Air Handling Units: Precision?

07/09/2007 6:04 AM

What is the difference between Air Handling Unit and Precision Air Handling Unit

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#1

Re: Air Handling Units: Precision?

07/09/2007 1:21 PM

Some airhandlers re circulate the air while other have to filter and remove the air incase the filter fails. You would not want a fume removal system to pump the same air back into the space. If the filter fails then you have a hazardous and maybe a explosive problem. Plus the motors would be sealed to prevent fire, explosions and harm to the motors.

__________________
If you never do anything you never have problems.
Register to Reply
Power-User
Fans of Old Computers - PDP 11 - New Member

Join Date: Mar 2007
Location: In a mushroom field somewhere in Canada. Kept in the dark and fed sh--, well you know.
Posts: 312
#2

Re: Air Handling Units: Precision?

07/10/2007 9:08 AM

Precision Air Handling Units have metering devices on them to allow you to adjust airflow. Non-precision units do not.

__________________
Dirt is for vegetables. Pavement is for racing.
Register to Reply
Power-User

Join Date: Feb 2007
Location: Nebraska
Posts: 104
Good Answers: 2
#3

Re: Air Handling Units: Precision?

07/10/2007 11:32 AM

I'm not sure what you mean by a Precision AHU but the closest thing I can think of are AHU's for Clean rooms. If you are looking at a class 100,000 room then in most cases you have one AHU for each room. Each AHU have filteration in each unit as well as filteration at the diffusers and return grilles. They control humidity as well as temperature. These units are specalized units made just for the clean room industry.

The other place that they need a great deal of control are Operating Rooms. These units are very special as well. OR AHU units are mostly all in one units which control Supply temp, humidity, relief air, and fresh air as well as all of the filtation needed for the rooms. They also include air flow measuring stations the monitor the airflow. Where as the Clean room units need a lot more support. Special exhaust systems, airvalves to control the airflow into and out of each room as well as AHU's to condition the freshair.

I hope this helps.

Register to Reply
Member

Join Date: Jul 2007
Posts: 8
#4
In reply to #3

Re: Air Handling Units: Precision?

07/18/2007 1:02 AM

yes your decription really aware of the thing to me thanks a lot

Register to Reply
Anonymous Poster
#5

Re: Air Handling Units: Precision?

07/29/2007 5:53 PM

Precision Air is A brand (manufacture) name