Tripping bcz of Earth Leakage Relay

12/28/2014 2:30 AM

We recently trying to start 75KW motor, we found tripping of ELR relay in the feeder of the motor.we meggered with 1000V and found value to be good. We laid 2 run cable for this motor of 95sq.mm. Changed the Earth lekage relay of the feeder also. And checked the relay setting too which perfectly matches with the existing ELR setting of 75KW motor. Earth cable has been laid from feeders nd terminated in good way nd also local field earthing found to be good. Please help us to diagnose the trip which is happening..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#1

Re: tripping bcz of Earth lekage relay

12/28/2014 8:25 AM

I suppose this is an ac 3 phase motor? right? at 15KW or more, correct me if I'm wrong, ac motor goes 3 phase.

1) Conduct insulation test of motor windings (L1, L2, L3) including earth what were the readings MegaOhms? See NEMA standards. You should get more than 76MegaOhms resistance to ground per line as per the NEMA standard.

2) Like wise, do an insulation test with the wires running from feeder to motor and earth leakage as well, what were the readings.

I suspect, you said you run only 2 wires for this, right? Must be lacking one, no wonder your ELR trip off. Is this be even possible?

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3
In reply to #1

Re: tripping bcz of Earth lekage relay

12/28/2014 11:11 AM

OP said "two cables". This doesn't necessarily mean "two conductors".

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: tripping bcz of Earth lekage relay

12/28/2014 9:56 AM

It has become evident that there must be a shortage of qualified electricians in the world.

I say that because of the astronomical number of people who come here and ask the forum to fix their electrical problems for them. Usually without providing any meaningful information.

And of course expecting to get their problems explained to them and solved for free.

Either it's a shortage of electricians or an excess of cheap-ased people who want others to work for them for free.

I'll go with # 2.

Hire a qualified electrician!!!!!!!!!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Tripping bcz of Earth Leakage Relay

12/29/2014 12:02 AM

Is it tripping during starting or after how long,did you measure starting current,time,vd etc

__________________
pnaban
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #4

Re: Tripping bcz of Earth Leakage Relay

12/29/2014 12:05 AM

What kind of starter is used,is it VFD,if so contact VFD specialists.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: Tripping bcz of Earth Leakage Relay

12/29/2014 1:21 AM

Mohsin Hamid,

You haven't come back with details to the queries of other posters. Let us know if you have solved the problem and details thereof.

In case you haven't, here is my penny's worth: Hope the ELR is connected to CBCT.

* Please check the power cables are centered properly. You mentioned there are two cables (3-core cable each, hopefully). Both have to be reasonably centered in the CBCT window reasonably.

* Presuming the cables are armoured type. If true, is the armour brought back through the CBCT window? This is important and has been responsible for many a spurious trip.

* The pickup setting of ELR - make sure the setting is at least 6A. Too sensitive setting can cause spurious trip during motor start

Look forward to hearing from you.

__________________
Raghunath
Register to Reply
Commentator

Join Date: May 2011
Posts: 91
#7

Re: Tripping bcz of Earth Leakage Relay

12/29/2014 7:25 AM

Now changed the setting of ELR higher. Before it was 2 Amps. Now it runs good. How to calculate the ELR setting. I had heared ELR setting shld be as low as possible. Since the leakage will be very minimum why current setting shld be made to 5 Amps..??

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Tripping bcz of Earth Leakage Relay

12/29/2014 9:03 AM

Have you made any effort to learn, "How to calculate the ELR setting"?

Where have you looked for the answer, so far?

Or do you just want us to do that for you too?

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JohnDG (1); lyn (2); mohsinhamid (1); Noudge79 (1); pnaban (2); raghun (1)

Previous in Forum: Troubleshooting of Demag Crane Error 36 & 55   Next in Forum: VFD

Advertisement