Bus Bar Ampere Rating from Existing Switchboard Data

01/14/2015 4:20 AM

Hi,

Anybody could advise how to find the Ampere rating of an Existing Switchboard from the available bus bar size?

Bus Bar size : 100x6-2 Copper, tin plateed, 440V, 50kA Short circuit Rating, 60 HZ. Ambient temperature 45 deg.

Can we use the thumb rule 1000/Sq. inch or 1.25A/sq.mm??

Un-fortunately no bus bar ampere rating is provided on the available data sheet.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#1

Re: Bus Bar Ampere Rating from Existing Switchboard Data

01/14/2015 6:23 AM

Those are good approximations of course, not to be relied upon. If the board/data sheet doesn't have a rating on it then it probably doesn't comply with switchboard standards in all sorts of ways, not just the current rating (e.g. IEC60439-1 or now IEC 61439-2).

__________________
rogerggbr
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2
In reply to #1

Re: Bus Bar Ampere Rating from Existing Switchboard Data

01/14/2015 11:24 AM

In my opinion you are right. In IEC 60439-1/1999-2004 Table 9 for 2 copper bars of100*5 the rated current is 1600 A. Tested for 1250 to 1600 A the temperature rise could be 23-25 K then ambient max. 45-47 K. [70 K rated temp. Table 2].

However, no calculation way is actually indicated here.

__________________
Julius
Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#3

Re: Bus Bar Ampere Rating from Existing Switchboard Data

01/14/2015 10:32 PM

You cannot determine ampere rating from bus size since it also depends on structure of switchgear and movement of air for cooling. What you will get is a range of amps. If you do not know the rating you must use the lowest value given, not the nominal one and go with that. The amount if any of insulation on the bus bar will inhibit cooling. The other consideration is the type of insulation, which could have a temperature limit. If the manufacturer is still in business, they will give you the values. The other possibility is to look up old catalogs from the manufacturer for the time period when the switchgear was manufactured.

Reply Score 1 for Good Answer
Anonymous Poster #1
#4

Re: Bus Bar Ampere Rating from Existing Switchboard Data

01/15/2015 12:26 AM

Thanks to all for the valuable answers:

Regards

Subhash

Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#5

Re: Bus Bar Ampere Rating from Existing Switchboard Data

01/15/2015 5:53 AM

If no other info available, I would guess the rating is the same as the incoming breaker. THis would put you on the safe side...

Reply
Active Contributor

Join Date: Jun 2011
Posts: 19
Good Answers: 1
#6

Re: Bus Bar Ampere Rating from Existing Switchboard Data

01/15/2015 8:02 PM

temperature rise alone does not do it.

The forces during short circuit are big and bus bar bracing need to be considered.

Reply Score 1 for Good Answer
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); 7anoter4 (1); Anonymous Poster (1); dennis461 (1); obouill (1); rogerggbr (1)

Previous in Forum: 100% Efficient Incandescent Bulbs   Next in Forum: E-Stop Circuit

Advertisement