SEL-451 relay CT Connections, Delta or Wye

11/29/2014 8:14 PM

We were planning on replacing old analog breaker failure relays with SEL-451.

The existing BF relays are connected, along with diff relays for gen/unit protection.

There are three sets of delta connected CT's two on output lines, one on main generator.

All three CT sets feed current to the diff protection through the two BF line relays.

A relay engineer said the SEL-451 will not 'work' with delta connected CT's.

We cannot simply re-wire the CT's to wye without replacing all relays at once.

I'll be calling the SEL engineers on my return to work.

Does anyone have any thoughts?

Register to Reply
Pathfinder Tags: SEL ct connection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: SEL-451 relay CT Connections, Delta or Wye

12/01/2014 8:56 AM

Hey dennis,

Why wouldn't you consider the SEL engineers information to be correct? We have had 3 phase, AC power around for more than 100 years. There really isn't new about this subject matter.

Stick to the advice of your local engineering experts. Their knowledge comes from a long history of mistakes that brought about the electrical code.

Oh, by the way, the electrical code was mostly written by the fire department. Care to take a guess as to why?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 19
Good Answers: 1
#3
In reply to #1

Re: SEL-451 relay CT Connections, Delta or Wye

12/01/2014 8:44 PM

In my original post, the relay engineer has less experience than I have, and I believe him to be mistaken.

You mention 100 years, I'm getting close, and then you divide by 1.732 and I'm there :-).

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4
In reply to #3

Re: SEL-451 relay CT Connections, Delta or Wye

12/02/2014 8:25 AM

OK, I get it now. But before I spend the time thinking about this problem, I would like to ask for clarification. In your original post, you mentioned three CT's on two lines of a generator (if I remember correctly). It would be helpful if you could upload a sketch of this arrangement.

I believe this is a good question but I think the relay engineer may have jumped to his conclusion before he understood what you asked of him. Unfortunately, that is a common mistake. It should be easy enough, however, to test this and I know just the place where you will be likely to obtain a correct answer for free.

What I am thinking about is how the current in a delta configuration might be re-mixed with other currents when it is converted to a "Y" configuration. The signal would still be there but it's magnitude would be reduced causing the relay to miss the event. The laws of conservation say that the signal is merely split or shared by the other devices thereby making them less sensitive.

Please sketch and upload the existing and proposed configuration that you described. I think it will help to produce some better answers. I like to use MSPaint because it is so easy to use. Create the drawing, save it, and attach using the camera icon in the editor and then we should be on track to providing a meaningful answer or direction.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Associate

Join Date: Apr 2014
Location: Erie, PA
Posts: 44
Good Answers: 1
#5
In reply to #3

Re: SEL-451 relay CT Connections, Delta or Wye

12/03/2014 11:39 AM

Does that mean you'll be 58 on March 6th?

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: SEL-451 relay CT Connections, Delta or Wye

12/01/2014 9:41 AM

I would contact SEL and follow all of their requirements for the relay you are using.

Any deviation from the SEL wiring requirements will render the relay(s) inaccurate or inoperative.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."