Recirculation of Fluids in a Pumping System

11/18/2014 2:33 PM

In a totally-closed pumping system transporting fluid around an enclosed loop using a positive displacement type of pump and having a check valve on the pump outlet, does the pump reach a condition where it will cavitate if the pump inlet pressure (or alternatively the liquid volume) becomes reduced too much ?

__________________
"Consensus Science got us into this mess, then why can't it get us out?" : Rephrase of Will Rogers Comment
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Recirculation of fluids in a pumping system

11/18/2014 2:49 PM

Cavitation is more common in centrifugal pumps.

However, reduction of vapor pressure is certainly possible with a PD pump.

Wiki says:

"Hydrodynamic cavitation describes the process of vaporisation, bubble generation and bubble implosion which occurs in a flowing liquid as a result of a decrease and subsequent increase in pressure. Cavitation will only occur if the pressure declines to some point below the saturated vapor pressure of the liquid and subsequent recovery above the vapor pressure. If the recovery pressure is not above the vapor pressure then flashing is said to have occurred. In pipe systems, cavitation typically occurs either as the result of an increase in the kinetic energy (through an area constriction) or an increase in the pipe elevation."

Depending on the type of PD pump in use, I'd say the damage could range from minimal to catastrophic.

I'd never allow this condition to exist and you won't have a problem.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Recirculation of fluids in a pumping system

11/18/2014 3:27 PM

It depends. Consider the possibility during the HazOp Study.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Aerospace Engineering - Aeromarine Vehicle Engineer

Join Date: Mar 2008
Location: Baltimore, MD
Posts: 148
Good Answers: 5
#3

Re: Recirculation of fluids in a pumping system

11/18/2014 5:47 PM

What is the fluid: water, hydraulic fluid, etc.?

What is the pump flow rate and operating pressure?

Does your system have a reservoir?

What is the diameter of the output, suction, drain lines?

If you want answers to your question, you need to bottle the egg

Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#4

Re: Recirculation of Fluids in a Pumping System

11/18/2014 10:47 PM

Looks like you will be wagging your tail in soup.

It will definitely warm up.

Is there anyting more in the system than a pump that feeds from outlet to inlet.

Why would there be a checkvalve on the outlet?

I reckon thats a hypothetical question?!

__________________
Common Sense Dictates
Register to Reply
3
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5

Re: Recirculation of Fluids in a Pumping System

11/19/2014 5:01 AM

If the fluid is liquid the circuit is unlikely to be totally closed as expansion would be a problem. In e.g. a central heating system there is either a header tank or an expansion vessel which allow the volume to vary. This should be connected close to the pump suction and this fixes minimum system pressure. (The header tank itself needs to be higher). There is a pressure rise across the pump followed by a fall around the circuit back to the inlet. Need to ensure the minimum pressure is enough for pump maximum requirement (usually at max flow if variable). In that case variation in system resistance does not change pump suction pressure so does not cause cavitation risk. If the exp vessel is connected anywhere else the pressure at pump suction varies with system resistance and it's quite possible for it to fall below cavitation point.

__________________
Give masochists a fair crack of the whip
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Recirculation of Fluids in a Pumping System

11/20/2014 1:54 AM

Domestic central heating circulating systems do not need a check valve. Cavitation is a rarity, and usually caused by something going on in the system such as an air-lock.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #6

Re: Recirculation of Fluids in a Pumping System

11/20/2014 4:12 AM

OP didn't say it is a heating system, I used that as an example. But I can't see why there would ba a NRV in any recirculation system, maybe special cases where it's needed, but I can't think of one offhand.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Recirculation of Fluids in a Pumping System

11/20/2014 5:01 AM

2*100% centrifugal pumps arranged in a parallel piping scheme as duty/standby would need non-return valves downstream of each pump. Centrifugal pumps are the most common circulator in pumped domestic central heating systems. The original poster is talking about positive displacement pumps, for which no non-return valve would be required were it a single pump installation; if the rotor of an installed standby pump were unrestrained, the actions of a parallel duty pump would tend to drive the standby pump backwards. The original poster still needs to consider the possibility of cavitation during the HazOp Study, on the assumption that this is some industrial installation that would merit using the protocol. Here, as elsewhere, details of the original poster's installation are too scant at this time to merit an absolute answer. <unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#9
In reply to #8

Re: Recirculation of Fluids in a Pumping System

11/20/2014 5:22 AM

OK pumps in parallel clearly need NRVs. I should have thought of that, I've installed enough of them.

__________________
Give masochists a fair crack of the whip
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".