Is Protecting Relay Coils Essential or Not?

12/14/2014 4:08 AM

I recently moved to another company. In my ex work place, we had to group all relay coils and indication lights for motor control centers and place them down stream a fused(4A) channel for protection. With my current employer, they said its not important. After reviewing some of their drawings, I noticed that they have linked relay coils directly across a 220V AC line and N down stream a 25A MCB. My ex employer used to claim that doing so would present a short circuit potential across the coil and is not acceptable, but my new employer seem to find it insignificant, and since my experience is fresh, I'm confused as to what perspective to adopt to be more valid in common practice.

Your insight is appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Is protecting relay coils essential or not?

12/14/2014 9:08 AM

If you want to keep your job, adopt the perspective of your new employer.

Register to Reply Good Answer (Score 2)
2
Anonymous Poster #1
#2
In reply to #1

Re: Is protecting relay coils essential or not?

12/14/2014 9:56 AM

Seriously Lyn?! At the very least he should cover his own butt and make sure he's not liable for any potential safety violations or equipment damage. If he's got a conscience he should re-think whether he really wants to work for this employer.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #2

Re: Is protecting relay coils essential or not?

12/14/2014 10:38 AM

1. "I recently moved to another company".

2. "they said its not important."

3. "My ex employer used to claim that doing so would present a short circuit potential across the coil and is not acceptable, but my new employer seem to find it insignificant."

Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#9
In reply to #1

Re: Is protecting relay coils essential or not?

12/14/2014 1:24 PM

funny guy :))

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#3

Re: Is protecting relay coils essential or not?

12/14/2014 10:06 AM

What wire size are you using for the control wiring to these relay coils and indicator lights? They better support 25A. I'm not aware of any code exceptions, you have to always protect the wire by a properly sized fuse or CB.

Me thinks your employer needs to be enlightened. Or not, as Lyn suggests.

Use the code book as justification for what is correct in your industry.

But fault current at 240V through a 25 amp MCB, probably will exceed the fusing current of the control wiring. If you've ever dealt with the trip time of circuit breakers, while sustaining fault current, you learn not to violate the wire size requirement.

My experience was running power through printed wiring boards in avionics. As a kid engineer, I found no one could give me guidance on this. The drafting department would ask you what the steady state current was, and design circuit traces to support that. I had to learn about fault current from my product during flight test. It took an electrolytic capacitor failing short in the power supply. Which smoked the circuit trace, and never tripped the breaker. So it glowed converting FR4 board material to carbon, then ash, which released major amounts of smoke. What made is worse was these traces burn like fire cracker fuses, and if they cross paths with other power traces, or something as innocent as +28/open discrete inputs (which is powered from a +28 CB), it started them on new burning paths. The current level will never trip the breaker. At least I learned something from it.

__________________
ignator -
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#11
In reply to #3

Re: Is protecting relay coils essential or not?

12/15/2014 4:13 AM

Typically there are so many ways component can fail and even catch on fire, without tripping a breaker or blowing a fuse. In the O.P.s case, a 4A fuse on a 220V line would still allow a downstream fault to consume 880 watts for a period of time without blowing the fuse. A kW-scale fault for a minute easily has enough power to start a fire. Yes, 4A is a safer limit than 25A, but neither is perfect. Instead one has to use reliably-built relays (thankfully, fully-shorted relay coils are rare, shorts across a few turns are more likely), and mount them overall in metal boxes to contain any high-power fault fires. We've often heard of TVs or computer monitors catching fire, and causing serious trouble, burning down houses etc. Those devices are internally fused, at a fairly low level, but that didn't prevent the fires. Too bad they were made in plastic rather than metal boxes. At least their power supplies could have been in metal boxes (closed-frame) inside the unit. Damn, every plastic-boxed wall wort, rug wort power supply is a walking time bomb, to mix metaphors.

__________________
Thanks, Win
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#4

Re: Is protecting relay coils essential or not?

12/14/2014 10:12 AM

At least approach/notify your Boss once. Trice will be an insult to superiority. Then carry on. If something bad happens, it's his call.

What's the probability of getting a short circuit? How much money and possible collateral damage would result for a short circuit event? If the odds are little, may be by experience your Boss is on the edge of it from experience.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply Score 1 for Good Answer
4
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#6

Re: Is protecting relay coils essential or not?

12/14/2014 11:56 AM

There is a fundamental misunderstanding here. Fuses and circuit breakers do not protect loads (relay). A current tripping device protects the wiring to these loads. It is also incorrect to consider these devices as current limiting devices. These devices are rated by the maximum current they will permit continuously. For a limited amount of time a fuse and circuit breaker will permit more current to flow.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 4)
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#7
In reply to #6

Re: Is protecting relay coils essential or not?

12/14/2014 12:18 PM

May be the main concerns of the OP is the interruption cause by a short circuit. If the equipment interrupts a mass production line which will eventually has a consequent down time and losses due to it. Definitely no effect on the load equipment but to supply panel there is or wherever a short circuit fault device is located.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Is protecting relay coils essential or not?

12/14/2014 1:14 PM

If, "the main concerns of the OP is the interruption <of a mass production line>cause by a short circuit" why didn't they say so?

To what mass production line are you referring?

I got the impression that the OP is looking at random drawings.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Is Protecting Relay Coils Essential or Not?

12/14/2014 10:24 PM

To further the above opinions, you must also disavow yourself of the idea that a circuit protective device, be it fuse or breaker, will "present" a short circuit potential across the coil. That potential failure mode is ALWAYS there, whether the protective device is in the circuit or not, and regardless of it's size.The circuit protective device simply prevents that risk from causing a fire if it happens.

Now as to what size protective device to use, that depends upon two things: the size and rating of the conductors, and to some extent the ratings of the ratings of any switching devices in the circuit. 25A is probably too high even if your conductors are rated for 25A, because I don't know of any standard control circuit devices rated for moe than 16A and most are rated for 10A or less. The use of a 4A fuse may have been based on some small reed relay type devices in your circuits, often rated less than 5A.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#12

Re: Is Protecting Relay Coils Essential or Not?

12/15/2014 8:57 AM

Not sure what you are faced with but in most cases the individual control transformer located in each section of the MCC has it's own fuse based upon the transformer size and the wiring size downstream of the transformer.

As there are usually more than one device in control circuits there usually is not separate fuses for each device in each control circuit.

If one of the devices suffers any failure that presents a current overload that exceeds the control transformer fuse rating, the fuse will open.

A fault of an individual device such as a 200mA relay coil normally does not cause enough fault current in the circuit to interrupt (blow) the fuse.

I have seldom seen individual protective fuses for each device in any circuit.

Also; In many cases the control transformer is properly fused on the primary side and not on the secondary side to take advantage of the transformer impedance during fault conditions to limit the fault current.

The location of the fuse is up to the designer and the size is limited/dictated by the control power transformer and control wiring size which is dependent on the number of devices in the control circuit, the total control circuit current load requirement(s), and the physical restrictions of the switchgear.

If the wiring is of the correct size and the fuses are properly sized, it does not really matter where the fuse is located (primary vs secondary) as long as the fuse interrupts current flow before the wiring and/or transformer is damaged.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#13

Re: Is Protecting Relay Coils Essential or Not?

12/15/2014 11:13 AM

My experience with relay, solenoid and contactor coils is that of motion of the armature or moving part is restricted or complete closing is prevented, the impedance climbs. This can take place over a period of time. Determine what effect a rise in impedance has on the circuit.

__________________
CRTL-Z
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#14

Re: Is Protecting Relay Coils Essential or Not?

12/15/2014 1:05 PM

The draw current of the energized relay coil is very small. Consequently, the wire is also very small. If the coil manages to draw excessive current (long before it becomes a short circuit) it will become an Open circuit and it will no longer be operational. Consequently, it is likely to be more of a nuisance than a significant problem. I am curious as to how the ex employer would prevent a short circuited coil. Perhaps he meant to protect the wire to the relay with a fused power connection? That seems to be excessive concern over a relay unless it drives an auto-destruct circuit.

The usual concern is about the potential voltage spike caused by magnetic energy stored in the coil when the power is interrupted. V = L di/dt so when the current is interrupted the voltage can become very large. Zero cross over circuits help to keep this to a minimum. For DC coils, a simple reverse biased diode protects other electronics upstream.

By the way, a boss with a little bit of information is a dangerous thing. Frequently anything that goes wrong with an electrical circuit is called a "short" by people with only a little bit of information. But a short circuit and an open circuit are two very different conditions. Short circuits usually generate a lot of smoke and occasionally some fire. Short circuits are rare while open circuits are quite common.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); engilis (1); ignator (1); JRaef (1); lyn (3); NotUrOrdinaryJoe (1); Noudge79 (2); redfred (1); SHOCKHISCAN (1); Unredundant (1); Winfield Hill (1)

Previous in Forum: Ballast Data   Next in Forum: Automatic Monitoring of Distribution Transformers

Advertisement