Dear All,

We have commission new VFD in our plant, during the start up of the plant we had run the VFD to 50% in DCS then increase to 100% full run, however when the reduce the speed to 0% all of a sudden the VFD trip. any advise please.

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#1

Re: VFD trip to 0%

12/19/2014 10:39 AM

That's a heck of a condition. It must be tired, feeling lazy at 0% it sleeps.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: VFD trip to 0%

12/19/2014 10:54 AM

The Force is not strong with me today, so I cannot read your mind to see what the trip display on the VFD said. Please use your fingers to transmit additional data by typing it into the keyboard.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #2

Re: VFD trip to 0%

12/19/2014 5:01 PM

haha

Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: VFD trip to 0%

12/19/2014 11:09 AM

Consider this: A VFD produces an output from nearly DC to frequencies much higher than you could possibly ever need.

Your motor is an AC device. As your VFD approaches 5% speed control, the output is effectively DC as far as the motor is concerned.

If you attempt to drive an AC motor with DC, the current will spike. I hope that explains what you need to know. If not, you should not be programming the VFD.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#5

Re: VFD Trip to 0%

12/23/2014 2:02 PM

I believe VFD is controlled by 4-20mA signal from DCS.

Check signal corresponding to 0 dose not fall below 4 mA at VFD.

Calibration of DCS signal may be required.

__________________