Interruption of Power Supply

01/03/2015 3:06 PM

Utility power supply 400 volts ,50 hz , TT earthing system was interrupted thrice in two hours time.At the third time and while energy saving lights in ceiling where on , sparking took place from one lighting point in ceiling and burning drops of molten pvc wires insulation started falling down which lead to fire as it is a carpet store.The lighting switches got damaged but the 10 amps single pole circuit breaker feeding the circuit didnt trip .

We took out a lengh of about 3 meters back from the subject lighting point where the fire started ,installed in hollow block through slab, and found completely burnt insulation of wires and complete adhesion of copper of the phase and neutral wires .

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Interruption of power supply

01/03/2015 3:12 PM

Well then, get it fixed and install a circuit breaker that will protect the wiring next time.

That is, assuming you can figure out what caused the copper wire to melt.

Reply
Active Contributor

Join Date: Sep 2012
Posts: 11
#2
In reply to #1

Re: Interruption of power supply

01/03/2015 4:01 PM

My question is what had happened to lead to that situation and what is the impact of power interruption on what happened?

Reply Off Topic (Score 6)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Interruption of power supply

01/03/2015 4:53 PM

What have you been doing since 9-2012?

Not much, apparently.

Did you ever get your own copy of NFPA/NEC codes?

My advice is to hire a competent local electrician to explain it to you.

Reply Off Topic (Score 4)
Active Contributor

Join Date: Sep 2012
Posts: 11
#7
In reply to #1

Re: Interruption of power supply

01/04/2015 2:26 AM

It seems I didnt address my questionare right.

I am trying to find the reason behind wires melting all along the route to lighting switch and why melting drops has dropped only from one point that lead to fire accident.

The main topic is fire accident.

I have gone through Schneider White Paper 18 and made some conclusions on the issue

but still I like to have it discussed with you.

Regards and appreciated

Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #7

Re: Interruption of power supply

01/04/2015 7:14 AM

What you are asking for is a forensic investigation while providing us the least amount of information. A forensic investigation cannot be done properly in a forum. The best you will get here is a group of qualified and unqualified people making a collection of WAG that you will have to see if they fit the remains. There is also a lot of added information that must be known that you have not presented to us. A short list of unknowns: wire dimension, anticipated current draw, type of lighting, water damage prior to fire, wiring pathway, insulation thickness, age of wire, ambient temperature. There are also a collection of unknowns that can only be found by a careful examination during a tedious, systematic dismantle of the damaged wires.

Good Luck

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #7

Re: Interruption of power supply

01/04/2015 10:59 AM

As I said in #3, discuss it with a competent local electrician.

No one here can solve your problems and tell you how to resolve them, without seeing the aftermath.

I will suggest two options, then leave you to flounder.

1. See above. Hire a competent local electrician to explain it to you.

2. See above. Hire a competent local electrician to install a new electrical service that complies with all applicable codes.

Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#13
In reply to #7

Re: Interruption of power supply

01/05/2015 1:58 AM

The reason for wire insulation melting, most probable one, is loose connection at the light switch terminals. The loose connection leads to heating (high contact resistance giving rise to excessive heat) and consequent melting of PVC. The PVC melt drops are expected to fall near the loose connection point initially and further, depending on the slope of the wire conduit or the wire itself, the pvc melt drops may travel along the conductor before falling down at the appropriate location.

Hope it makes sense.

__________________
Raghunath
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Interruption of power supply

01/03/2015 4:54 PM

What many people forget is that circuit breakers do fail. Most of the time a circuit breaker fails but a short circuit does not happen so nobody knows of the failure. This is why regular maintenance and testing of circuit breakers is recommended, although few do it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#5

Re: Interruption of power supply

01/03/2015 10:31 PM

Have you contacted your local power provider and ask if there were any faults at their side? Or, asked neighbors probably at different distribution transformer.

Your describing a low voltage scene. It could be caused by upstream line fault of the affected wires and switches.

Say for example a 220Vac, 1A(220VA) equipment if voltage dropped a half, say, 110Vac then load will be sustained under (220VA). Thus, circuit current will be at 2 A. Worst is, if it drops lower than that.

I suggest you conduct ocular inspection on your power panel, there might be rodent or lizard infiltrated the enclosure and connected the buses. Also inspect all connected equipment especially motors. There might be failing equipment/transformer/winding that caused the low voltage.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#6

Re: Interruption of power supply

01/03/2015 11:24 PM

Circuit Breaker probably failed. They fail both to both open and closed. If it fails open it won't reset or flow electricity. If it fails closed it won't trip for an overload condition when it should.

Have a qualified licensed electrician do the following, at the least. Don't do it yourself unless you are a qualified licensed electrician!

Remove the old breaker and toss it. If the buss bars are aluminum have him coat the contact point on them with an appropriate anti-oxidation paste. Replace all the wiring on that circuit from the breaker panel to the fixture. Check it out to make sure it is correct. Connect the wire to an appropriately sized new circuit breaker and install that in the panel. Check all contacts and voltages. Also use a clamp on amp meter to assure that the appropriate current is flowing to the new bulb. This should be done at the panel. If that doesn't work, fire the unqualified licensed electrician and get the best, probably most expensive also, licensed electrician you can find. The money is a wise investment.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: Interruption of power supply

01/04/2015 5:49 AM

First of all the circuit breaker worked twice. It seems to me the available short-circuit current is more than the circuit breaker short-circuit current could withstand and at third time of interruption the contacts were welded and did not open.

If this is a reliable manufacturer at least 10 kA could be the rated.

I don't think the short-circuit in a lighting circuit could be more than 2-3 kA.

In this case the circuit breaker was damaged or poor manufactured.

__________________
Julius
Reply
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#11
In reply to #8

Re: Interruption of power supply

01/04/2015 7:23 PM

Hi,

The kA rating of the CB should be the same as the in both cases you are looking to have the CB operate in a fault situation where the short-circuit is on the distribution network side of the demarcation point. Typically the magnitude of the fault current is this is driven by the fault current at the zone sub-station, and is then moderated by the impedance of the conductors and distance of the installation from the zone sub-station.

Looking at a spreadsheet of maximum fault currents at zone substations on my employer's network the maximum P - G is 15kA and the minimum is 2.77kA (P-P is slightly less in each case).

Reply
Active Contributor

Join Date: Jun 2014
Posts: 19
Good Answers: 1
#12

Re: Interruption of Power Supply

01/04/2015 11:23 PM

Hi,

Insidious high resistance L-N fault likely happened the first 2 times due to failing insulation - your lighting point terminals have come loose? - I2R heating! The overcurrent device (OCD) probably tripped on thermal; these events precipitated a short circuit the third time which the OCD could not handle because of:

(i) poor quality OCD

(ii) interrupting capacity of OCD is less than the prospective short circuit current at the point of short circuit.

Regards

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: Interruption of Power Supply

01/05/2015 3:34 AM

Sounds like it was an arcing ground (earth) fault, which if the resistance is high enough, will keep the current too low to trip the circuit breaker, but create heat high enough to melt the wire insulation. It's not as uncommon as one might think, in fact here in the US we now must use new types of circuit breakers called "Arc Fault Circuit Interrupters"(AFCIs) in places where that type of fault can lead to fires.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#17
In reply to #14

Re: Interruption of Power Supply

01/07/2015 5:50 AM

I always thought arcing grounds are relevant in MV systems!

Can wire capacitance be that significant in LV systems to cause arcing grounds!!

__________________
Raghunath
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#18
In reply to #17

Re: Interruption of Power Supply

01/09/2015 12:11 AM

In my opinion this phenomenon is a little bit more complicate. See [for instance]:

http://www.neiengineering.com/wp-content/uploads/2012/05/Arcing-Fault-Current-and-the-Criteria-for-Setting-Ground-Fault-Relays-in-Solidly-Grounded-Low-Voltage-Systems.pdf

__________________
Julius
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15

Re: Interruption of Power Supply

01/05/2015 11:06 AM

I agree with jraef. For instance a 2.5 mm^2 copper will melt in 5.7 sec. for 300 A

and 1.5 mm^2 at 180 A will melt in the same time.

300 A it is 30*Irated of the circuit breaker [Irated=10 A].

According to Circuit Breaker Characteristic Trip Curves and Coordination Bulletin No. 0600DB0105 Data Bulletin [Square D] the circuit breaker will trip in 10 to 30 sec.only.

__________________
Julius
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16
In reply to #15

Re: Interruption of Power Supply

01/05/2015 12:20 PM

Sorry! My glasses! It will be for 30 A [3 times Irated] the circuit breaker will trip in

10 to 30 sec. but the 1.5 mm^2 copper wire will melt in 20 sec.

__________________
Julius
Reply
Reply to Forum Thread 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: