Incomer Tripping on Differential Protection

11/28/2014 12:18 PM

Recently when we started 6.6kV,1400kW motor,the main incomer got trippped on differential protection.We could later find out the reason,which was due to leakage current in the CT secondary terminals at the front side of the panel.The incomer CT ratio: 2000/1A.But we could not pin point why this has happened now and not before when the motor was started so many times before also recently.Hope someone couldhelp me out here.

Thank you.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: Incomer tripping on differential protection

11/28/2014 5:06 PM

The CT insulation obviously failed which happens sometimes.

You did not state how long the CT has been in service.

I would make sure the voltage rating of the CT meets the application requirements.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#2
In reply to #1

Re: Incomer tripping on differential protection

11/28/2014 10:07 PM

We have identified the problem,which was in connector from which it goes to protection relay.There was leakage current due to this faulty connector.B/w, the incomer of 6.6kV board is fed from a 33kV/6.6kV transformer.

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#3
In reply to #2

Re: Incomer tripping on differential protection

12/01/2014 12:16 PM

In addition to the above you may also check whether 2nd. harmonic blocking filter circuit in the relay is functioning properly.

Manindra.