Anonymous Poster #1

Designing Or Sizing A Single Phase (50 Hz) UPS System

12/22/2014 4:48 AM

I read the old postings about UPS in CR4 but no good...So I would like to ask as I am uploading a simple standby UPS system diagram by Electrical Engineering World forum to get the point straight. (a) I may take a rated UPS to fit my needs (b) I may design my own for the load....Lets go both ways:

Assuming: I have a single phase critical load of 1500 W which would be supplied by the UPS in an event of main utility power shut down for at least 3 hours on on and off basis of main power load shedding...

(1) What sort of batteries? Parallel or series? I know it but not much my specialty :)

(2) Need to design or size an inverter to output 220 V single phase (no fluctuation)?

(3) Rating of inverter in KW and how much of input DC voltage be better suited, 12 V, 24 V or ...

(4) Sizing charger for the said batteries?

(5) You could see in the diagram that the main AC is feeding the charger before power failure. Any under/over voltage on the main before shut down hasn't been addressed. It's a fact that under voltage on the main happens on daily basis, so need to size an AVR/AVS or else on the main AC input? Wouldn't I need one on the inverter output of 220 V in case of battery back up system during main shut down?

(6) Would prefer Static Transfer Switch over ATS for electro-mechanical failure reasons? Any suggestions?

(7) Any recommendation on a control systems to make everything function etc. CPU, dial-up modem etc.

(8) Charging and discharging times?

(9) etc.

Thanks in advance!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Designing or Sizing a single phase (50 Hz) UPS System

12/22/2014 4:52 AM
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#8
In reply to #1

Re: Designing or Sizing a single phase (50 Hz) UPS System

12/22/2014 2:36 PM

What? No safety ground!?!

Preposterous!

Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Designing or Sizing a single phase (50 Hz) UPS System

12/22/2014 6:28 AM

Why bother building one when you can go out and buy a commercial one for far less that will work right the first time and every time?

Most any 2000 VA or larger commercial unit will carry 1500 watts as long as what ever battery bank you have it attached can hold it up.

Price would be around $200 - $300 American (you will never build one for less) fora good used one plus what ever your battery bank sets you back.

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6
In reply to #2

Re: Designing or Sizing a single phase (50 Hz) UPS System

12/22/2014 10:27 AM

I second that notion

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#7
In reply to #2

Re: Designing or Sizing a single phase (50 Hz) UPS System

12/22/2014 12:31 PM

I third it.

__________________
Good moaning!
Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#9
In reply to #7

Re: Designing or Sizing a single phase (50 Hz) UPS System

12/22/2014 11:04 PM

Fourth it.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Designing Or Sizing A Single Phase (50 Hz) UPS System

12/22/2014 9:04 AM

Take your requirements/questions to three different UPS suppliers and ask therm.

Even if someone here tried to explain it to you, you'd still need thehelpofyouru PS supplier.

Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#4

Re: Designing Or Sizing A Single Phase (50 Hz) UPS System

12/22/2014 9:09 AM

Try APC!

They most likely have a solution for you off the shelf!

http://www.apc.com/tools/wizard/home/zoneForm.cfm?ISOCountryCode=us&gclid=CJz95srp2cICFROTfgodVysADQ

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#5

Re: Designing Or Sizing A Single Phase (50 Hz) UPS System

12/22/2014 10:13 AM

Ametek has sorts of products like this. Powervar their user manual has its diagram and basic features you could find as a reference to your design. Nothing special about it other than switching ac to dc inverter power in times of interruption, although some design adds up surge protection and flitering features. You could even google some wiring diagrams of this stuff. Use google image.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
3
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#10

Re: Designing Or Sizing A Single Phase (50 Hz) UPS System

12/22/2014 11:41 PM

I recommend an on-line UPS where the inverter is always supplying the load and the only thing that changes is the battery charger stops working when the utility power is not up to snuff. These are also sometimes known as dual conversion as well. Some loads will not operate correctly when an off-line UPS switches from the mains to the inverter. The delay that invariably occurs can cause all kinds of problems. All depends on the nature of your load. For three hours of load backup, you will need a substantial external battery bank. For rough estimates, you will need 27 amp hours at 220 volts (2 kVA) multiplied by an efficiency penalty factor of about 1.2 to account for inverter losses.

A GC2 6V battery for a golf cart is about 200 amp hrs for an approximate energy of 1.2 kW-hrs. Of course that is discharging the battery down to nothing which does not make for good battery life. A good rule of thumb is to take about half its capacity per event. So if each GC2 battery is good for about 0.6 kW-hrs, and you need about 7.2 kW-hrs then twelve GC2 lead-acid batteries will make for a robust UPS.

That's only 744 pounds or 338 kilograms of batteries.

You can shave the battery down in size if you can add an automatic start generator that will pick up the battery charging if the power is off for more than five or ten minutes. Short outages will be carried by the smaller battery bank and the generator keeps things going for the longer outages.

Reply Good Answer (Score 3)
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#11

Re: Designing Or Sizing A Single Phase (50 Hz) UPS System

12/23/2014 1:28 PM

What you have described as well as shown in your drawn wiring diagram is an emergency power source, NOT a UPS! Similar to an emergency light scenario, will operate only when regular power source is interrupted... It is battery powered that get recharge via regular power source.

In a real sense of true UPS system, the load is always connected to it, (need No transfer switch), regardless whether the outside commercial power is available or not. The pre-conditioned UPS output power is always provided, with or without commercial source, and until a predetermined length of time which is typically dependent on the type of battery used and its state of charge condition!

This type of system is more elaborate to design or expensive to acquire. Mostly recommended for critical loads and applications!

Good luck!

__________________
vsar
Reply
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Brave Sir Robin (2); Crabtree (1); cuba_pete (1); Fredski (1); lyn (1); Noudge79 (1); Original_Macgyver (1); tcmtech (1); vsar (1)