I HAVE DESIGNED A ELECTRICAL BUS DUCT SYSTEM
BUS BAR RATING : 4000 AMPS
BUS BAR MATERIAL :ALLUMUNIUM
CONFIGURATION : PHASE 4x( 120x10) mm AL FLAT /PHASE
NEUTRAL : 2 X ( 120 x10) AL FLAT
OVER ALL LENGTH OF BUS DUCT : .8 METER
ATMOSPHERIC TEMPERATURE 40 C MAX & 2 C MIN
MY QUESTION IS THAT WHAT TECHNIQUE SHOULD BE USED TO COMPENSATE THE EXPANSION & CONTRACTION OF THE BUS BAR LENGTH DUE TO CHANGE IN ATMOSPHERIC TEMPERATURE
S.GHOSH
Re: ELECTRICAL BUS BAR
12/22/2014 12:34 PM
Do keep the noise down, Mildred. There's no need to SHOUT. And if you haven't allowed for expansion then the design is incomplete.
Good moaning!
12/22/2014 1:35 PM
Re: Electrical Bus Bar
12/22/2014 4:28 PM
Point of clarification.
You have PARTIALLY designed a bus duct system. Now, do the rest of the design. That's the mechanical part you don't have yet.
12/22/2014 6:39 PM
you call yourself a designer???????
Good Answers: 19
12/23/2014 10:59 PM
It is not clear whether the these busbars will be mounted inside steel enclosure. Enclosure size is required. Normally the bus trunking systems are designed for an ambient temperature of 50 deg C and final temperature of 85 deg C.It is not clear for what atmospheric conditions these bustrunking systems are designed, In any case 4 x120 x10 mm aluminum busbars per phase will not carry 4000 Amps. Derations have to be applied. Please therefore reconsider your design and selection of busbars.
The busbars selected by you will carry 4200 A open air .Derating has to be applied for temperature, enclosure design etc.
Ramesh,Freelance Electrical/automation Consultant
12/26/2014 12:42 PM
DEAR SIR
THANK YOU VERY MUCH FOR YOUR RESPONSE
I DO NOT HAVE ANY DOCUMENTATION IN CONTEXT TO DE RATING FACTOR .WILL YOU BE KIND ENOUGH TO SUGGEST THE DE RATING FACTOR OR ANY DOCUMENT WHICH CAN HELP ME IN DECIDING UPON THE DE RATING FACTOR.
THANKING YOU
S.GHOSH
Good Answers: 42
12/27/2014 2:23 PM
lyn proposed "ch.13 Bus Conductor Design and Applications" is very good. You may have the entire Aluminum Conductor Handbook:
http://www.aluminum.org/sites/default/files/Aluminum%20Electrical%20Conductor%20Handbook.pdf
The ABB Switchgear Manual 11th ed. ch.4 you can follow also in order to calculate the busbar.