not that I'm aware of, but you might look on the internet. It's not an exact science, definitely not to 6 decimal places!

I agree with #9. One minute you're wondering why it's 11.3 amp, not 9.73, next you're querying 1 percentage point.

__________________
Give masochists a fair crack of the whip
Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#12

Re: Crompton Greaves Induction Motor Data

11/14/2014 2:07 PM

I want to see how that guy above sets a thermal relay with a precsion around 1 mA. :)

Neither the motor current nor the settings of conventional thermal motor protection relays is very precise, let allow a +/- couple of % and surrounding temperature play a role too.

Reply
Anonymous Poster #1
#13
In reply to #12

Re: Crompton Greaves Induction Motor Data

11/14/2014 10:16 PM

The above link for induction motor from Crompton Greaves showsFrame size too. It is mentioned in the catalog as: 63 to 400 for TEFC.

But in my motor nameplate rating, Frame has been defined as MD132M and BPM123M. How to interpret this?

Regs,

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15
In reply to #13

Re: Crompton Greaves Induction Motor Data

11/15/2014 6:58 AM

The 123 is a typo. The prefix letters may designate items such as extended or stepped shafts, such as used for some types of pumps. They have little or no effect on amperage characteristics.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#14

Re: Crompton Greaves Induction Motor Data

11/15/2014 5:51 AM

Is it FLC or Staring Current?. I would like to what is the problem in the performance of the motor?. Is it getting heated up?. We have used similar size motors suitable for Crane Duty and they have worked well without any problem. Crompton is well known and reliable make.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Reply
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); bigg (1); Codemaster (3); JRaef (1); Plimos (1); sauravbabu (1); SolarEagle (1); suresh sharma (1); Tornado (3)

Previous in Forum: Vibration of Motor Increases When Switched Over to VFD Mode   Next in Forum: Serious Distortion Issues with TDA2030 Amplifier Kit

Advertisement