Transformer Rating

01/21/2015 6:33 PM

I'm designing a circuit with 16 contactor whose operating coils are in parallel. The inrush VA rating for each coil is 75VA 120VAC. I calculated the total inrush current to be 10a. What size transformer should I use 480VAC\120VAC 1500kva or 480VAC\120VAC 2500kva?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Transformer Rating

01/21/2015 7:07 PM

Me thinks you have made a large mistake... 1500 kVA or 2500 kVA. You mean 1.5 kVA or 2.5 kVA right?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Active Contributor

Join Date: Jan 2015
Posts: 13
#5
In reply to #1

Re: Transformer Rating

01/21/2015 8:06 PM

I meant 1.5kva and 2.5kva you're right thanks. I have 16 powerflex 40 drives. When we activate the estop it kills the 480 to the drives. On power up sometimes we lose the internal supply in the drive and have to replace it. We want to reconfigure the circuit by adding a contactor between the drive output and the motor.we keep the power on the drive constantly and active the contactor during an estop. I need to upgrade my transformer to handle the inrush current from the additional contactors. 16 total. 10amps of inrush current. We are currently we using a 480\120 1.5kva. What do I go to to handle the added current? 2.5kva?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Transformer Rating

01/21/2015 7:10 PM

Kva is way overkill; 1000va might even suffice. The inrush load will be brief. However, I would check with the transformer and coil manufacturers that the momentary voltage dip is still enough to pull in the coils.

Would it be possible to energize some and then the remainder of the coils in two steps?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Transformer Rating

01/21/2015 7:38 PM

I am a little confused. Based on your previous question you appear to be trying to start 16 motors simultaneously using what appear to be DOL motor starters. Why DOL and why simultaneously? How large are the motors and what are the motors driving?

What exactly are you trying to do and why are you not using either soft starters, 480V control coils without the transformer, etc. Are you qualified to perform this work as the content of your posts is worrying?

Can you please provide more information on your application.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Jan 2015
Posts: 13
#4
In reply to #3

Re: Transformer Rating

01/21/2015 7:53 PM

We have allen bradley powerflex 40.whenever the estop is hit it kills the 480 to the drive. On power up the drive loses the internal power supply. We wanted to keep the power on the drive continuously and add a contactor on the output to isolate the motor from the drive during an estop. I have 16 drives to isolate. I need to upgrade the control transformer to feed the additional contactors

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7
In reply to #4

Re: Transformer Rating

01/21/2015 8:23 PM

If it were me I would run the E-stop to the drive's E-stop to allow the drive ramp down function if necessary (load dependent) along with keeping the electronics live for rapid restart and then use padlockable isolators next to the motors for electrical isolation (visual indication of electrical isolation and ability to lockout for maintenance are important safety features recommended or required in many countries).

However it depends on your countries local codes.

Also be aware that opening contactors on the live output side of the drive can result in drive damage and parallel contactors won't help if a single motor needs to be taken off line for maintenance.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13
In reply to #4

Re: Transformer Rating

01/22/2015 2:13 AM

You still haven't said why you want to restart all these motors at once. I fear for the main supply fuses. Bu%%er the control transformer!

__________________
Good moaning!
Register to Reply
Active Contributor

Join Date: Jan 2015
Posts: 13
#6
In reply to #3

Re: Transformer Rating

01/21/2015 8:18 PM

We have 16 powerflex 40 drives. Whenever the estop circuit is activated it kills the 480 to the drives. On power up sometimes we lose the drives internal power supply and have to replace the drive. We wanted to add a contactor between the drive and the motor so when we activate the estoppel the 480 stays on the drives and the contactor isolates the drive and motor. We are currently using a 480\120 1.5kva control transformer. The additional contactors pickup current is 10 amps total. Would going to a 480\120 2.5kva provide enough current for the additional contactors?

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #6

Re: Transformer Rating

01/21/2015 8:30 PM

Would going to a 480\120 2.5kva provide enough current for the additional contactors?

Sure, but I don't recommend this contactor system as a way of isolating the motors, especially if the drive is going to still be running under load when the contactor on the drive output opens.

The drive manual should indicate that this is not recommended by the manufacturer as it could cause damage to the drive, and it certainly isn't recommended if you plan on leaving all the drives running at full output then throw all the contactors closed to restart the motors for obvious safety and maintenance reasons (ie using the contactors as motor controllers rather than no-load isolators).

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2015
Posts: 13
#12
In reply to #3

Re: Transformer Rating

01/21/2015 11:34 PM

Thanks you guys were very helpful. Norris534

Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Transformer Rating

01/21/2015 9:20 PM

Aside from this being a bad idea from the outset as JOAT said, the formula for correctly sizing a CPT is to take the square root of the (total inrush)2 + (total sealed)2

But since you will not have any other contactors sealed in already at the time you do this, it really is going to be just the total inrush.

Since you did not provide us with those values or anything else to go by, (other than if it is a PF40 the motors are 15HP or less), we cannot assess your determination.

SWAG: typical IEC contactor for 10-15HP (Allen Bradley 100-C23), inrush data on the coil is 70VA, so 16 contactors comes to 1120VA inrush. If you use a good quality CPT like at A-B 1497, not a cheap piece of junk, it has a higher inrush capability without falling out of acceptable regulation ranges. So a 350VA CPT will handle 2298VA inrush and maintain 90% secondary voltage, assuming a 40% PF, which may be a little high, but you've got lots of wiggle room there. If you use a general purpose distribution transformer or some other piece of cheap junk, you will need 1200VA minimum, so since they jump from 1000 to 1500, you had better go with the 1500VA. I would opt for a good quality smaller transformer if it were me.

Now, if this is a new project and you don't already own the drives, start over with the PF525 and forget the contactors, you can use the Safe Torque Off feature that is built-in. The PF40 is not capable of that, the design is too old.

But if you do already have the drives and need to do this, take the following precautions:

1) Use a N.O. aux contact of each contactor fed to the drive to break the I01 input (Stop) if the contactor opens. The Aux contact will open before the main contacts open, so the drive will turn off immediately before you open the contactor, saving you from the misery of blown transistors. This will also prevent someone from closing the contactor with the drive already enabled, which is often instant death for the drive.

2) Remove the "Enable" jumper from the PF40 (RTFM), it makes it so that taking power off of I01 immediately turn the output off. If you have another reason to want controlled Decel under all by E-stop conditions, set up another of the inputs as a "normal Stop" and program the Stop functions the way you want it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Jan 2015
Posts: 13
#10
In reply to #9

Re: Transformer Rating

01/21/2015 10:04 PM

13 of the drives are 2hp, 3 are 1hp and l'd planned on connecting the enable through the aux contactors to shut down the drives. Currently and additional MCR contactor removes the 480 from all drives when the estop is activated. Total inrush^2 + total sealed^2 square root is coil impedance, correct? Recommended 525 but we have to upgrade the plc also. Company would rather replace the unit than do that. It's a pallet wrap machine. Should I use a transformer just to feed the contactors alone? That's what I had in mind. PLC is a 500.

Register to Reply
Active Contributor

Join Date: Jan 2015
Posts: 13
#11
In reply to #9

Re: Transformer Rating

01/21/2015 10:10 PM

MAde a mistake, total power not impedance. Planned on Using AB C12 Contactors

Register to Reply
Active Contributor

Join Date: Jan 2015
Posts: 13
#14
In reply to #9

Re: Transformer Rating

01/22/2015 8:53 PM

FOr JRAEF post How do I determine my primary and secondary current values for fusing? Need some help

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#15
In reply to #14

Re: Transformer Rating

01/23/2015 3:07 AM

Use the code book.

1500va - Slow blow fuses, wire sized at least 125% of fuse rating, fuse rating to protect transformer and wire large enough to handle the fuses - looks approximately 10 amp time delay fuse and 16 AWG(min) TEW/AWM wire on the secondary. Primary current is reduced be the voltage ratio - about 1/4 with 480 volt primary - choose next largest standard fuse - say 3 amps - slow blow -if it blows on inrush use the next larger fuse.

Cheap transformers have high inrush - check with supplier - you may end up with a 15 amp primary fuse and 14 AWG wire. Many of the small transformers can be ordered as a kit with the primary and secondary fuses mounted on their terminal boards (IE: Hammond)

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); GW (1); jack of all trades (3); JRaef (1); norris534 (7); North of 60 (1); Tornado (1)