Previous in Forum: Is Protecting Relay Coils Essential or Not?   Next in Forum: LED Lighting Problem
Close
Close
Close
7 comments
Rate Comments: Nested
Anonymous Poster #1

Automatic Monitoring of Distribution Transformers

12/14/2014 6:00 AM

In my project i fail to know which mechanism can i use to shutdown the distribution transformer of 11kv automatically once a fault has been detected.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#1

Re: Automatic monitoring of distribution transformers

12/14/2014 10:37 AM

You mean this fault?

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Anonymous Poster #2
#2

Re: Automatic monitoring of distribution transformers

12/14/2014 12:26 PM

what does you text book recommend?

Reply
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Automatic Monitoring of Distribution Transformers

12/14/2014 1:18 PM

How about an 11kV circuit breaker or switch fitted with a remote-trip option and connected in series with said transformer fault detecting mechanism.

More information can be found using an internet search.

__________________
jack of all trades
Reply Good Answer (Score 2)
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #3

Re: Automatic Monitoring of Distribution Transformers

12/14/2014 10:13 PM

That would be a case of the protection and switching system far exceeding the cost of the transformer. Typical pole top transformers are often marked CSP (Completely Self Protected), here's the specs on one brand. The other way it's done is with a loop recloser scheme, more expensive but more reliable, still uses the same CSP transformer, but controls the primary supply, it all depends how important the load is.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Active Contributor

Join Date: Feb 2009
Posts: 12
#5

Re: Automatic Monitoring of Distribution Transformers

12/14/2014 10:53 PM

I very important to got a VCB to open the high voltage side and a MCCB to open de low voltage side, for protect your transformer you have to use the high pressure valve with contacts for trip and for alarm, also use a differential relay to sense any current dis balance and trip the VCB in the high voltage side and also the low voltage side.if you have buchholz relay use the contact trip to work with the low an high voltage breaker

Hope this can help us.

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6

Re: Automatic Monitoring of Distribution Transformers

12/15/2014 1:53 PM

Then ask your Mentor.

__________________
Good moaning!
Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#7

Re: Automatic Monitoring of Distribution Transformers

12/18/2014 12:13 AM

(I'm assuming you're a student or just curious.) As the other posters mentioned, it all depends on what you want to achieve and why. Criticality of the transformer or the supply will dictate. If you are referring to small pole-mounted distribution transformers, a good old drop-down fuse setup could be quite adequate.

Reply
Reply to Forum Thread 7 comments