Sizing Neutral Grounding Transformer

01/19/2015 5:03 AM

Hie all

I have a distribution transformer 50MVA 132/11kV YNd11. The phase to ground fault level at 11kV is 670A/phase to give a neutral current of 2.01kA. How do I calculate the rating of the earthing transformer on the delta side together with the series resistor size.

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Sizing Neutral Grounding Transformer

01/19/2015 8:13 AM

Some combination of these?

Register to Reply
Participant

Join Date: Jan 2015
Posts: 3
#2
In reply to #1

Re: Sizing Neutral Grounding Transformer

01/19/2015 8:47 AM

Hie lyn. The problem is on the formula to use for my calculations. Please may you help me.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Sizing Neutral Grounding Transformer

01/19/2015 11:16 AM

Here are a couple of links that can help you determine the parameters needed for your grounding transformer. If you don't understand them, then you need to hire a qualified electrical engineer to do the calculations for you.

http://www.pacificcresttrans.com/grounding-transformer-faqs/

http://forums.mikeholt.com/showthread.php?t=53152

Be careful! If you still aren't sure, get outside help.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6
In reply to #3

Re: Sizing Neutral Grounding Transformer

01/20/2015 12:38 AM

First of all I agree with you.

However, in my opinion IEEE could be a basis at the beginning:

IEEE 32 IEEE Standard Requirements, Terminology, and Test Procedures for Neutral Grounding Devices.

Clause 2. Basis for Rating.2.2 Rated Current.

"Unless otherwise specified, the basis for this rating shall be the thermal current. This will be the current through the neutral device during a ground-fault condition at the device location."

__________________
Julius
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Sizing Neutral Grounding Transformer

01/19/2015 1:01 PM

You don't. Without knowing the nature of the 11kV loads and how they're connected leaves you with no way to know if and when fault current even flows. Also anyone who adds a vector quantity like phase currents without considering the phase angle isn't qualified to do this type of work. The only safe and ethical thing to do is remove yourself from this job or subcontract the work to a qualified electrical engineer.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Sizing Neutral Grounding Transformer

01/19/2015 3:53 PM

Given this is a 50MVA distribution transformer you are talking about I am assuming this is simply a homework question.

We don't do homework questions here on CR4 (please view site rules).

__________________
jack of all trades
Register to Reply
Participant

Join Date: Jan 2015
Posts: 3
#7

Re: Sizing Neutral Grounding Transformer

01/20/2015 1:07 AM

From what I have done so far, I just calculated the line to ground fault level for the circuit. What am not sure now is that do I really have to use the fault level for that circuit or I have to multiply it by a certain multiplier to come up with the rating of the grounding transformer

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); jack of all trades (1); lyn (1); PeterT (1); proslion (2); RAMConsult (1)