Paralleling of 66KV Lines

01/07/2015 12:28 PM

Two 66kv lines one comming from 132/66kv substation and other comming from 220/66kv substation both line parallel at one 66kv bus the load on both line after paralleling is more than the actual load it is morethan single line load what is the reason? And which factor affected?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: paralleling of 66kv lines

01/07/2015 12:45 PM

Circulating currents because of badly matched transformers feeding your incoming 66kV lines. Call the utility.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: paralleling of 66kv lines

01/07/2015 1:50 PM

60 is right on. The 220 kv sub is carring the load and part of the load connected to the 132 kv sub. I suspect that you have a back feed, reverse power flow, from 220 kv sub thru the 66 kv system to 132 kv other load.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: paralleling of 66kv lines

01/07/2015 1:58 PM

Assuming for the moment that this is an authorized connection, could you please tell us how you are measuring your load and what those measurements are. I suspect that you are only viewing some of the data that makes for a valid analysis, such as only using Amps and Volts when you actually need the MW, MVAR for each line to make a valid conclusion.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#4

Re: Paralleling of 66KV Lines

01/08/2015 7:58 AM

Hi,

Welcome to CR4. Your question is unclear. Are you involved with these power lines? I can only assume that paralleling them will increase the maximum load if done correctly. If not, see Lyn's picture.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman