HT to HT Voltage Regulator

11/29/2014 1:05 AM

We have 5MW Solar Power plant which is connected with 33KV Grid. The grid voltage is not stable in this remote area. It varies from 26KV to 37KV depend on some certain conditions. So we are in search of HT Voltage regulator which could rectify our plant Voltage. We have 10 Inverters (220V Output Voltage) followed by 5 transformers(33KV Sec. Voltage). The common output of all 5 transformers are connected with Grid. We need HT voltage regulator which will be installed between our plant and grid to regulate and supply 31KV-35KV to all 5 Transformers which we need to start Inverters.
Is there any other way to regulate plant HT voltage?Do ONTC transformer of 33KV/33KV feasible ?
Please suggest regarding this.
Thanks in Advance.

__________________
pstanwar9229
Register to Reply
Pathfinder Tags: HT Voltage Regulator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: HT to HT Voltage Regulator.

11/29/2014 9:06 AM

My suggestion is to find the original consultant/installer who designed your system and force him to correct this glaring error, if not then your "fix" (if one exists) is going to cost you many years of your "free" solar energy output.

Your situation illustrates the problem of buying on price alone and not having competent engineers, who have done this before, guide you. Reminds me of the saying "How come there's never enough money to do it right, but always enough money to do it over?"

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#2

Re: HT to HT Voltage Regulator.

11/29/2014 11:22 AM

Regulate it at 220V prior to step up transformer 33KV. Simple Buck and Boost operation of Voltage Stabilizer could do the job at lower voltage.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#3
In reply to #2

Re: HT to HT Voltage Regulator.

11/30/2014 3:43 AM

I agree, all circuitry to deal with the varying incoming line voltage, and the varying output voltage should be at the 220V level. The 1MW inverter designs should be such that they regulate their output currents to find the maximum-power-point of draw from the solar panels, rather than to establish a preset output voltage. This activity would be at the solar current-input and 220V level. If the controllers in his 1MW inverters are unable to do this, pstanwar9229 has a problem. If he proposes five 220V add-on-regulator stages, these each have to contain a 1MW dc rectifier plus a second new 1MW inverter output, which is not an inexpensive matter. He might as well scrap his existing inverters and purchase new appropriate ones which can handle the task.

__________________
Thanks, Win
Register to Reply
Participant

Join Date: Nov 2014
Location: South Pacific
Posts: 2
#4

Re: HT to HT Voltage Regulator.

11/30/2014 5:11 AM

Get 5 new transformers with built in HT voltage regulation. Here's a link of a supplier who is in India. http://jindaltransformers.com/manufacturer/distribution-transformers/jindal/automatic_voltage_regulator.html

__________________
know what you don't know
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1268
Good Answers: 27
#5

Re: HT to HT Voltage Regulator.

11/30/2014 11:44 AM

Typical source of power variations in HT supplies are due to un-expected load demands from an improperly designed distribution system! The most common contributing factors of voltage fluctuations are due to voltage drops along the grid, triggered or caused by under-sized transmission lines, (improper wire gauge either for aluminum or copper).

The solution of using of voltage regulator is temporary and limited. Most of the time will only be applicable if the problem is mostly over-voltage in nature? A longer term solution is to increase power plant capacity and/or the use of properly sized transmission lines, (proper AWG, aluminum or copper), in the network. Demand factor needs to be considered in the design supply!

__________________
vsar
Register to Reply
Guru

Join Date: Jul 2012
Location: Madison, WI.
Posts: 2074
Good Answers: 77
#7
In reply to #5

Re: HT to HT Voltage Regulator.

12/01/2014 8:31 AM

Improperly designed, what you mean by that......

__________________
Knowing is the end result of learning, not believing.
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1268
Good Answers: 27
#8
In reply to #7

Re: HT to HT Voltage Regulator.

12/01/2014 9:45 AM

rashavarek -

Part of good engineering practices is to ensure that transmission lines in the supply grid are properly sized to meet the designed capabilities of the power source... Considerations for present and future demand should also be incorporated and considered as a good business practice.

Adding new power source(s) just to supplement and meet increased power demand without corresponding changes in its transmission mode will be an issue, problematic as the OP is now encountering!

Read and digest OP's comment /response...

__________________
vsar
Register to Reply
Active Contributor
India - Member - New Member

Join Date: Oct 2010
Location: India
Posts: 20
#6

Re: HT to HT Voltage Regulator

12/01/2014 12:47 AM

Thanks all all for your valuable suggestions.

Our Plant has 10 Inverters each 500KW, 5 Transformer with dual LT side winding.

When our plant was commissioned there was not such kind of situations like Under or Over Voltage. These issues are increased now a days because of Lots of Wind Farms installed nearby us. I agree with @vsar that here are under-sized transmission lines. The Grid is quite old and can't hold too much generation.

Is it SAFE to install a voltage regulator between Inverter and Transformer?

__________________
pstanwar9229
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1268
Good Answers: 27
#9
In reply to #6

Re: HT to HT Voltage Regulator

12/01/2014 10:13 AM

Having a voltage regulator although not a complete protection may make your investment a bit safer... You still need to install an automatic system disconnect for your protection from extreme grid fluctuations beyond the limits of your regulators?

__________________
vsar
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Kennie (1); Noudge79 (1); pstanwar9229 (1); RAMConsult (1); rashavarek (1); vsar (3); Winfield Hill (1)